Problems With The Power Distribution Block
I'm sorry, but that Rockwell Disribution block has just GOT to go, or at least not be made mandatory. I'm sure it is a fine product, but just not in this application. For the sake of Rockwell's good name, I think it needs to keep it's home in its intended application. Bare wires screwed into terminals just doesn't work in FIRST. And the size and weight doesn't either. I inspected at two regionals. I couldn't find any team that was glad to have it. Most teams expressed their frustration with being required to use it.
Additionally, my team experienced the wires continually loosening and falling out of it, and the electrical engineers on the team also express their concerns with this item in the kit of parts. So, for everyone else replying to this thread, I know you don't like the thing. But, please state the specific problems it has caused for you. Last edited by sanddrag : 26-03-2007 at 01:00. |
|
#2
|
|||
|
|||
|
Re: FIRST, if you listen to one suggestion this year, let it be this one
One of the screws in the center coupler (little yellow thing) of the ground distribution wiggled loose during competition. Well, apparently when we started pushing the bot to its limit, a spark gap was created between the coupler and the block, causing both to melt. No fun.
|
|
#3
|
||||
|
||||
|
Re: FIRST, if you listen to one suggestion this year, let it be this one
Everyone knew about this issue a while ago. A little Loctite will fix the problem.
|
|
#4
|
|||
|
|||
|
Re: FIRST, if you listen to one suggestion this year, let it be this one
Everyone? I'm pretty sure I didnt. And what about the rooks who don't even know what Loctite is?
|
|
#5
|
|||
|
|||
|
Re: FIRST, if you listen to one suggestion this year, let it be this one
I thought loctite ate plastic, so, I didn't go for it. Is this a different type of plastic that it doesn't eat?
|
|
#6
|
|||||
|
|||||
|
Re: FIRST, if you listen to one suggestion this year, let it be this one
While we're talking about electrical stuff...
I am a big fan of the 2005 Power Distribution Block Thing made by IFI. I would love to see them return to bring simplicity back to robots' electrical systems. I helped wire two rookie robots in the pits at Boston on Thursday, and having that single block would have made things easier, and simpler for the rookie teams to understand. |
|
#7
|
|||
|
|||
|
Re: FIRST, if you listen to one suggestion this year, let it be this one
Our main problem with it was one that was already pointed out: that the wires continued to slip out, as tightly as I or any other member or mentor screwed the screw in. If FIRST intends to continue with this power distribution block, I would suggest that they give us tips on how to keep those wires in.
|
|
#8
|
|||||
|
|||||
|
Re: FIRST, if you listen to one suggestion this year, let it be this one
Quote:
And I know there are plenty other threads concerning this but while I already went off the topic already for all those who are wondering if the RC will change - Also coming from the horses mouth (IFI) more than likely......... not. They are happy with its current size and dimensions and why change something that works perfectly. However when ever the ancient DB9 Port is completely extinct then start looking for a new RC configuration but until then don't hold your breath =). While Loctite is a good answer to keeping almost any screw in place I would not use a whole lot of it b/c like many have said it will need to be taken apart someday. I'm pretty sure they're other solutions out there. Maybe instead of using Loctite do some test with some crazy glue. While it's not strong enough as loctite it should get the job done and be able to be undone with just a little bit of heat. Last edited by mtaman02 : 26-03-2007 at 07:21. |
|
#9
|
|||
|
|||
|
Re: FIRST, if you listen to one suggestion this year, let it be this one
Quote:
Do they make a dip tank full of loctite that we can submerge our whole robot in? I was not aware of this problem. I don't recall this being in any of the team updates. I get a little concerned using loctite for this application. Even though we use blue loctite... we someday might need to take this apart! |
|
#10
|
||||
|
||||
|
Re: FIRST, if you listen to one suggestion this year, let it be this one
Quote:
Secondly, be very careful about reccomending loctite. Know your application and the type of loctite so that you can guage the reaction. Test on a sample (NOT ON THE ROBOT) to ensure compatability. *note* I believe that Loctite is a good idea for this application, but please make sure that the type of loctite you use is compatable with the plastics and vynal wire coverings. |
|
#11
|
|||||
|
|||||
|
Re: FIRST, if you listen to one suggestion this year, let it be this one
At Bayou, we checked our wires on and we ended up putting in some Loctite. I was against it, but after a mentor showed me how loose some of the wires were I said anything was better than nothing, and so we gave it a go. Well, none of the wires popped out to my knowledge and the drive team didn't have to tighten them after we put in the Loctite so I was satisfied. It works...but I'll get to do a better electrical inspection come Thursday at Lone Star and be even more sure!
Do I see it as necessary? No, but FIRST has their reasons I assume and now I know about ferrules and have all summer to think of new ways to keep wires in! Make this your off season project if you don't have one and than you won't have to worry about how to make wires stay in tight next year. Pavan. |
|
#12
|
|||||
|
|||||
|
Re: FIRST, if you listen to one suggestion this year, let it be this one
Quote:
-Danny |
|
#13
|
|||
|
|||
|
Re: Problems With The Power Distribution Block
I know that some manufacturers of similar power distribution blocks (not sure about Rockwell--I haven't spent enough time looking) have spring loaded connectors that may be more suitable for our applications. At least that way the vibration wouldn't loosen the screws and let the wires fall out.
|
|
#14
|
|||||
|
|||||
|
Re: Problems With The Power Distribution Block
The spec sheet for the terminal blocks suggests tightening the screws that hold the wires in, to 17 to 35 lb-in torque. That's a lot of torque to apply with a slot screwdriver! Maybe what's needed is to make sure someone with strong hands tightens the connections.
Also double check the wires are stripped the minimum 5/8" length. Having a checklist to double check the tightness of the screws before competition, is a good idea. Last edited by MrForbes : 27-03-2007 at 12:47. Reason: not too tight! |
|
#15
|
|||||
|
|||||
|
Re: Problems With The Power Distribution Block
Quote:
|
![]() |
| Thread Tools | |
| Display Modes | Rate This Thread |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Power Distribution Block Grounding | Karma | Electrical | 15 | 22-01-2008 07:18 |
| Question:Power Distribution Block | Pavan Dave | Electrical | 35 | 20-03-2007 20:10 |
| Power distribution Block? | Pontchartrain | Electrical | 3 | 27-01-2006 07:30 |
| Stinger Fuse Block and Power Distribution Block | Don Wright | Electrical | 2 | 30-03-2004 10:45 |
| Power Distribution Block | DukesElectrical | General Forum | 0 | 09-02-2004 23:48 |