  #1   Spotlight this post!  
Unread 31-03-2002, 11:03
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,811
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Circuit Breakers: Tripping

I thought this was important enough to start a new thread so here goes...
Over the last two weekends I have had the opportunity to inspect many robots that have been tripping circuit breakers. In all cases I was informed by the team members that they were tripping due to current overload. When questioned though most reports were that the breakers tripped when in shoving matches or when grabbing a goal. With a few when just running all by themselves. Additionally most teams reported never having tripped in practice, only in competition.
So this is what I observed...
1. The majority of robots that tripped had their breaker hard mounted to the robot frame.
2. If a team used the #6 wire to cushion the breaker, the breaker was mounted vertically (i.e. wires out the top and bottom.)or the wires were not flexible.
3. The teams had aggressive tread design or tank treads that caused a lot of vibration when running.
4. The team play strategy was to "bang" a goal out of position.
5. The robot had a high center of gravity or short wheelbase causing some bouncing while running.
Of the robots I observed, vibration or impact were involved in some form or another in every case. Some robots tripped just running from one side to the other on the second day. (This I am guessing is in relation to the carpet getting beat up over the course of a competition and causes an irregular surface.)
I still cannot point to current tripping as a possibility. It may be a contibuting factor in some robot designs made worse by vibration. One team who suspected they were tripping on overloads and were replacing breakers every few matches graciously opened one for inspection. No major defects were noted, but the design of the breaker would suggest that heat, vibration, and current could all contribute to a trip condition and very likely multiple vibrations or impacts would make tripping more likely.
One final note, in the case of one team, the wire clamp on the circuit breaker was loose. Loose connections on high current wires cause heat and the heat from that connection was transmitted to the thermal cutout in the breaker and tripped it off. Tight wires and no more trips.
Hope this helps. If you have had problems tripping breakers and are going to nationals, I'd like to see your robot. I am usually in our pit, just stop by.
Good Luck All
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #2   Spotlight this post!  
Unread 06-04-2002, 20:38
DanL DanL is offline
Crusty Mentor
FRC #0097
Team Role: Mentor
 
Join Date: Jan 2002
Rookie Year: 2001
Location: Somerville, MA
Posts: 682
DanL is just really niceDanL is just really niceDanL is just really niceDanL is just really niceDanL is just really nice
Send a message via AIM to DanL
Not really the pushing

I don't really think it's the banging thats tripping the robots. Our robot is a, quite frankly, kamikazee. We ran out of weight for a claw mechanism, so all we have no is really powerful/fast drive system. Guess what we use it for - running into other robots... and hard (team 596, the Sci-Clones can attest to that - at the nyc regional, we kinda bent one of their pnumatic cylinders. But don't worry, there are no hard feelings between us - actually we picked them as our alliance partners =D).

Anyways, at the SPBLI Long Island regional, we were tripping our main breaker like mad. During our practice rounds, we were flipping the breaker every few minutes. This was fixed by drilling some bolts into our thick wheels and actually decreasing their surface area (see what we mean here ). The wheels themselves were dragging while turning (tank-steering), and this was over-working our motors. This fixed our main breaker problems.

Even so, practically every other round during the actual competition, our main breaker flipped and we sat there. We were ramming a lot, and that probably contributed to it somewhat, but our main problem was with the drive train. We have the opportunity to go down on treads (for uber-power). Turns out this was our problem. The treads seemed to have too much friction moving. Some of our idlers didn't spin that well, and so (I think this is how you describe it) the motors were working too hard. Bam - we lost power. Anyways, at the NYC Regional, we added some bearings to our idlers so that they spun like a dream, and presto - our breaker problems were no more.

Few robots were banging as hard as we do. Look at the scratches on the front plate in the above picture, we bent some Bosch extrusion, heck, we even chipped some lexan - who knows what we did to other robot (again, sorry 596) =D Anyways, what it comes down to is that although banging did have some effect on the breaker, I suggest that if your still having breaker problems after hanging the breaker loosely and perpendicular to the front of the robot, you look into your drive train, not your playing tactics.
__________________
Dan L
Team 97 Mentor
Software Engineer, Vecna Technologies
  #3   Spotlight this post!  
Unread 06-04-2002, 20:57
Clark Gilbert's Avatar
Clark Gilbert Clark Gilbert is offline
Registered User
no team
Team Role: Alumni
 
Join Date: May 2001
Rookie Year: 2000
Location: Columbus, IN
Posts: 1,946
Clark Gilbert has a reputation beyond reputeClark Gilbert has a reputation beyond reputeClark Gilbert has a reputation beyond reputeClark Gilbert has a reputation beyond reputeClark Gilbert has a reputation beyond reputeClark Gilbert has a reputation beyond reputeClark Gilbert has a reputation beyond reputeClark Gilbert has a reputation beyond reputeClark Gilbert has a reputation beyond reputeClark Gilbert has a reputation beyond reputeClark Gilbert has a reputation beyond repute
Exclamation TechnoKat Breaker Secrets Revealed...lol

Ok....I am not an electrical person and this is basically all copied and pasted from an email i recieved about our breaker problems...this may help some people...


------------------------------------------------------------------------------------

I've picked two of the five breakers as being much better performers, these two
>go about 45% longer at 120 amps, compared to the worst breakers.
>
>COLD SPRAY WORKS
>Precooling the breaker provides 60% more duration on the first power cycle.
>This rises to 120% more duration on repeated power cycles at 5 minute intervals
>(to simulate the high cycle rate found in finals competition). Bottom-line: a
>10 second blast of cold spray will restore the breaker to its original
>performance even if it has just been overloaded. Where do we get more of this
>stuff. I've used my only can during this test?

------------------------------------------------------------------------------------

1. Suspend our best circuit breaker by the 6 ga. wire and 2-4 strips of latex
tubing, directly between the battery and the power panel
2. Possibly move the power panel closer to the battery (or the battery closer
to the power panel) so we can cut down the length of 6 ga. wire.

------------------------------------------------------------------------------------

Ok....it's me again.....i know our final solution to our problem was that we did some electrical work...mounted the breaker onto a flexible/bouncy kind of V shaped lexan strip...and we really use the Cold Spray....

__________________
Purdue Alumni
Cummins, Inc.
  #4   Spotlight this post!  
Unread 06-04-2002, 20:59
Jay Lundy Jay Lundy is offline
Programmer/Driver 2001-2004
FRC #0254 (The Cheesy Poofs)
Team Role: Alumni
 
Join Date: Jun 2001
Rookie Year: 2001
Location: Berkeley, CA
Posts: 320
Jay Lundy is a name known to allJay Lundy is a name known to allJay Lundy is a name known to allJay Lundy is a name known to allJay Lundy is a name known to allJay Lundy is a name known to all
Our breaker is mounted vertically on the piece of wood in the center of our robot where all our electronics are. We are an aggressive 2 goal grabbing robot and we've gotten into a lot of pushing matches and we've had some hard impacts (so hard that we bent our goal latch once) and our breaker has never tripped.

Maybe the wood dampens the shock, but who knows.

We haven't actually measured the amps we pull during pushing matches, but we use a dual-motor drive train, we transfer the weight of the goals, and our treads have a high coefficient of friction and we still haven't tripped it.
  #5   Spotlight this post!  
Unread 06-04-2002, 21:03
Greg McCoy's Avatar
Greg McCoy Greg McCoy is offline
boiler up!
FRC #3940 (CyberTooth)
Team Role: Engineer
 
Join Date: Feb 2002
Rookie Year: 2002
Location: Kokomo, IN
Posts: 484
Greg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond reputeGreg McCoy has a reputation beyond repute
Send a message via AIM to Greg McCoy
As Clark's quote stated, the breakers are highly variable in their trip time. Maybe you just got a "good" breaker
  #6   Spotlight this post!  
Unread 06-04-2002, 21:51
Ian W. Ian W. is offline
College? What?
no team (Gompei and the Herd)
Team Role: College Student
 
Join Date: Jan 2002
Rookie Year: 2002
Location: Worcester, MA | Smithtown, NY
Posts: 1,464
Ian W. is a name known to allIan W. is a name known to allIan W. is a name known to allIan W. is a name known to allIan W. is a name known to allIan W. is a name known to all
Send a message via AIM to Ian W.
Yes, as SDM said above, we had lots of problems at our first regional. We tripped both the main breaker and the 20 and 30 amp ones. So, if our robot wasn't moving in jerks across the field, it was dead. Anyways, we really cut down on the friction at NYC (second regional for us) and we had a huge power increase. Not only did we stop tripping breakers (any of them) we had a huge increase in the speed and power of our robot. As Dan said, if the problem is not electrical, make sure your drivetrain has as much graphite, nylon washers (to reduce friction and contact between parts), and anything else that might produce friction. You'll be amazed at the amount of power that your robot now has. I know i was.

Also, make sure your frame is not grounded (by the light or anything else) cause that was tripping some bots i saw.
__________________
AIM --> Woloi
Email --> ian@woloschin.com
  #7   Spotlight this post!  
Unread 07-04-2002, 04:40
ahecht's Avatar
ahecht ahecht is offline
'Luzer'
AKA: Zan
no team
Team Role: Alumni
 
Join Date: Dec 2001
Rookie Year: 2002
Location: Billerica, MA
Posts: 978
ahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond reputeahecht has a reputation beyond repute
Send a message via ICQ to ahecht Send a message via AIM to ahecht Send a message via Yahoo to ahecht
As a quick fix, we unscrewed our breaker from the frame, laid a piece of latex tubing down flat where our breaker was, and screwed the breaker back down on top of the tubing. This whole operation took less than five minutes, and we never had the breaker trip after that.
__________________
Zan Hecht

Scorekeeper: '05 Championship DaVinci Field/'10 WPI Regional
Co-Founder: WPI-EBOT Educational Robotics Program
Alumnus: WPI/Mass Academy Team #190
Alumnus (and founder): Oakwood Robotics Team #992


"Life is an odd numbered problem the answer isn't in the back of the book." — Anonymous WPI Student
  #8   Spotlight this post!  
Unread 10-04-2002, 12:40
Manoel's Avatar
Manoel Manoel is offline
Registered User
FRC #0383 (Brazilian Machine)
Team Role: Mentor
 
Join Date: Jun 2001
Rookie Year: 2000
Location: Porto Alegre, RS, Brazil
Posts: 608
Manoel has a reputation beyond reputeManoel has a reputation beyond reputeManoel has a reputation beyond reputeManoel has a reputation beyond reputeManoel has a reputation beyond reputeManoel has a reputation beyond reputeManoel has a reputation beyond reputeManoel has a reputation beyond reputeManoel has a reputation beyond reputeManoel has a reputation beyond reputeManoel has a reputation beyond repute
Send a message via ICQ to Manoel Send a message via MSN to Manoel
We had lots of problems with the main breaker tripping due to impact. After changing it's orientation and cushioning it, the problem of impact was gone. We did, however, trip the breaker due to current: We were alone in the mid-field (thus, no chance of impact), with 2 drill motors, 2 chapuia, 2 seats, the light and the compressor on. Will never happen again, but it is indeed possible to trip it by current.
__________________
Manoel Flores da Cunha
Mentor
Brazilian Machine
Team # 383
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
speed controllers & circuit breakers deuceswild Electrical 2 15-01-2003 14:46
circuit breakers.... archiver 2001 2 23-06-2002 23:58
Circuit breakers archiver 2000 8 23-06-2002 23:30
Circuit Breakers ark_1230 Electrical 28 09-04-2002 23:16
Shocking News about Circuit Breakers Joe Johnson Technical Discussion 0 19-03-2002 12:08


All times are GMT -5. The time now is 09:00.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi