Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
On the subject of the 60 amp breakers, I do not believe that any team can trip this breaker on current overload. The breaker has been tested and has predictable trips when run at 120 volts AC and 45 volts DC. Even though the battery at full charge is capable of delivering 450 amps, the terminal voltage at that current would be low enough to reset the robot controller before the circuit breaker would have a chance to react. These circuit breakers are very susceptible to impact trips, however. (try it yourself by tapping on the circuit breaker on either side the wires enter, you will be surprised at how little it takes.)They are especially sensitive to shocks from the sides, where the the wires are attached. For this reason, circuit breakers should not be firmly mounted in the robot such that any shock to the robot is transmitted directly to the circuit breaker. Teams have been successful in adding a few inches of extra #6 wire when installing the breaker. This allows the wire to absorb most of the shock and keeps the breaker from shock tripping.
We add a small block of plastic to the breaker that is wider than the body by 1 inch on both sides. (This allows us to tywrap the #6 wires to prevent flex failures in the wire at the breaker.) Then we bend the wires back so that there is several inches before they are attched to a frame member. That extra wire then absords the impacts to the frame.
I saw several impact trips at Great Lakes this weekend.
Hope this helps,

P.S. The clips on circuit breakers (in a distribution panel) are to prevent someone from turning them off accidently. They do not prevent the breaker from tripping on either current overload or impact.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
 


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
speed controllers & circuit breakers deuceswild Electrical 2 15-01-2003 14:46
circuit breakers.... archiver 2001 2 23-06-2002 23:58
Circuit breakers archiver 2000 8 23-06-2002 23:30
Circuit Breakers: Tripping Al Skierkiewicz Electrical 7 10-04-2002 12:40
Shocking News about Circuit Breakers Joe Johnson Technical Discussion 0 19-03-2002 12:08


All times are GMT -5. The time now is 05:25.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi