30a breaker for 40a spot on pdb
Can we buy 30a breakers that fit in the wide 40a breaker spot on the PDB?
Bruce |
|
#2
|
|||||
|
|||||
|
Re: 30a breaker for 40a spot on pdb
As long as they are identical to the 30A snap-action breakers provided in the KOP, yes. <R42-B>.
|
|
#3
|
||||
|
||||
|
Re: 30a breaker for 40a spot on pdb
I am sure that you can buy one but you cannot use it. Only 40a breakers can go in the 40a breaker slots.
|
|
#4
|
||||
|
||||
|
Re: 30a breaker for 40a spot on pdb
Can you tell me what rule denies this possibility?
Thanks Bruce |
|
#5
|
|||||
|
|||||
|
Re: 30a breaker for 40a spot on pdb
I already did. <R42-B>. If you are using breakers that are not identical to the KOP snap-action ones, you are in violation of the rules.
|
|
#6
|
||||
|
||||
|
Re: 30a breaker for 40a spot on pdb
I guess I was asking MPG what rule says they are illegal. I was wondering if the breaker supplier had 30a breakers taht fit in the 40a slots and if taht was legal. We have our cims on 40a breakers even though I warned the team that pulling 160a from 4 cims would result in the main tripping which is infinately worse than temprarilu tripping a snap action breaker. It poped in the last game of the championship match in Milwaukee so we want t change them to 30s. Problem is we will have to redo the entire PDB to make this change at Atlanta if we cannot find 30's that will fit int he 40a slots. Having only about 2 hours for pit setup and robot inspecctions and needed robot changes in Atlanta this year, we were looking for an easier way to switch to 30's.
Bruce |
|
#7
|
||||
|
||||
|
Re: 30a breaker for 40a spot on pdb
Bruce, we've got 4 cims, each on a 40, and you pop the 40's LONG before you should be popping the main breaker. In point of fact in 2008 we had 4 cims and 2 fisher price all drawing hard when we lifted a trackball and rounded the corner, and we STILL never popped our main breaker. That main breaker doesn't pop immediately at it's stated amperage - just like the snap-action breakers and have a small period of time where it can go over the rated amperage.
I'd be suspicious of your main breaker, or of some sort of short / wiring issue causing it to let go. I've never heard of a team popping that main breaker simply through motor use (though I'm sure it's happened). |
|
#8
|
|||||
|
|||||
|
Re: 30a breaker for 40a spot on pdb
I can't find anything saying it's illegal to put a 30A in a 40A slot. Best practice? Maybe, maybe not--I'll defer to the EEs around here on that.
However, you have to use the supplied 30A breakers, or identical ones, in the PDB. That means that you're going to be redoing your PDB unless the KOP 30As will fit into the 40A slots (which I'm guessing you've already tried). If the 30As don't fit into the 40A slots, then <R42-B> effectively prohibits 30As in a 40A slot. Unless you're coming in on Thursday, you've got Wednesday night and all morning Thursday to get ready to compete. |
|
#9
|
||||
|
||||
|
Re: 30a breaker for 40a spot on pdb
Quote:
The best way to fix this issue would be to decrease your current draw, rather than forcing your circuit to break earlier. That would just change the issue from "my robot can't move anymore" to "my robot stops every few seconds", which both suck. Last edited by Chris is me : 30-03-2010 at 21:48. |
|
#10
|
|||
|
|||
|
Re: 30a breaker for 40a spot on pdb
Popping the 130A main breaker shouldn't be a big worry. Can it be done using standard KoP components in a safe and legal way? Of course. Is it easy? Nope.
I believe the 130A breaker is thermal based. Last year, we managed to trip it during practice, after running for ~1.5-2 hours stopping only to do battery changes. Our robot last year utilized just about every KoP motor, short of 1 globe and the window. At peak current, it was probably getting close to 250A. On average, I would guess it was approximately 100A (due to the nice slippery floor surface). My point is, during a 2 minute match, it would be near impossible to pop the main breaker without an electrical fault. If I were you, I would just run the motors through 40A breakers. I suspect that even stalling the motors for 2 minutes wouldn't trip the main breaker, although it would begin tripping the 40A ones pretty quick. Sustained 200-250A for 2 minutes through the main breaker might be enough, but I don't see how you can possibly sustain such a high current draw for a full match. I'd be more worried for the batteries at that point... |
|
#11
|
||||
|
||||
|
Re: 30a breaker for 40a spot on pdb
Quote:
|
|
#12
|
|||||
|
|||||
|
Re: 30a breaker for 40a spot on pdb
OK,
The 120 amp main breaker and all the other breakers have basically the same construction. The only difference is the main breaker is not auto resettable. All the breakers are capable of over current up to 600% of rated current for a few seconds. Changing to smaller breakers does not limit the current supplied to the motors. CIMs will still pull 129 amps in stall even if you feed them with 5 amp breakers. The main breaker occasionally trips but more often this is due to external forces rather than an over current condition. |
|
#13
|
||||
|
||||
|
Re: 30a breaker for 40a spot on pdb
Yes, the CIM's may be protected by a 40A breaker... but have you measured how much they're actually drawing? During normal (non-stall) operation, it's no where near as much. One year we were worried about current draw, and decided to measure... Turns out it was a fairly constant 40-50A during normal use - 7 total motors running almost constantly, 4 of those CIM's.
If you're really worried about it, i would suggest investing in a clamp meter. Simply put, it uses the magnetic field generated by the current traveling through a wire in order to measure that current. You can clamp it over one of the battery leads, or one of the wires going to your wheels, and see what sort of draw you're getting. It can be EXTREMELY helpful in diagnosing problems. specifically last year with our shooter... we used it after initial construction and saw numbers that we felt were too high (about 3 times what we expected). After some slight mechanical adjustments to reduce friction in the system, the numbers came in line with the expectations. So get a clamp meter, and see if you have any issues in your system first - maybe one or more of your sprockets isn't properly aligned, generating a lot of friction and thus high current. Set the robot up to drive straight into a wall and see what happens - do the motors stall out because of high friction wheels? What sort of current does each motor draw in this scenario? (keep in mind, this is essentially the worst case for most robots) |
|
#14
|
||||
|
||||
|
Re: 30a breaker for 40a spot on pdb
Ok, I know what everyone is saying that the breakers should last well above their rated amperage but this is not true and it is not the issue or the question. I physically tested all of the breakers yesterday because we are adding a programmed throttling device that limits the cim motor power under high loads. We have an external ammeter that measures the amperage draw to 2 amps. Yesterday I WAS ACTUALLY STALLING A CIM and tripping the 40 amp breaker, the problem is each 40 amp breaker will let you pull 50 amps for about 2 seconds before it trips. They let you spike up to 80 amps for a fraction of a second. We can draw 180 + amps for over 30 seconds JUST FROM OUR CIMS. We also have a vacuum that draws up to 30 amps continuously. WE ACTUALLY TRIPPED OUR BREAKER IN A MATCH. So its not a question of whether or not it can happen, it did. Switching to 30 amp breakers would partially solve the issue. I tested them and they allow about 35 amps draw for a second before they trip. This would mean MAX from the cims we could draw 140 amps for just second. This would partially solve our issue, it would just be a lot easier to swap them they have to re wire. We are counting more on our current draw feedback to keep this issue from happening again. But it does happen, the main can be tripped.
However we might try swapping out our main breaker to see if that is the issue. I was looking at charts previously posted and it should last for 20 seconds with 200% draw. We didn't have low enough ohm resistors to test the main breaker. I'm am not yelling so don't get the wrong impression I just want to make it clear what the issue is. Thanks for everyone's valuable input ![]() Last edited by robself705 : 31-03-2010 at 19:50. |
|
#15
|
||||
|
||||
|
Re: 30a breaker for 40a spot on pdb
Echoing this, I worked field at Dallas and I saw a stop 20 seconds into an elimination match because their Lexan cover hit the breaker and physically turn it off, sad story but it happens. I've also see one that wasn't clicked all the way and turned off after the robot moved about 3 ft, it was out for basically all of teleop, again, sad story.
|
![]() |
| Thread Tools | |
| Display Modes | Rate This Thread |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| A Tip for the PDB | Pavan Dave | Electrical | 4 | 06-01-2008 22:20 |
| CIM motor on 30A | jason701802 | Motors | 4 | 05-02-2007 20:23 |
| What guage wire do you use for 40A circuits | SuperBK | Electrical | 6 | 21-01-2007 14:58 |
| Bad 40A Breaker | Richard Wallace | Electrical | 3 | 18-02-2003 21:42 |
| Our 20A and 30A and 40A breakers . . . | Frank(Aflak) | Technical Discussion | 8 | 01-02-2003 08:36 |