D-link dropping out

our wireless network bridge keeps dropping out when we run our robot.

one of our mentors thinks that the voltage to the bridge is dropping causing the connection to fail.

is this possible or what else could be causing this?
  #2   Spotlight this post!  
Unread 08-03-2012, 18:45
RufflesRidge RufflesRidge is offline
Registered User
no team
 
Join Date: Jan 2012
Location: USA
Posts: 989
RufflesRidge has a brilliant futureRufflesRidge has a brilliant futureRufflesRidge has a brilliant futureRufflesRidge has a brilliant futureRufflesRidge has a brilliant futureRufflesRidge has a brilliant futureRufflesRidge has a brilliant futureRufflesRidge has a brilliant futureRufflesRidge has a brilliant futureRufflesRidge has a brilliant futureRufflesRidge has a brilliant future
Re: D-link dropping out

Is the bridge running through the 12V-5V convertor connected to the dedicated 12V supply on the end of the Power Distribution board? (not the regular 12V connectors along the long sides)
  #3   Spotlight this post!  
Unread 08-03-2012, 18:46
dellagd's Avatar
dellagd dellagd is offline
Look for me on the field!
AKA: Griffin D
FRC #2590 (Nemesis) #2607 (The Fighting Robovikings)
Team Role: Mentor
 
Join Date: Sep 2011
Rookie Year: 2011
Location: PA
Posts: 890
dellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond repute
Re: D-link dropping out

Hello, and welcome to the forum!

Before I start, I'd just like to tell you that generally it is frowned upon to create a user with the name "helpme". Forums are about helping others too, so yeah!

Anyway, we need to know a bit more about your robot. Are you supplying the bridge with power from the 12 volt converter?

What is defined at "dropping out"? Does the radio reset and do a full reboot (like you just turned on the robot)? Or does it just drop out for a few seconds?

This may seem unrelated, but are you using a 2CAN on your robot? We were, and it was causing us to loose communications with the robot, sometimes for a moment, sometimes indefinitely.
__________________
Check out some cool personal projects in computers, electronics, and RC vehicles on my blog!

2016 MAR DCMP Engineering Excellence Award
2016 MAR Westtown Innovation in Control Award
2016 MAR Hatboro-Horsham Industrial Design Award
2015 Upper Darby District Winners - Thanks 225 and 4460!
2015 Upper Darby District Industrial Design Award
2015 Hatboro-Horsham District Winners - Thanks 2590 and 5407!
2014 Virginia Regional Winners - Thanks so much 384 and 1610, I will never forget that experience!
2014 Virginia Quality Award
2014 MAR Bridgewater-Raritan Innovation in Control Award
2014 MAR Hatboro-Horsham Gracious Professionalism Award
2013 MAR Bridgewater-Raritan Innovation in Control Award
2012 MAR Lenape Quality Award
  #4   Spotlight this post!  
Unread 08-03-2012, 18:56
helpme helpme is offline
Registered User
None #3662
 
Join Date: Mar 2012
Location: washington
Posts: 7
helpme is an unknown quantity at this point
Re: D-link dropping out

Quote:
Originally Posted by RufflesRidge View Post
Is the bridge running through the 12V-5V convertor connected to the dedicated 12V supply on the end of the Power Distribution board? (not the regular 12V connectors along the long sides)
yes.

Quote:
Originally Posted by dellagd View Post
Hello, and welcome to the forum!

Before I start, I'd just like to tell you that generally it is frowned upon to create a user with the name "helpme". Forums are about helping others too, so yeah!

Anyway, we need to know a bit more about your robot. Are you supplying the bridge with power from the 12 volt converter?

What is defined at "dropping out"? Does the radio reset and do a full reboot (like you just turned on the robot)? Or does it just drop out for a few seconds?

This may seem unrelated, but are you using a 2CAN on your robot? We were, and it was causing us to loose communications with the robot, sometimes for a moment, sometimes indefinitely.
when we turn on the robot the wireless works but when we move the bridge manipulator/ ball elevevator the connections stops and we have to reconnect from the driverstation.

no we have pwm.

also we just bout a new d-link.
  #5   Spotlight this post!  
Unread 08-03-2012, 19:26
dellagd's Avatar
dellagd dellagd is offline
Look for me on the field!
AKA: Griffin D
FRC #2590 (Nemesis) #2607 (The Fighting Robovikings)
Team Role: Mentor
 
Join Date: Sep 2011
Rookie Year: 2011
Location: PA
Posts: 890
dellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond reputedellagd has a reputation beyond repute
Re: D-link dropping out

It might be interesting to hook up a multi-meter to the wires that go to the wireless bridge and see if the voltage drops when you loose comms.

Also, just generally watch the lights on the robot and the bridge to see if anything changes from normal behavior.
__________________
Check out some cool personal projects in computers, electronics, and RC vehicles on my blog!

2016 MAR DCMP Engineering Excellence Award
2016 MAR Westtown Innovation in Control Award
2016 MAR Hatboro-Horsham Industrial Design Award
2015 Upper Darby District Winners - Thanks 225 and 4460!
2015 Upper Darby District Industrial Design Award
2015 Hatboro-Horsham District Winners - Thanks 2590 and 5407!
2014 Virginia Regional Winners - Thanks so much 384 and 1610, I will never forget that experience!
2014 Virginia Quality Award
2014 MAR Bridgewater-Raritan Innovation in Control Award
2014 MAR Hatboro-Horsham Gracious Professionalism Award
2013 MAR Bridgewater-Raritan Innovation in Control Award
2012 MAR Lenape Quality Award
  #6   Spotlight this post!  
Unread 08-03-2012, 19:37
MrBasse MrBasse is offline
Registered User
FRC #3572 (Wavelength)
Team Role: Coach
 
Join Date: Jul 2011
Rookie Year: 2010
Location: Norton Shores, MI
Posts: 679
MrBasse has a reputation beyond reputeMrBasse has a reputation beyond reputeMrBasse has a reputation beyond reputeMrBasse has a reputation beyond reputeMrBasse has a reputation beyond reputeMrBasse has a reputation beyond reputeMrBasse has a reputation beyond reputeMrBasse has a reputation beyond reputeMrBasse has a reputation beyond reputeMrBasse has a reputation beyond reputeMrBasse has a reputation beyond repute
Re: D-link dropping out

Just out of curiosity, what is the battery voltage doing when you lose communication, watch the graphs in the DS and check to see if you bridge manipulator is draining all the power.

Are you sure it is the wireless losing communication? Is it possible that something isn't running right and drops the voltage so low the crio is rebooting? I guess in short, do you lose communication, robot code, or both?
__________________
Andrew Basse
Coach - FRC Team 3572 - Wavelength
  #7   Spotlight this post!  
Unread 08-03-2012, 21:10
slijin's Avatar
slijin slijin is offline
Pockets
AKA: Samuel Lijin
FRC #0694 (StuyPulse)
Team Role: Mentor
 
Join Date: Jan 2010
Rookie Year: 2010
Location: New York City
Posts: 537
slijin is a splendid one to beholdslijin is a splendid one to beholdslijin is a splendid one to beholdslijin is a splendid one to beholdslijin is a splendid one to beholdslijin is a splendid one to beholdslijin is a splendid one to behold
Re: D-link dropping out

What proof do you have that your bridge is actually dropping out?

The dedicated power output functions down to a 4.5V input, and it takes a lot to force a voltage dip big enough to bring you down that far.
__________________

2010-12 CT Chairman's
2011 Galileo 5th seed
2010 NY Regional Winners
  #8   Spotlight this post!  
Unread 09-03-2012, 00:47
helpme helpme is offline
Registered User
None #3662
 
Join Date: Mar 2012
Location: washington
Posts: 7
helpme is an unknown quantity at this point
Re: D-link dropping out

Quote:
Originally Posted by dellagd View Post
It might be interesting to hook up a multi-meter to the wires that go to the wireless bridge and see if the voltage drops when you loose comms.

Also, just generally watch the lights on the robot and the bridge to see if anything changes from normal behavior.
will try this thnx.

Quote:
Originally Posted by MrBasse View Post
Just out of curiosity, what is the battery voltage doing when you lose communication, watch the graphs in the DS and check to see if you bridge manipulator is draining all the power.

Are you sure it is the wireless losing communication? Is it possible that something isn't running right and drops the voltage so low the crio is rebooting? I guess in short, do you lose communication, robot code, or both?
we just lose communication.


Quote:
Originally Posted by slijin View Post
What proof do you have that your bridge is actually dropping out?

The dedicated power output functions down to a 4.5V input, and it takes a lot to force a voltage dip big enough to bring you down that far.
communication with the robot is lost....
  #9   Spotlight this post!  
Unread 09-03-2012, 00:58
EricH's Avatar
EricH EricH is offline
New year, new team
FRC #1197 (Torbots)
Team Role: Engineer
 
Join Date: Jan 2005
Rookie Year: 2003
Location: SoCal
Posts: 19,813
EricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond repute
Re: D-link dropping out

We realize that communication is dropping out. What we don't know is why.

Every question we ask here is aimed at finding out why it's dropping out, so you can fix the root cause of the problem. There are a few possible reasons that comms can drop.

--Voltage could be dropping really low (see the battery voltage check request), which opens up a few more places to look for the problem.
--A non-electrical problem could be cropping up. How's the Ethernet connection holding, and is it loose?
--Lights will tell a lot. What are they doing, particularly the ones on the cRIO and the bridge?
--Do comms drop out under any other conditions than the bridge material/ball collector moving? If no, then it's going to be somewhere in that mechanism. Is it pulling a cable, or close to the D-link?
__________________
Past teams:
2003-2007: FRC0330 BeachBots
2008: FRC1135 Shmoebotics
2012: FRC4046 Schroedinger's Dragons

"Rockets are tricky..."--Elon Musk

  #10   Spotlight this post!  
Unread 09-03-2012, 01:29
roystur44's Avatar
roystur44 roystur44 is offline
Mentor/Sponsor
AKA: Roy Dumlao
FRC #4543 (Apollo Robotics)
Team Role: Mentor
 
Join Date: Mar 2010
Rookie Year: 2006
Location: San Jose,California
Posts: 362
roystur44 has a reputation beyond reputeroystur44 has a reputation beyond reputeroystur44 has a reputation beyond reputeroystur44 has a reputation beyond reputeroystur44 has a reputation beyond reputeroystur44 has a reputation beyond reputeroystur44 has a reputation beyond reputeroystur44 has a reputation beyond reputeroystur44 has a reputation beyond reputeroystur44 has a reputation beyond reputeroystur44 has a reputation beyond repute
Send a message via Yahoo to roystur44
Re: D-link dropping out

Strain relief the 5v connector that plugs into the back of the Dlink. A jolt will jiggle the connector and cause a voltage drop to the radio. We secure the cable and tape our connector down in competition
__________________
Roy Dumlao

Mentor/Sponsor
2006-2012 971
2013-2017 4543
  #11   Spotlight this post!  
Unread 09-03-2012, 05:21
Dale(294engr]'s Avatar
Dale(294engr] Dale(294engr] is offline
Mentor/Sponsor since '98
FRC #0294 (Beach Cities Robotics)
Team Role: Engineer
 
Join Date: Jan 2004
Rookie Year: 1998
Location: Redondo Beach, CA
Posts: 92
Dale(294engr] is a glorious beacon of lightDale(294engr] is a glorious beacon of lightDale(294engr] is a glorious beacon of lightDale(294engr] is a glorious beacon of lightDale(294engr] is a glorious beacon of lightDale(294engr] is a glorious beacon of light
Re: D-link dropping out

Quote:
Originally Posted by dellagd View Post
It might be interesting to hook up a multi-meter to the wires that go to the wireless bridge and see if the voltage drops when you loose comms.

Also, just generally watch the lights on the robot and the bridge to see if anything changes from normal behavior.
A DMM might not see a drop out of brief time that will cause this problem.

An oscilloscope is preferred Voltage Vs time instrument but time consuming
Solicit an EE mentor to expedite scope usage.

A digital storage scope will view long time unsynced scan (DSO)
Seek out resources you have or can borrow.
Since problem is mystery, initially use long scan duration, if blob drop out is evident
try external sync to your suspected motor with faster scan to see detail over time of "glitch" or other suspected devices to determine root cause to fix.

Teams at each regional will have a scope for these hard time related problems: sagging bus, intermittent shorts, (RS-775?),

Potential Problem Note: high powered motors: CIM RS775 & FP stall current each is over 100A

all motors start-up with a high brief stall current "glitch" ~50ms-350ms (low mass shooter - drivetrain)
depending on load mass, acceleration to speed varies as a function of gearing.
if geared too fast (like direct drive), glitch is longer, due to less torque available to move load to arrive at higher end speed

The longer & higher peak amplitude the spin up glitch, the lower the voltage dips to all other loads, especially sensitive electronically controlled ones for a longer time, potentially causing reset, drop out, reboot, jerky action, noise induced indeterminate's etc.

It is important to identify such basic problems early; gear changing can be challenge in the heat of competing.

For sure make good mechanically solid low resistance crimps, minimize insertion cycles of critical connectors and autoReset Breakers (20, 30, 40A) loose fit/crimp/screw = higher contact resistance! use welding cable stranded wire of heavier gauge especially on longer runs for less tension on connections and less path R.

competition batts drop ~1v at battery terminal for every ~50A drawn typically
then add Vsag from robot wiring resistance to load in question.

2 CIMS stalled draw 2x133A 266A causing >5v sag at fully charged batt terms to 12.6-5= 7.5v
could be trouble once rest of wiring connection resistance is added say 5v or less at load for a few hundred milliseconds??

Excluding average state of charge battery Rinternal = .020 ohms
Is rest of your the total serial current path out & back to batt consisting of connectors, crimps, wiring, 2 breakers, total less than .010 ohms? if exactly then .01*266 = another 2.66v GONE! 7.5-2.7= 4.8v at load end voila!!

Good Luck .. hope this inside knowledge may help find the culprit...

I'll be at LA (=Long Beach) & STL as bearded iridescent green capped RI to help teams with tough electrical problems.
  #12   Spotlight this post!  
Unread 09-03-2012, 05:51
slijin's Avatar
slijin slijin is offline
Pockets
AKA: Samuel Lijin
FRC #0694 (StuyPulse)
Team Role: Mentor
 
Join Date: Jan 2010
Rookie Year: 2010
Location: New York City
Posts: 537
slijin is a splendid one to beholdslijin is a splendid one to beholdslijin is a splendid one to beholdslijin is a splendid one to beholdslijin is a splendid one to beholdslijin is a splendid one to beholdslijin is a splendid one to behold
Re: D-link dropping out

Quote:
Originally Posted by helpme View Post
communication with the robot is lost....
I cannot emphasize more how correct Eric is. Although loss of communications is generally symptomatic of a bridge problem, keep in mind that the problem can still lie elsewhere. The most conclusive and definitive way to determine if your bridge is power cycling is to observe the lights on the bridge and to see if they all turn off. If so, then you can be certain that your bridge is indeed cutting out.

Another suggestion to consider is a secure power connection - does the barrel connector going into the bridge ensure a steady power supply, or does it wobble out when you run the mechanisms at fault?

Quote:
Originally Posted by helpme View Post
when we turn on the robot the wireless works but when we move the bridge manipulator/ ball elevevator the connections stops and we have to reconnect from the driverstation.
Please clarify what you mean by "reconnect". Are communications restored by themselves after you lose comms? If so, how long does the reconnection take? If not, what do you have to do to reestablish communication?
__________________

2010-12 CT Chairman's
2011 Galileo 5th seed
2010 NY Regional Winners
  #13   Spotlight this post!  
Unread 11-03-2012, 16:46
michael714's Avatar
michael714 michael714 is offline
Registered User
FRC #3863 (Pantherbotics)
Team Role: Teacher
 
Join Date: Apr 2006
Rookie Year: 2007
Location: Newbury Park, CA
Posts: 46
michael714 is on a distinguished road
Click enable lose comms

Just had a similar problem and sure enough, you're trouble shooting recommendations worked. We were pressing the Enable button on the driverstation (the soft button) and then losing comms immediately. I had somebody eyeball the robot and it turned out that when I pressed the Enable button, it looked like power cycled on the robot. We noticed an error indication on a drive wheel Victor, so we replaced that Victor. We're back in action! Thanks folks!
  #14   Spotlight this post!  
Unread 13-03-2012, 00:07
blackflame2996's Avatar
blackflame2996 blackflame2996 is offline
Alumni
AKA: David Donahue
FRC #2996 (Cougars Gone Wired)
Team Role: Alumni
 
Join Date: Nov 2011
Rookie Year: 2011
Location: Colorado springs, CO
Posts: 67
blackflame2996 is a name known to allblackflame2996 is a name known to allblackflame2996 is a name known to allblackflame2996 is a name known to allblackflame2996 is a name known to allblackflame2996 is a name known to all
Re: D-link dropping out

It seems that your DAP is powering off due to a voltage drop or surge of interference. At the Kansas City regional, we had a similar problem with an Axis 206 camera: whenever we moved our bridge arm, the camera would power off. we fixed this problem by isolating the camera from all metal, supporting it with a piece of polycarbonate plastic. Try isolating the power wire from those running to and from the Jags or victors.
__________________
2009 Regional Winners
2011 Regional Chairman's Award
2012 Regional Winners
2013 Regional Chairman's Award
  #15   Spotlight this post!  
Unread 13-03-2012, 16:57
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,792
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: D-link dropping out

There is a failure mode on the 5 volt convertor that will send 7 volts to the radio on full battery voltage and then as the battery goes down so to does the output of the convertor. It acts just a like a resistor. I believe that the failure mode is caused by a reverse electrical connection at some point. Double check the output voltage of the convertor.
Blackflame, the camera body is connected to the negative lead of the power supply. If you have other frame shorts, it is possible to shutdown the power supplies in the PD as reported by it's designer.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 04:39.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi