Power Distibution Board - Broken stud

Our 2013 power distribution boards stud broke on the first usage BEFORE the nut was even tight (power cable still loose on stud). It was installed by a multi-year seasoned electrical guy. Yes it was the correct original metric nut. I presume there is no warranty. Thats 3 power distributions boards we have with damaged or broken studs. Thats $570 of not usable in the competition boards and I suspect a minimum of one out of every two boards we own.

If we are in that situation, chances are a lot of other teams are. So there could a thousand or more of these boards in this condition in the FIRST community. I do know the apparent reason the boards use a brass metric stud / pcb mount is there is not US equivalent. And its brass so it can be soldered to the PCB and handle the high currents. But with an ongoing 50% failure/damage rate we are seeing, its time for FIRST to work harder for a solution that will have a reasonable MTBF in the FIRST environment.

We have in past cut the studs off, drilled and tapped the brass block for a 1/4" steel bolt which seems work fine and handle the 120amp max current without any issues. Too bad FIRST will not allow its usage in the competitions.

Our 2013 Digital Side car was DOA this year so between the two boards thats over $350 after taxes and shipping we have to spend to replace the boards which both had a MTBF of 0 minutes apparently with no warranty.
Reply With Quote
  #2   Spotlight this post!  
Unread 26-02-2013, 15:06
Ether's Avatar
Ether Ether is offline
systems engineer (retired)
no team
 
Join Date: Nov 2009
Rookie Year: 1969
Location: US
Posts: 8,024
Ether has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond repute
Re: Power Distibution Board - Broken stud

Quote:
Originally Posted by de_ View Post
Our 2013 power distribution boards stud broke on the first usage BEFORE the nut was even tight (power cable still loose on stud). It was installed by a multi-year seasoned electrical guy. Yes it was the correct original metric nut.
Not meant to be argumentative, just wondering: was he using a torque wrench when this happened?


Reply With Quote
  #3   Spotlight this post!  
Unread 26-02-2013, 15:26
Jon Stratis's Avatar
Jon Stratis Jon Stratis is offline
Electrical/Programming Mentor
FRC #2177 (The Robettes)
Team Role: Mentor
 
Join Date: Feb 2007
Rookie Year: 2006
Location: Minnesota
Posts: 3,735
Jon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond repute
Re: Power Distibution Board - Broken stud

The PDB was introduced in 2009 for Lunacy, if I remember correctly. Since then, we've only had to buy one replacement a couple of years ago, for a board that got burned out after being mis-wired. We've never had any of the studs on our boards break off.

Now, for our story this year on a broken PDB:

This year, we're using an old board. About 4PM the day we bagged the robot one of our mechanical guys wanted to run a motor manually - we have a rig set up that allows us to safely (this part can't be emphasized enough for teams that want to do something similar!) do this with our Anderson PowerPole connectors, and it even has variable speed control! Anyways, when the mentor went to power the motor, he plugged into the wrong side of the PowerPole connectors, feeding 12V into the PDB through the Wago connectors while the robot was turned off. When they powered on the robot, there were a lot of red LEDs on the PDB and stuff didn't work.

While all this was happening, I was in the car heading to the build space from work. I got a phone call from the guilty mentor that started with "I think I did something very bad..." After getting the full description of what he was seeing, I told him the board needed to be replaced with one of our old "spares". Seemingly at the same time, the electrical team came to the same conclusion after doing some searching on CD.

So, take this lesson to heart: mechanical mentors should never touch anything electrical!


Anyways, what I'm getting at is you're seeing a 50% failure rate, but most teams aren't. My team hasn't seen any failures that we didn't directly cause through misuse. If there really were that many failures of the studs across all FIRST teams, we would have heard a lot more about it than the occasional breakage we hear about now.
__________________
2007 - Present: Mentor, 2177 The Robettes
LRI: North Star 2012-2016; Lake Superior 2013-2014; MN State Tournament 2013-2014, 2016; Galileo 2016; Iowa 2017
2015: North Star Regional Volunteer of the Year
2016: Lake Superior WFFA
Reply With Quote
  #4   Spotlight this post!  
Unread 26-02-2013, 15:13
FrankJ's Avatar
FrankJ FrankJ is offline
Robot Mentor
FRC #2974 (WALT)
Team Role: Mentor
 
Join Date: Feb 2011
Rookie Year: 2009
Location: Marietta GA
Posts: 1,899
FrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond repute
Re: Power Distibution Board - Broken stud

I talked to a representative from Total Electronics at worlds last year. He seemed to be a stand up guy. If the issue really is a defective part & not operator error. (I do not judge these things over the internet ) I expect they will stand behind it.

I have found AndyMark as well to stand behind their products.

Last edited by FrankJ : 26-02-2013 at 15:22.
Reply With Quote
  #5   Spotlight this post!  
Unread 26-02-2013, 15:39
Alan Anderson's Avatar
Alan Anderson Alan Anderson is offline
Software Architect
FRC #0045 (TechnoKats)
Team Role: Mentor
 
Join Date: Feb 2004
Rookie Year: 2004
Location: Kokomo, Indiana
Posts: 9,112
Alan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond repute
Re: Power Distibution Board - Broken stud

Quote:
Originally Posted by de_ View Post
Thats 3 power distributions boards we have with damaged or broken studs. Thats $570 of not usable in the competition boards and I suspect a minimum of one out of every two boards we own.

If we are in that situation, chances are a lot of other teams are.
The other possibility is that your team simply doesn't understand how to tighten the nuts properly. I have first-hand experience with only two broken PDB studs out of literally hundreds of boards, one caused by an unsupervised and untutored student cranking down the nut too hard, and the other caused by a cross-threaded nut being overtorqued when it was obviously stuck. I have heard of fewer than a dozen in the history of this control system, including your three.

My sample and yours have greatly different qualities. Is there any way we can get a reliable survey of PDB breakage across all of FRC?
Reply With Quote
  #6   Spotlight this post!  
Unread 26-02-2013, 16:05
EricVanWyk EricVanWyk is offline
Registered User
no team
 
Join Date: Jan 2007
Rookie Year: 2000
Location: Boston
Posts: 1,597
EricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond reputeEricVanWyk has a reputation beyond repute
Send a message via AIM to EricVanWyk
Re: Power Distibution Board - Broken stud

Quote:
Originally Posted by Alan Anderson View Post
Is there any way we can get a reliable survey of PDB breakage across all of FRC?
The single hardest part of my job is that I have no way of knowing about errors that go unreported. The worst feeling is finding out that there was a fixable issue that has gone unresolved because of lack of information.


That said, this really does sound like user error to me.
Reply With Quote
  #7   Spotlight this post!  
Unread 26-02-2013, 16:23
IndySam's Avatar
IndySam IndySam is offline
Registered User
FRC #0829 (Digital Goats)
Team Role: Mentor
 
Join Date: Nov 2005
Rookie Year: 2004
Location: Indy
Posts: 3,347
IndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond reputeIndySam has a reputation beyond repute
Re: Power Distibution Board - Broken stud

We have every PD board we have ever received and they are all still completely functional, including a prototype board. In all the time FIRST has used these boards I have never seen a broken stud that wasn't from OE.
__________________
"Champions are champions not because they do anything extraordinary but because they do the ordinary things better than anyone else." —Chuck Knoll


2015 Indianapolis District Winner
2014 Boilermaker Regional Industrial Design Award
2013 Smoky Mountain Regional Industrial Design Award
2012 Boilermaker Engineering Excellence Award
2010 Boilermaker Rockwell Innovation in Control Award.
2009 Buckeye J&J Gracious Professionalism Award
2009 Boilermaker J&J Gracious Professionalism Award
2008 Boilermaker J&J Gracious Professionalism Award
2007 St Louis Regional Winners
Reply With Quote
  #8   Spotlight this post!  
Unread 27-02-2013, 11:25
de_ de_ is offline
Registered User
AKA: Dave Edwards
FRC #1310 (Runnymede Robotics)
Team Role: Mentor
 
Join Date: Apr 2005
Rookie Year: 2005
Location: Toronto, Ontario
Posts: 256
de_ is a jewel in the roughde_ is a jewel in the roughde_ is a jewel in the roughde_ is a jewel in the rough
Re: Power Distibution Board - Broken stud

If you only install 1 board a year and a mentor does it as opposed to a random student, then sure you are less likely to have a problem.

But in our team, random students installed at least 5 boards on various desktop and test & competition robots this year alone (many when I am not there).

What is the probability a student will realize the stub is brass and its tensile strength is 19K PSI versus the grade 8 fasteners we use which is 150K psi. Zero. We don't teach metallurgy in our high school. We don't own a torque wrench. What student could possibly recognize the metric nuts Zero - looks just like a 1/4 nut. Standard 1/4" 20 nut fits on the stud and tries quite happily to cut a thread into the soft brass. That is how a student trashed our first PDE.

This is a $190 hidden mine waiting to explode, especially in a dynamic high student to mentor ratio environment. Count your self lucky if you have not had it happen yet.

The particular student in this case has install a lot of PDEs over the years. He's installed a lot of brass pneumatic fittings in aluminum with no issues. He has no history of brute force. He used a small wrench. So don't blame the student.

Our robot is probably 50% over budget this year and now we should be buying a new PDE and a new Digital side cars as both did not survive even a minute in our student environment. Is it the students fault or is it a design fault? I can't find fault with the students.

What I will do between trying to get a robot built and buying replacement parts is try to find the time to make a warning label for future PDEs that warns the studs are brass and metric and will break 7.5 times easier than a grade 8 bolt. Something FIRST might consider. I will also send a link of this post to FIRST.
Reply With Quote
  #9   Spotlight this post!  
Unread 27-02-2013, 11:54
Jon Stratis's Avatar
Jon Stratis Jon Stratis is offline
Electrical/Programming Mentor
FRC #2177 (The Robettes)
Team Role: Mentor
 
Join Date: Feb 2007
Rookie Year: 2006
Location: Minnesota
Posts: 3,735
Jon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond repute
Re: Power Distibution Board - Broken stud

Quote:
Originally Posted by de_ View Post
If you only install 1 board a year and a mentor does it as opposed to a random student, then sure you are less likely to have a problem.

But in our team, random students installed at least 5 boards on various desktop and test & competition robots this year alone (many when I am not there).

What is the probability a student will realize the stub is brass and its tensile strength is 19K PSI versus the grade 8 fasteners we use which is 150K psi. Zero. We don't teach metallurgy in our high school. We don't own a torque wrench. What student could possibly recognize the metric nuts Zero - looks just like a 1/4 nut. Standard 1/4" 20 nut fits on the stud and tries quite happily to cut a thread into the soft brass. That is how a student trashed our first PDE.

This is a $190 hidden mine waiting to explode, especially in a dynamic high student to mentor ratio environment. Count your self lucky if you have not had it happen yet.

The particular student in this case has install a lot of PDEs over the years. He's installed a lot of brass pneumatic fittings in aluminum with no issues. He has no history of brute force. He used a small wrench. So don't blame the student.

Our robot is probably 50% over budget this year and now we should be buying a new PDE and a new Digital side cars as both did not survive even a minute in our student environment. Is it the students fault or is it a design fault? I can't find fault with the students.

What I will do between trying to get a robot built and buying replacement parts is try to find the time to make a warning label for future PDEs that warns the studs are brass and metric and will break 7.5 times easier than a grade 8 bolt. Something FIRST might consider. I will also send a link of this post to FIRST.
It really comes down to student training. You don't have to go into too much detail or talk about metallurgy. We have a small bag in our electrical kit labeled "PDB Nuts" with spares of the correct nuts in it. The students on the electrical team know its there, and we make it a talking point every year that it takes different nuts than the rest of the robot. When we go over all of the electrical components, we stress that they need to make things tight, but they can't crank down on them like they would on frame members - plastic will crack, and even if it doesn't it will compress and damage circuitry. Our students do all the install work for us, and we have never had a problem. We typically install 2-4 of them each year, as part of practice robots, demo's, bench-top test boards, etc.
__________________
2007 - Present: Mentor, 2177 The Robettes
LRI: North Star 2012-2016; Lake Superior 2013-2014; MN State Tournament 2013-2014, 2016; Galileo 2016; Iowa 2017
2015: North Star Regional Volunteer of the Year
2016: Lake Superior WFFA
Reply With Quote
  #10   Spotlight this post!  
Unread 27-02-2013, 12:18
de_ de_ is offline
Registered User
AKA: Dave Edwards
FRC #1310 (Runnymede Robotics)
Team Role: Mentor
 
Join Date: Apr 2005
Rookie Year: 2005
Location: Toronto, Ontario
Posts: 256
de_ is a jewel in the roughde_ is a jewel in the roughde_ is a jewel in the roughde_ is a jewel in the rough
Re: Power Distibution Board - Broken stud

Its not student training: The last one broke with a well trained student. We will not get a better student.
Reply With Quote
  #11   Spotlight this post!  
Unread 27-02-2013, 13:06
Ether's Avatar
Ether Ether is offline
systems engineer (retired)
no team
 
Join Date: Nov 2009
Rookie Year: 1969
Location: US
Posts: 8,024
Ether has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond repute
Re: Power Distibution Board - Broken stud


http://www.chiefdelphi.com/forums/sh...90#post1240690

Are these two problems related?


Reply With Quote
  #12   Spotlight this post!  
Unread 27-02-2013, 13:15
de_ de_ is offline
Registered User
AKA: Dave Edwards
FRC #1310 (Runnymede Robotics)
Team Role: Mentor
 
Join Date: Apr 2005
Rookie Year: 2005
Location: Toronto, Ontario
Posts: 256
de_ is a jewel in the roughde_ is a jewel in the roughde_ is a jewel in the roughde_ is a jewel in the rough
Re: Power Distibution Board - Broken stud

Kevin, Where are you getting your data re other teams experiences re the stud ? Have you surveyed them ?

I have already stated I know exactly why how the current PDE ended up as is. So don't go there.

I can tell you 0 studs failed on the previous design (that was a $30 part). They were not brass.
Reply With Quote
  #13   Spotlight this post!  
Unread 27-02-2013, 13:49
Kevin Sevcik's Avatar
Kevin Sevcik Kevin Sevcik is online now
(Insert witty comment here)
FRC #0057 (The Leopards)
Team Role: Mentor
 
Join Date: Jun 2001
Rookie Year: 1998
Location: Houston, Texas
Posts: 3,597
Kevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond reputeKevin Sevcik has a reputation beyond repute
Send a message via AIM to Kevin Sevcik Send a message via Yahoo to Kevin Sevcik
Re: Power Distibution Board - Broken stud

Quote:
Originally Posted by de_ View Post
Kevin, Where are you getting your data re other teams experiences re the stud ? Have you surveyed them ?

I have already stated I know exactly why how the current PDE ended up as is. So don't go there.

I can tell you 0 studs failed on the previous design (that was a $30 part). They were not brass.
Nothing scientific, just subjective impression based off the teams I work with here in Texas, and the lack of outcry on CD. If it was a very common problem, you'd see a lot more about it here. Look at the kerfuffle on the BAG Motors. By Paul Copioli's count, it's something that's affecting a very small percentage of motors, but there's several teams on here talking about it.
__________________
The difficult we do today; the impossible we do tomorrow. Miracles by appointment only.

Lone Star Regional Troubleshooter
Reply With Quote
  #14   Spotlight this post!  
Unread 27-02-2013, 13:55
FrankJ's Avatar
FrankJ FrankJ is offline
Robot Mentor
FRC #2974 (WALT)
Team Role: Mentor
 
Join Date: Feb 2011
Rookie Year: 2009
Location: Marietta GA
Posts: 1,899
FrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond repute
Re: Power Distibution Board - Broken stud

Here is a data point: We have six of these boards on various robots. We have one a broken stud. Relatively untrained student screwed on a 1/4-20 nut with an experienced mentor looking over her shoulder. Definitely operator error in our case.

We are now powering that PD board through a Wago connector for a test bed.

Last edited by FrankJ : 27-02-2013 at 13:57.
Reply With Quote
  #15   Spotlight this post!  
Unread 27-02-2013, 13:42
FrankJ's Avatar
FrankJ FrankJ is offline
Robot Mentor
FRC #2974 (WALT)
Team Role: Mentor
 
Join Date: Feb 2011
Rookie Year: 2009
Location: Marietta GA
Posts: 1,899
FrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond repute
Re: Power Distibution Board - Broken stud

So where did it fail? Is it at the button of the stud where it transitions to the square? Does the nut turn freely on the stud? Was the stud bent or the threads damaged?

You are never going to get a grade 8 fastener in this application. You can teach the difference without going into metallurgy.

Occasionally even the best of us make mistakes. I would like to say it wasn't so.
Reply With Quote
Reply


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 19:10.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi