Re: yes comunication, yes code but no response by robot
Quote:
Originally Posted by Alan Anderson
That's not a helpful answer. How can we know that you know what "the most current" is?
--> Please look at the Driver Station app's Diagnostics Tab and relay what it reports as the DS Version and cRIO image.
The cRIO has a bank of DIP switches between the LEDs and the Reset Button.
Each of the six switches can be either on or off.
--> Is SAFE MODE selected on or off?
--> Is CONSOLE OUT selected on or off?
--> Is IP RESET selected on or off?
--> Is NO APP selected on or off?
--> Is USER1 selected on or off?
--> Is NO FPGA selected on or off?
While you're at it, look at the cRIO's LEDs.
--> Is POWER indicating lit or dark?
--> Is FPGA indicating lit or dark?
--> Is STATUS indicating lit or dark?
--> Is USER1 indicating lit or dark?
So parts of the robot do respond to the code? That narrows things down a lot. I assume you're talking about using the digital output module in cRIO Slot 8, with the Solenoid Breakout on it, but I'd like to make sure.
---> Is the appropriate LED on the module lighting up when you activate the solenoid?
Let's try confirming that the problem is isolated to the Digital Sidecar.
---> Does the Driver Station report the battery voltage correctly?
It would help a lot if we could see your system. Is there any way you can take a photo of your Digital Sidecar, showing all of its connections? If so, specifically show both ends of the 37-pin cable to the cRIO, both ends of the power connection to the Power Distribution board, and both ends of the PWM cable to your speed controller. Please do it while the system is powered up and enabled, so we can try to interpret what the LEDs are trying to say.
|
ds version 10.02.08.00
crio image java-2010_v20
all switches on
power led on
all other leds off
|