Question Circuit Breakers

Does anyone know which specific 60A circuit breaker is included in the kit?

Are they single, double or triple poled?

What is the voltage rating, and what type is it?
__________________
Andrew Kraemer
Team 979
Dayton Dominators

Last edited by ark_1230 : 02-03-2002 at 20:53.
  #2   Spotlight this post!  
Unread 05-03-2002, 12:49
junkyarddawg junkyarddawg is offline
Registered User
no team
 
Join Date: Jan 2002
Location: Zeeland, Michigan
Posts: 36
junkyarddawg is an unknown quantity at this point
SquareD

The 60 amp breaker that comes in your kit is in a grayish box with yellow & blue print on it and roughly 4" x 3 1/2" x .75". There is a picture of it with all the details in the kit of parts section of the rule book, which you can access right on line at the USFIRST.ORG site. You can buy a replacement from your local SquareD distributor. The phone book may list Brands with the yellow page ad for "electrical distributors." Otherwise call any electrical distributor and they can tell you where to get one if they don't have it.

Tim Gates
Team #288
RoboDawgs
  #3   Spotlight this post!  
Unread 18-03-2002, 16:50
Greg McCoy's Avatar
Greg McCoy Greg McCoy is offline
boiler up!
FRC #3940 (CyberTooth)
Team Role: Engineer
 
Join Date: Feb 2002
Rookie Year: 2002
Location: Kokomo, IN
Posts: 484
Greg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond repute
Send a message via AIM to Greg McCoy
So how many teams have tripped it in competition?
  #4   Spotlight this post!  
Unread 18-03-2002, 18:06
Ian W. Ian W. is offline
College? What?
no team (Gompei and the Herd)
Team Role: College Student
 
Join Date: Jan 2002
Rookie Year: 2002
Location: Worcester, MA | Smithtown, NY
Posts: 1,464
Ian W. is a name known to allIan W. is a name known to allIan W. is a name known to allIan W. is a name known to allIan W. is a name known to allIan W. is a name known to all
Send a message via AIM to Ian W.
we have, so now we need to turn off parts of our robot before ramming/pulling other objects on the field.
__________________
AIM --> Woloi
Email --> ian@woloschin.com
  #5   Spotlight this post!  
Unread 19-03-2002, 12:02
Joe Johnson's Avatar Unsung FIRST Hero
Joe Johnson Joe Johnson is offline
Engineer at Medrobotics
AKA: Dr. Joe
FRC #0088 (TJ2)
Team Role: Engineer
 
Join Date: May 2001
Rookie Year: 1996
Location: Raynham, MA
Posts: 2,648
Joe Johnson has a reputation beyond reputeJoe Johnson has a reputation beyond reputeJoe Johnson has a reputation beyond reputeJoe Johnson has a reputation beyond reputeJoe Johnson has a reputation beyond reputeJoe Johnson has a reputation beyond reputeJoe Johnson has a reputation beyond reputeJoe Johnson has a reputation beyond reputeJoe Johnson has a reputation beyond reputeJoe Johnson has a reputation beyond reputeJoe Johnson has a reputation beyond repute
60 Amp Breaker: Shocking News...

In the Elimination Rounds at the Buckeye Regional, a number of teams, including Chief Delphi, had problems with the 60 Amp circuit breaker tripping.

I have been one of the voices saying that teams should not have any problems so I am especially anxious to get the word out on this issue to set the record straight.

Here is my story:

I knew we should have been okay on that breaker. There is no way we pull more than an average 100 Amps during a match, no almost no matter what we are doing. The charts tell me at 100A the breaker should take 2 minutes to trip. Yet we were going dark about ½ way through the match! What gives?

I thought perhaps it was a bad breaker but tests on the breaker we took out of our machine (thinking it might be bad) showed that it did not trip in less than 2 minutes when we tested it at 100A constant.

Shock turned out to be the explanation. If we just tap the breaker on the side of the housing with the handle of a screw drive (and not too hard either), the break time is effectively cut in half. This was found to be true at several different test conditions.

When we reviewed the tapes of our matches, in every match that we tripped the breaker, the robot took a hit right at the moment the beacon went dead.

I think we have found the smoking gun...

Bottom line: Teams that can figure out a way to keep their breaker from getting an impact load may be able to extend the trip time of their breaker by a factor of 2.

This is a important bit of news that we plan on implementing at the Great Lakes Regional this week.

Stay tuned for more results as the story continues...

Joe J.

Last edited by Joe Johnson : 19-03-2002 at 13:26.
  #6   Spotlight this post!  
Unread 19-03-2002, 16:26
Mikeman602 Mikeman602 is offline
Registered User
#0602
 
Join Date: Mar 2002
Location: Leesburg, VA
Posts: 10
Mikeman602 is an unknown quantity at this point
Send a message via AIM to Mikeman602
Our 60A breaker tripped when we took a particulary hard hit during the qualifying matches at VCU.

Michael D.
Team 602
  #7   Spotlight this post!  
Unread 19-03-2002, 16:49
ahecht's Avatar
ahecht ahecht is offline
'Luzer'
AKA: Zan
no team
Team Role: Alumni
 
Join Date: Dec 2001
Rookie Year: 2002
Location: Billerica, MA
Posts: 978
ahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond repute
Send a message via ICQ to ahecht Send a message via AIM to ahecht Send a message via Yahoo to ahecht
Re: 60 Amp Breaker: Shocking News...

Quote:
Originally posted by Joe Johnson
Bottom line: Teams that can figure out a way to keep their breaker from getting an impact load may be able to extend the trip time of their breaker by a factor of 2.
Would putting a clip on the breaker help? I know that many of the breakers in my house have a clip on them (which, i guess, turns them into auto-reset breakers), but would such a clip be legal in competition? If so, where would I get such a clip? Also, would it be legal to wire in a toggle switch if the breaker is locked?
__________________
Zan Hecht

Scorekeeper: '05 Championship DaVinci Field/'10 WPI Regional
Co-Founder: WPI-EBOT Educational Robotics Program
Alumnus: WPI/Mass Academy Team #190
Alumnus (and founder): Oakwood Robotics Team #992


"Life is an odd numbered problem the answer isn't in the back of the book." — Anonymous WPI Student
  #8   Spotlight this post!  
Unread 19-03-2002, 17:03
Ian W. Ian W. is offline
College? What?
no team (Gompei and the Herd)
Team Role: College Student
 
Join Date: Jan 2002
Rookie Year: 2002
Location: Worcester, MA | Smithtown, NY
Posts: 1,464
Ian W. is a name known to allIan W. is a name known to allIan W. is a name known to allIan W. is a name known to allIan W. is a name known to allIan W. is a name known to all
Send a message via AIM to Ian W.
hmm, maybe that's why our breaker blew a few times, for now reason at all. well, i think we'll still turn off none vital parts of the robot before we ram/push/etc. other things on trhe field. doesn't hurt to play it safe.
__________________
AIM --> Woloi
Email --> ian@woloschin.com
  #9   Spotlight this post!  
Unread 19-03-2002, 17:18
Kris Verdeyen's Avatar
Kris Verdeyen Kris Verdeyen is offline
LSR Emcee/Alamo Game Announcer
FRC #0118 (Robonauts)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 2001
Location: Houston, TX
Posts: 699
Kris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond repute
Joe, we had the same problem in training before ship. I remember someone saying that the breakers should be cable-tied in the 'on' position during matches to avoid tripping from shock, but I'm not sure that would help.

Our immediate solution was to first replace the offending breaker, and second, mount the new one vertically so as to avoid the largest part of the shock when we smash into the goals.

It also seems like someone might be clever enough to figure out the internal geometry of the breaker, and mount it so that the forces from the increased current are cancelled out by the forces from the impact, allowing you an instantaneous current peak.

Ok, so maybe that last bit was a little far-fetched.

One more issue, though - if the failures you're having are not shock-induced, current spikes can trip these breakers in very short time frames. So you don't need to average 100A if you have a 200A instantaneous spike. The spike will trip the breaker magnetically.
__________________
...Only a few people are awake and they live in a state of constant total amazement. -JP Shanley, Joe vs. the Volcano

Last edited by Kris Verdeyen : 19-03-2002 at 17:22.
  #10   Spotlight this post!  
Unread 19-03-2002, 17:36
RebAl's Avatar
RebAl RebAl is offline
ISee It When I Believe It
None #0329 (The R.A.I.D.)
Team Role: Mentor
 
Join Date: Jan 2002
Rookie Year: 2001
Location: N.Y.
Posts: 215
RebAl will become famous soon enough
Send a message via ICQ to RebAl Send a message via AIM to RebAl
A clip would not make it auto reset since you need to switch it to on then off then on again (and probally against the rules), the best way to avoid shock tripping is to mout the beraker perpendicular to the force ie. not parallel to the floor. This way the shock wont effect the tripping mechinism. Also if you suspend it with taught rubber tubing it should buffer out the major shocks.

Last edited by RebAl : 19-03-2002 at 19:21.
  #11   Spotlight this post!  
Unread 19-03-2002, 21:31
Greg McCoy's Avatar
Greg McCoy Greg McCoy is offline
boiler up!
FRC #3940 (CyberTooth)
Team Role: Engineer
 
Join Date: Feb 2002
Rookie Year: 2002
Location: Kokomo, IN
Posts: 484
Greg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond repute
Send a message via AIM to Greg McCoy
I'm not sure on this, but I think that the breaker will trip even if the switch is forced in the on position constantly. Even if it could be "kept on", it would defy the whole purpose of the 60 Amp breaker, which is to prevent overheating and a potentially major fire hazard.

I hadn't thought about shock affecting the breaker, but it makes sense now that I think about it. Often, the biggest amp load is when the robot runs into something and the motors are pushing hard, which also happens to be a big physical shock. Bad combo for the 60 Amp circuit breaker.
  #12   Spotlight this post!  
Unread 20-03-2002, 10:52
Leo M Leo M is offline
Registered User
#0384 (Tucker Tigers)
 
Join Date: Jun 2001
Location: Richmond, VA
Posts: 70
Leo M is just really niceLeo M is just really niceLeo M is just really niceLeo M is just really niceLeo M is just really nice
You can download the technical documentation on the breaker at this site:

http://www.squared.com/us/products/c...56A630064BC8F/$file/QOUcircuitbreakerFrameset.htm

Download document 0720CT9401, "QOU Miniature Circuit Breakers and Switches".

Tripping mechanisms are shown on pages 1 & 2 - both the thermal (inverse time) and the magnetic (instantaneous).

Thr trip curve is the right-hand one on page 14. It shows both the "inverse time" characteristic of the thermal mechanism, and the "instantaneous" magnetic mechanism.

Look at figure 1 on page 2. Of course a breaker on the verge of tripping will trip off when "mechanically agitated". It really wouldn't matter much what the mounting orientation is, either. It's ready to trip, it gets hit, it trips.

Once you look at, it appears very simple - deceptively so. Many such things will come back to bite you in your engineering career.

Beware of using equipment in applications outside the design basis. Very few electrical distribution cabinets move. Even the best of us (i.e., Dr. Joe) can be fooled on occasion.
__________________
Leo M.
  #13   Spotlight this post!  
Unread 21-03-2002, 14:39
RebAl's Avatar
RebAl RebAl is offline
ISee It When I Believe It
None #0329 (The R.A.I.D.)
Team Role: Mentor
 
Join Date: Jan 2002
Rookie Year: 2001
Location: N.Y.
Posts: 215
RebAl will become famous soon enough
Send a message via ICQ to RebAl Send a message via AIM to RebAl
Here is Square D's responce about shock impact:

Alexander,
There is no technical information on this application. QOU breakers are
susceptible to shock
or a large impact. Suggest locating the breaker where it won't receive that
shock or large
impact.
Sherry Glass
CIC Tech Support
  #14   Spotlight this post!  
Unread 24-03-2002, 10:46
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,811
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
On the subject of the 60 amp breakers, I do not believe that any team can trip this breaker on current overload. The breaker has been tested and has predictable trips when run at 120 volts AC and 45 volts DC. Even though the battery at full charge is capable of delivering 450 amps, the terminal voltage at that current would be low enough to reset the robot controller before the circuit breaker would have a chance to react. These circuit breakers are very susceptible to impact trips, however. (try it yourself by tapping on the circuit breaker on either side the wires enter, you will be surprised at how little it takes.)They are especially sensitive to shocks from the sides, where the the wires are attached. For this reason, circuit breakers should not be firmly mounted in the robot such that any shock to the robot is transmitted directly to the circuit breaker. Teams have been successful in adding a few inches of extra #6 wire when installing the breaker. This allows the wire to absorb most of the shock and keeps the breaker from shock tripping.
We add a small block of plastic to the breaker that is wider than the body by 1 inch on both sides. (This allows us to tywrap the #6 wires to prevent flex failures in the wire at the breaker.) Then we bend the wires back so that there is several inches before they are attched to a frame member. That extra wire then absords the impacts to the frame.
I saw several impact trips at Great Lakes this weekend.
Hope this helps,

P.S. The clips on circuit breakers (in a distribution panel) are to prevent someone from turning them off accidently. They do not prevent the breaker from tripping on either current overload or impact.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #15   Spotlight this post!  
Unread 24-03-2002, 11:02
anomly_rox anomly_rox is offline
Registered User
#0816
 
Join Date: Mar 2002
Location: West Ampton
Posts: 12
anomly_rox is an unknown quantity at this point
my robot took numerous hard hits philly to the side the breaker is on and so on, we never blew out once. Is it possible there is just a batch of bad breakers out there?

Last edited by Brandon Martus : 21-04-2003 at 02:51.
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
speed controllers & circuit breakers deuceswild Electrical 2 15-01-2003 14:46
circuit breakers.... archiver 2001 2 23-06-2002 23:58
Circuit breakers archiver 2000 8 23-06-2002 23:30
Circuit Breakers: Tripping Al Skierkiewicz Electrical 7 10-04-2002 12:40
Shocking News about Circuit Breakers Joe Johnson Technical Discussion 0 19-03-2002 12:08


All times are GMT -5. The time now is 09:01.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi