How to wire a SMC Solenoid Valve SY5220-5DO-C6 ?
http://content.smcetech.com/pdf/SY3.5.7.9000.pdf
Page Number 18. It is a 24VDC double solenoid valve.I just couldn't find anyway to wire it.I mean which port is positive and which is ground ? And there is also one more port on it.Also , it writes "1" next to one of the ports and "2" next to another. |
|
#2
|
|||||
|
|||||
|
Re: How to wire a SMC Solenoid Valve SY5220-5DO-C6 ?
Which style of connector are you using? Typically, the black wire goes to "ground" and the red wire goes to the pin you're using to control the solenoid. For a 24 volt solenoid, you will be using the Solenoid Breakout board on the NI 9472 digital sourcing module in slot 3 of the cRIO. Follow the Robot Power Distribution Diagram (24V Solenoid).
|
|
#3
|
|||
|
|||
|
Re: How to wire a SMC Solenoid Valve SY5220-5DO-C6 ?
Quote:
Except of that , I know that it should be wired to the solenoid breakout. |
|
#4
|
|||||
|
|||||
|
Re: How to wire a SMC Solenoid Valve SY5220-5DO-C6 ?
Just to clarify: you aren't using a connector designed to plug in to the pins on this series of solenoid valve?
|
|
#5
|
||||
|
||||
|
Re: How to wire a SMC Solenoid Valve SY5220-5DO-C6 ?
Given your part number is a DIN connector, you will need to put some wires to the DIN connector. Remove it from the valve, take out the screw on top and separate the wiring.
Then have a look at: http://literature.rockwellautomation...a548_-en-p.pdf It shows some connections for rockwell's connectors, but the type is an ISO standard, so I would look at the pictures and try and match it to yours. You could then put a ohm-meter on the coil connections to see if you see a connections (should be low, but not 0). Hope this helps. |
|
#6
|
||||
|
||||
|
Re: How to wire a SMC Solenoid Valve SY5220-5DO-C6 ?
Be aware that the Cv value for that solenoid is 0.33 (P->A/B) which is very slightly over the 0.32 that is allowed by FIRST [R71-C]. The only SY5000 series solenoid which is below 0.32 is the -C4.
Also note that this solenoid specifies 6mm diameter tubing, which is OK by the rules, but different from the 1/4" tubing in the kit. I think they do fit together, but I don't know if they provide a reliable seal and are easily removed. I'm no expert in pneumatics, but have had to do a lot of learning for FIRST. |
![]() |