Mike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond repute
Re: Fuse Help

Quote:
Originally Posted by the man View Post
We did and they didnt call it so they must one not care or two it is ok, We couldent get it to run a 20 with out kicking out so that was our fix.
You need a 20A feeding the Spike and a 20A installed in the Spike. It is not an issue of getting caught by your inspectors. It is a safety issue. The Spike is only rated at 20A.

instead of using a bigger CB, investigate why it is tripping. You have a shorted wire or a bad compressor. It needs to be fixed.

Regards,

Mike