No auto-resetting fuses on Spikes?
I thought I remember reading in years past that the general recommendation was to replace the standard 20A automotive fuse on the Spikes with the auto-resetting fuses we use everywhere else. I don't remember this violating any of the rules, yet <R65> and the Q&A this year say differently... was I incorrect in past years? I don't remember this only applying to the compressor.
https://frc-qa.usfirst.org/Question/...-solenoids-etc -Rob |
|
#2
|
||||
|
||||
|
Re: No auto-resetting fuses on Spikes?
Yes, you were incorrect in past years. At least for the past 6 seasons I've been involved with, this same rule has been in place.
|
|
#3
|
|||||
|
|||||
|
Re: No auto-resetting fuses on Spikes?
The only allowed use of a 20-amp breaker instead of a fuse has been for the air compressor.
This rule has been the same since at least 2006, and is only in place because the inrush current of the compressor can occasionally surge over 20 amps for a brief moment causing them to trip. |
|
#4
|
|||||
|
|||||
|
Re: No auto-resetting fuses on Spikes?
R60 in 2010 allowed the breaker on any Spike. We used window motors on Spikes with breakers without issue.
R55 in 2011 banned it again. This is another rule that really makes no sense. But, it is a rule. |
|
#5
|
|||
|
|||
|
Re: No auto-resetting fuses on Spikes?
The inrush current profile of a compressor is very different from that of a potentially stalled motor. The protection profile of a self reseting breaker is very different from that of a one time fuse. This isn't an arbitrary rule.
|
|
#6
|
|||
|
|||
|
Re: No auto-resetting fuses on Spikes?
Quote:
If you have a reset breaker in there, it will snap, reset, snap again, reset, over and over again, not providing proper circuit protection and causing something else more important to become the fuse, sometimes with frightening consequences. The use of the resetting breaker in the compressor is a concession suggested by, I believe, the manufacturer of the compressor. It has a high in-rush current on startup, but a much lower running current. Other motors don't have that characteristic. Dr. Bob Chairman's Award is not about building the robot. Every team builds a robot. |
|
#7
|
|||||
|
|||||
|
Re: No auto-resetting fuses on Spikes?
To me, it's like saying you can't use a CIM on a Victor because the stall current of a CIM is greater than the current rating of the Victor. The Victor can handle significantly more current for quite a while, longer than it will take for the breaker to trip.
The stall current for all of the Spike-legal motors is below or very slightly above 20a anyway, so it's irrelevant since the Spike can supply stall current indefinitely. The resetting breaker gives me more peace of mind that a one-time fuse, in terms of vehicle reliability and maintenance. |
|
#8
|
||||
|
||||
|
Re: No auto-resetting fuses on Spikes?
I have never understood why spikes have fuses. They are already current protected by the PD board with an auto resetting breaker. Furthermore, I have (outside of FIRST) used a spike to switch 40A+ with no issue. I personally like the idea of downgrading the auto resetter in the PD board to a 10A or 15A. At least this way the system will give you warning that a mechanism is drawing too much power with a temporary shut down rather than a "oh too bad, no more using that function for the rest of the match, better luck next time!" blown fuse.
|
|
#9
|
|||||
|
|||||
|
Re: No auto-resetting fuses on Spikes?
Quote:
The breakers are there and sized to protect the wiring from melting and bursting into flame, not the electrical components along that wiring. Electrical components must protect themselves, as their circuit designers are the only ones who know what the design limitations are. Wires are slow to burn components, but electronics are quick to fry components. The Snap-Action circuit breakers we use are slow to respond components to match wiring characteristics of slow to burn. Last edited by Mark McLeod : 05-02-2013 at 09:25. |
|
#10
|
|||||
|
|||||
|
Re: No auto-resetting fuses on Spikes?
Quote:
|
|
#11
|
|||||
|
|||||
|
Re: No auto-resetting fuses on Spikes?
Quote:
At stall, the breaker will trip between 3.9 and 47 seconds. The motor will certainly not last 47 seconds at stall. Spike specs: According to Vex Pro site Quote:
It's still like saying a Victor can't ever handle more than 60a (rated continuous current) so we can't connect a possibly larger load to it. The Spike will live with a 20a breaker and any Spike-legal motors. The 20a breaker will still trip if the wire shorts, which could already happen with a 20a breaker in a Spike for the pump. |
|
#12
|
|||||
|
|||||
|
Re: No auto-resetting fuses on Spikes?
Right, but the motor can operate between 20A-<30A, above the spikes continuous rating. Potentially up to 47 seconds with the snap action breaker.
|
|
#13
|
|||||
|
|||||
|
Re: No auto-resetting fuses on Spikes?
Quote:
-40a continuous -60a for up to 2s -100a for up to 0.2s At 60a, the 40a snap action MX5 will trip between 3.9 and 47 seconds. According to the Jaguar's spec, it has exceeded its spec limit before the best-case breaker trip. So maybe we shouldn't use Jaguars, because we can pull more current with a CIM than they are rated for before the breaker will trip? The point is that, in our use-case, it is reasonable to exceed the continuous current ratings for a short period of time. The Spike also has the highest relative current rating of any FRC-legal controller. |
|
#14
|
|||||
|
|||||
|
Re: No auto-resetting fuses on Spikes?
Quote:
I agree with that but unfortunately the rules are the rules. I'm also curious to know how those 20A snap actions typically behave above 20A. The data sheet gives a huge range... |
|
#15
|
|||
|
|||
|
Re: No auto-resetting fuses on Spikes?
the robot moves with the safety enabled. And when the joystick moves forward and back one light is green the other red. When turning left both lights are red and when turning right both lights are green. They were a solid Orange when enabled but not moving. The lights still flash orange when not enabled. Is that okay?
Otherwise I would like to thank everyone for there help in fixing the problem! |
![]() |