Power Distibution Board - Broken stud
Our 2013 power distribution boards stud broke on the first usage BEFORE the nut was even tight (power cable still loose on stud). It was installed by a multi-year seasoned electrical guy. Yes it was the correct original metric nut. I presume there is no warranty. Thats 3 power distributions boards we have with damaged or broken studs. Thats $570 of not usable in the competition boards and I suspect a minimum of one out of every two boards we own.
If we are in that situation, chances are a lot of other teams are. So there could a thousand or more of these boards in this condition in the FIRST community. I do know the apparent reason the boards use a brass metric stud / pcb mount is there is not US equivalent. And its brass so it can be soldered to the PCB and handle the high currents. But with an ongoing 50% failure/damage rate we are seeing, its time for FIRST to work harder for a solution that will have a reasonable MTBF in the FIRST environment. We have in past cut the studs off, drilled and tapped the brass block for a 1/4" steel bolt which seems work fine and handle the 120amp max current without any issues. Too bad FIRST will not allow its usage in the competitions. Our 2013 Digital Side car was DOA this year so between the two boards thats over $350 after taxes and shipping we have to spend to replace the boards which both had a MTBF of 0 minutes apparently with no warranty. |
|
#2
|
||||
|
||||
|
Re: Power Distibution Board - Broken stud
Quote:
|
|
#3
|
||||
|
||||
|
Re: Power Distibution Board - Broken stud
The PDB was introduced in 2009 for Lunacy, if I remember correctly. Since then, we've only had to buy one replacement a couple of years ago, for a board that got burned out after being mis-wired. We've never had any of the studs on our boards break off.
Now, for our story this year on a broken PDB: This year, we're using an old board. About 4PM the day we bagged the robot one of our mechanical guys wanted to run a motor manually - we have a rig set up that allows us to safely (this part can't be emphasized enough for teams that want to do something similar!) do this with our Anderson PowerPole connectors, and it even has variable speed control! Anyways, when the mentor went to power the motor, he plugged into the wrong side of the PowerPole connectors, feeding 12V into the PDB through the Wago connectors while the robot was turned off. When they powered on the robot, there were a lot of red LEDs on the PDB and stuff didn't work. While all this was happening, I was in the car heading to the build space from work. I got a phone call from the guilty mentor that started with "I think I did something very bad..." After getting the full description of what he was seeing, I told him the board needed to be replaced with one of our old "spares". Seemingly at the same time, the electrical team came to the same conclusion after doing some searching on CD. So, take this lesson to heart: mechanical mentors should never touch anything electrical! Anyways, what I'm getting at is you're seeing a 50% failure rate, but most teams aren't. My team hasn't seen any failures that we didn't directly cause through misuse. If there really were that many failures of the studs across all FIRST teams, we would have heard a lot more about it than the occasional breakage we hear about now. |
|
#4
|
||||
|
||||
|
Re: Power Distibution Board - Broken stud
I talked to a representative from Total Electronics at worlds last year. He seemed to be a stand up guy. If the issue really is a defective part & not operator error. (I do not judge these things over the internet
) I expect they will stand behind it.I have found AndyMark as well to stand behind their products. Last edited by FrankJ : 26-02-2013 at 15:22. |
|
#5
|
|||||
|
|||||
|
Re: Power Distibution Board - Broken stud
Quote:
My sample and yours have greatly different qualities. Is there any way we can get a reliable survey of PDB breakage across all of FRC? |
|
#6
|
|||
|
|||
|
Re: Power Distibution Board - Broken stud
Quote:
That said, this really does sound like user error to me. |
|
#7
|
|||||
|
|||||
|
Re: Power Distibution Board - Broken stud
We have every PD board we have ever received and they are all still completely functional, including a prototype board. In all the time FIRST has used these boards I have never seen a broken stud that wasn't from OE.
|
|
#8
|
|||
|
|||
|
Re: Power Distibution Board - Broken stud
If you only install 1 board a year and a mentor does it as opposed to a random student, then sure you are less likely to have a problem.
But in our team, random students installed at least 5 boards on various desktop and test & competition robots this year alone (many when I am not there). What is the probability a student will realize the stub is brass and its tensile strength is 19K PSI versus the grade 8 fasteners we use which is 150K psi. Zero. We don't teach metallurgy in our high school. We don't own a torque wrench. What student could possibly recognize the metric nuts Zero - looks just like a 1/4 nut. Standard 1/4" 20 nut fits on the stud and tries quite happily to cut a thread into the soft brass. That is how a student trashed our first PDE. This is a $190 hidden mine waiting to explode, especially in a dynamic high student to mentor ratio environment. Count your self lucky if you have not had it happen yet. The particular student in this case has install a lot of PDEs over the years. He's installed a lot of brass pneumatic fittings in aluminum with no issues. He has no history of brute force. He used a small wrench. So don't blame the student. Our robot is probably 50% over budget this year and now we should be buying a new PDE and a new Digital side cars as both did not survive even a minute in our student environment. Is it the students fault or is it a design fault? I can't find fault with the students. What I will do between trying to get a robot built and buying replacement parts is try to find the time to make a warning label for future PDEs that warns the studs are brass and metric and will break 7.5 times easier than a grade 8 bolt. Something FIRST might consider. I will also send a link of this post to FIRST. |
|
#9
|
||||
|
||||
|
Re: Power Distibution Board - Broken stud
Quote:
|
|
#10
|
|||
|
|||
|
Re: Power Distibution Board - Broken stud
Its not student training: The last one broke with a well trained student. We will not get a better student.
|
|
#11
|
||||
|
||||
|
Re: Power Distibution Board - Broken stud
|
|
#12
|
|||
|
|||
|
Re: Power Distibution Board - Broken stud
Kevin, Where are you getting your data re other teams experiences re the stud ? Have you surveyed them ?
I have already stated I know exactly why how the current PDE ended up as is. So don't go there. I can tell you 0 studs failed on the previous design (that was a $30 part). They were not brass. |
|
#13
|
|||||
|
|||||
|
Re: Power Distibution Board - Broken stud
Quote:
|
|
#14
|
||||
|
||||
|
Re: Power Distibution Board - Broken stud
Here is a data point: We have six of these boards on various robots. We have one a broken stud. Relatively untrained student screwed on a 1/4-20 nut with an experienced mentor looking over her shoulder. Definitely operator error in our case.
We are now powering that PD board through a Wago connector for a test bed. Last edited by FrankJ : 27-02-2013 at 13:57. |
|
#15
|
||||
|
||||
|
Re: Power Distibution Board - Broken stud
So where did it fail? Is it at the button of the stud where it transitions to the square? Does the nut turn freely on the stud? Was the stud bent or the threads damaged?
You are never going to get a grade 8 fastener in this application. You can teach the difference without going into metallurgy. Occasionally even the best of us make mistakes. I would like to say it wasn't so. ![]() |
![]() |