Voltage Regulator
Does anybody know if it is within the rules to use a voltage regulator on the robot between the battery and the controller to prevent the controller from automatically powering down if the supply voltage is under 7.5V?
|
|
#2
|
||||||
|
||||||
|
Re: Voltage Regulator
Quote:
It is not legal to connect a custom circuit to the power input of the robot controller anyway. |
|
#3
|
||||
|
||||
|
Re: Voltage Regulator
Quote:
ok, thanks, that's what i was wondering about mainly, the custom circuit. And yes i am aware that the backup battery will take over, but it seems that the controller tends to power off before it switches to the backup battery. Well, i guess i'm only talking about when we are drawing a significant amount of current from the battery and the voltage temporarily drops. If the voltage drops slowly the backup battery works then. Last edited by Robby : 17-01-2005 at 22:36. |
|
#4
|
||||
|
||||
|
Re: Voltage Regulator
Quote:
Secondly, you have a backup battery connector on the RC which is intended to serve this purpose. Connect a 7.2 V battery (such as the one from the Robovation kit) to the RC, and it will power it, even if the main battery is depleted. |
|
#5
|
||||
|
||||
|
Re: Voltage Regulator
Quote:
You should do this experiment. power up your robot with both a 12V and the 7.2V battery installed. Now disconnect the 12V. Your controller will continue to operate until you either disconnect the 7.2V battery OR press the RC reset button. You do not need a regulator. |
|
#6
|
|||||
|
|||||
|
Re: Voltage Regulator
Robby,
In reality there is an internal regulator built into the controller. If you are drawing significant currents and drawing the voltage down so far that the backup battery takes over, you have some other problems to correct. The controller switch is just a symptom of a bigger problem. It might be as simple as a loose connector on the battery or a poorly made crimp on the wires feeding the controller. But it could be something wrong in you mechanical systems. Find the cause and fix it. |
![]() |
| Thread Tools | |
| Display Modes | Rate This Thread |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Victors Non-linear!!! | Rickertsen2 | Control System | 63 | 08-01-2005 00:42 |
| voltage regulators vs. speed controlers | Greg Needel | Electrical | 8 | 06-08-2004 23:31 |
| Voltage on Frame | Greg | Electrical | 31 | 02-03-2004 13:49 |
| RC Circuits | Melissa Nute | Math and Science | 3 | 25-01-2004 05:02 |
| Output voltage in PBASIC | diego25 | Programming | 7 | 31-01-2002 22:50 |