#1
|
|||
|
|||
|
PID control: need D values > 10000??
We're using CANJaguar and PID control on our robot arm's shoulder joint. The arm is driven by a pair of highly-geared motors, with an encoder directly on the joint. We're having a very tough time getting the right values for PID, and need some help. Specifically, we feel we need some D to prevent oscillation and overshoot, but have had no success getting any value of D to work.
We've been testing different PID values using BDC-Comm, initially with motor power disconnected. We're trying out different values of P, I and D, and watching the motor output voltage as we move the arm. Our P and I experimentation gives us sensible results, but D seems almost non-functional. We test by setting P and I to zero, choosing a value for D, and the moving the arm and watching the motor voltage. Unless we set D above 10000 (yes, ten thousand) the BDC-Comm voltage display never budges from zero. The max value for D (at least in BDC-Comm) is 32767, so that seems really strange. BDC-Comm testing with motor connected shows that if I have all three terms set to 0, and stop action set to coast then the arm can easily be moved (obviously). I'd expect that I could then use a D value as a brake, resisting any motion. But, I have to bump my D value up to above 5000 before I get any braking action. If I set D to very negative (-10000) I get an apparent reduction in friction. Why does this require such enormous values of D? It's conceivable that if we could use a D of, say, 100000 we'd be fine, but that won't work in BDC-Comm, and even if they'd work in Java using weird values "because they work" doesn't seem like the right approach. Thanks, Dan Edit: I think I've found the answer, but my three posts to that effect have yet to show up, So, I'm trying this. Ether pointed me the right way: the problem is our counts-per-second. Arm moves 220 degrees max, directly coupled to a 360 degree per rotation encoder, so that's only 220 counts total. We want control of motions of a few degrees a second, or a few counts a second. Given the PID iteration time of a millisecond, that won't work (and is why D is totally ineffective; P and I are probably hampered as well.) Lesson: we gotta get more counts, probably moving the encoder to an intermediate shaft on our gearbox. Last edited by dtgriscom : 19-03-2012 at 12:28. Reason: Aren't being allowed to post to this thread |
|
#2
|
||||
|
||||
|
Re: PID control: need D values > 10000??
Have you tried using the Ziegler-Nichols Method for tuning your PID Controller? I'm not familiar with BDC-Comm. Did you write your own PID code?
|
|
#3
|
|||
|
|||
|
Re: PID control: need D values > 10000??
BDC-Comm is the TI tool for communicating over CAN bus directly to a Jaguar motor controller. No cRIO or Driver Station involved, which lets us try values quickly and without worrying about possible software bugs (at least outside the Jaguar).
We have a controls expert who was stymied at getting good PID control working due to the ineffective D term. I don't think it's our tuning procedure; it's either a bug in the Jaguar's firmware (which seems unlikely) or a problem in our understanding of the use of PID on the Jaguar (more likely). |
|
#4
|
||||
|
||||
|
Re: PID control: need D values > 10000??
According to this post, D is multiplied by the difference in error, not by the (difference in error)/(sample time). Since the PID in the Jag runs at 1000Hz, that factor of 1000 needs to be in your D gain. That's my guess.
What's the resolution (counts per degree) of your encoder, and how fast are you moving the arm (degrees per millisecond) when you're looking for a voltage? |
|
#5
|
|||||
|
|||||
|
Re: PID control: need D values > 10000??
Quote:
And I have a question. When you have a functioning system, what are your other values? Because it's possible that your P could be too low, as well. (but Ether's idea above me looks right, as well) |
|
#6
|
|||
|
|||
|
Re: PID control: need D values > 10000??
Quote:
Quote:
Our two motors drive Banebot 16:1 gearboxes, which are both plugged into a single 6:1 Andymark Toughbox driving the shoulder. Moving the encoder to the output of one of the Banebot gearboxes would cut the required D term by a factor of six, which might be enough. Moving the encoder to the shaft of one of the motors would be even better, but I don't think that's possible with our motors. Lesson: if you want reasonable PID control, you need to have a reasonable number of counts per second on your encoder. Thanks, all! Dan |
|
#7
|
||||
|
||||
|
Re: PID control: need D values > 10000??
The D (derivative) term helps to compensate for short term disturbances. Its effect decays over time. It can have a destabilizing influence on the loop. It is generally the last term to determined if it is used at all. Generally a properly tuned loop will have a little overshoot & oscillation decaying to 0 in 2-4 oscillations. I am not sure how you tune a loop without the load connected.
The jags use a 32 fixed point integer for the constants--16.16. one bit for sign, 15 bits lefts of the decimal point, 16 bit right of the decimal point. |
|
#8
|
||||
|
||||
|
Re: PID control: need D values > 10000??
I don't know much about the Jaguar/CAN PID implementation but I can tell you that your system will act very differently with the load attached. The control loop is electro-mechanical. The numbers you get w/o a load are nearly useless and perhaps why D has little or no effect.
HTH |
|
#9
|
||||
|
||||
|
Re: PID control: need D values > 10000??
My reading of the OP's post is that he is not trying to tune the system without a load. He is observing the effect of the P, I, and D gains in order to confirm that they do what he would expect. And he is questioning what he is observing. Quote:
|
|
#10
|
||||
|
||||
|
Re: PID control: need D values > 10000??
Quote:
|
|
#11
|
||||
|
||||
|
Re: PID control: need D values > 10000??
For a position PID, the D term looks at how fast the process variable is moving toward or away from the setpoint, and whether the process variable is above or below the setpoint. For a fixed setpoint, the effect of the D term on the PID output is such that it acts as a speed-dependent "brake" whenever the process variable is moving toward or away from the setpoint. |
|
#12
|
||||
|
||||
|
Re: PID control: need D values > 10000??
Quote:
I used to tune flow & pressure control loops. Admittedly the transfer function for a position or velocity loop might look different. I generally found the process measurement value to be noisy enough to make the derivative term useless. Obviously others have found it useful since it is a lot easier to find PID controllers rather than PI controllers. |
|
#13
|
||||
|
||||
|
Re: PID control: need D values > 10000??
Quote:
Quote:
![]() |
|
#14
|
|||
|
|||
|
Re: PID control: need D values > 10000??
Quote:
It is about as easy to make a generic PID controller as PI, and then the user has the option of setting the D term to zero, resulting in a PI controller. So, from a marketing point of view, it makes sense to make the PID controller whether most people use the D or not. |
|
#15
|
||||
|
||||
|
Re: PID control: need D values > 10000??
Quote:
Quote:
Here's an excerpt from the Jag firmware source code that I linked to in an earlier post: Code:
// Compute the new control value.
//
llOutput = (((long long)psState->lPGain * (long long)lError) +
((long long)psState->lIGain *
(long long)psState->lIntegrator) +
((long long)psState->lDGain *
(long long)(lError - psState->lPrevError)));
|
![]() |