hi,
our team has almost a day left before we put the robot in a box and ship it out so please answer quick. we have programmed and wired correctly the 2 double solenoids that we are using, the lights changed from side to side (like their suppose to), and the the pneumatic pistons have pressure in them. But when we push the buttons to go down and up the pistons do not change. please help thanx |
|
#2
|
||||
|
||||
|
Re: Solenoid problems
Do the lights on the solenoid breakout board (on the cRio) change along with the ones of the valves?
|
|
#3
|
||||
|
||||
|
Re: Solenoid problems
yes, they do change at the same time the valves do.
|
|
#4
|
|||||
|
|||||
|
Re: Solenoid problems
|
|
#5
|
||||
|
||||
|
Re: Solenoid problems
1. they are 24v
2. they are wired 24v 3. yes it is bright green 4. it is two pin ports 5. and yes they are red out side and black inside |
|
#6
|
||||
|
||||
|
Re: Solenoid problems
the solenoid break out is actually 12vs... ops found the problem but how do we fix that?
|
|
#7
|
|||||
|
|||||
|
Re: Solenoid problems
Someone else just asked that earlier today--use the open slots in the 24V port the cRIO connects to. I believe they're C and NC, can't quite remember which wire goes to which.
|
|
#8
|
|||||
|
|||||
|
Re: Solenoid problems
The PDB datasheet suggests the terminals go +-+-. Best bet is to check with a voltmeter, though.
|
|
#9
|
||||
|
||||
|
Re: Solenoid problems
Thank you for all your help!
Now it is time to put the robot in the box! |
|
#10
|
|||||
|
|||||
|
Re: Solenoid problems
What do you mean?
We have two whole hours left. Enough time for a redesign... ![]() |
![]() |