Quote:
Originally Posted by the man
We did and they didnt call it so they must one not care or two it is ok, We couldent get it to run a 20 with out kicking out so that was our fix.
|
You need a 20A feeding the Spike and a 20A installed in the Spike. It is not an issue of getting caught by your inspectors. It is a safety issue. The Spike is only rated at 20A.
instead of using a bigger CB, investigate why it is tripping. You have a shorted wire or a bad compressor. It needs to be fixed.
Regards,
Mike