#1
|
|||
|
|||
|
Spike Relay Double Solenoid
We are using LabView 8.6 and we are trying to program an SMC double Solenoid connected to a Spike relay. We have programmed a single relay but it does not work for our double solenoid. Only our single solenoid. We've connected both red wires of the double solenoid to the M+ and the M- of the Spike relay. How can we adjust our code so it works with a double solenoid?
![]() -Thank you in advance ![]() |
|
#2
|
|||
|
|||
|
Re: Spike Relay Double Solenoid
Here is the link to the IFI documentation for the spike. See the two solenoid wiring example to check your wiring.
http://content.vexrobotics.com/docs/...uide-sep05.pdf Set relay forward momentarily to switch to one position. Set relay reverse momentarily to switch to other position. Valve will maintain position without power. Other points: Dual solenoid valves must have air pressure applied to move the spool in the valve This years KOP the dual solenoid valve is 24V, check documentation about this. Spike is designed for 12v so you will have to us the NI solenoid driver card with special 24v wiring to use this years valve. |
|
#3
|
|||||
|
|||||
|
Re: Spike Relay Double Solenoid
What does the True case for the Relay Set have in it (should be "Forward")?
|
![]() |
| Thread Tools | |
| Display Modes | Rate This Thread |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| How to connect the 12v solenoid to the cRIO and spike relay? | hannigan | Pneumatics | 3 | 13-02-2010 09:21 |
| Relay (Spike) | elbuo | Electrical | 2 | 09-02-2009 20:36 |
| Spike relay question | Zack Briggs | Electrical | 17 | 19-02-2008 14:48 |
| Pneumatics (Spike Relay, Solenoid etc.) Programming | oceansidehs | Programming | 8 | 10-02-2007 13:58 |
| Spike Relay Input | nwagers | Electrical | 3 | 16-07-2002 22:23 |