CAN Installation Details
We are having trouble with CAN controlling a motor with the cRio. When the same serial connector is connected to the computer directly and using BDC-COMM, the Jaguar and motor work fine. That seems to eliminate wiring.
We have assigned a different address to the Jaguar (10). We have updated the Jaguar firmware to v.92. We get error -52007 on the CANReceive.vi. (could be spelled wrong). I'm concerned that we have not updated all the pieces properly. The FirstForge website now says that the CAN LabView components and drivers are all Obsolete. All of the files are now supposed to be part of the regular distribution. What does that mean and how are all of the pieces installed? The cRio needs the CAN driver? Is that included with the 2011 update for the cRio? CAN vi's for LabView are obviously required. Are those installed by default? We are using the vi's that are in the "User VIs" section. We found other VIs under WPI. Which should we be using? We can we find details or project examples. Thank you for the help, ...Duane |
|
#2
|
||||
|
||||
|
Re: CAN Installation Details
Everything necessary for the use of CAN is included in the updates. When the imaging tool is installed, BDC-Comm and the latest firmware versions are also installed. Then, when you go to reimage your cRIO, there is a new option for the CAN plugins. The language update includes the CAN library.
Make sure you have reimaged your cRIO. I don't use labview so I can't help you with that part. |
|
#3
|
||||
|
||||
|
Re: CAN Installation Details
Quote:
I don't understand part of this statement "When the imaging tool is installed, BDC-Comm and the latest firmware versions are also installed." I need more reference. I don't understand which imaging tool you are referring too. Is this the cRio imaging tool? Is BDC-COMM the application or the firmware drivers? It seems that details are important in this case. |
|
#4
|
||||
|
||||
|
Re: CAN Installation Details
Sorry, Yes, by imaging tool I was referring to the cRIO Imager. I don't remember which update it came with, but when it's installed BDC-COMM, the firmware, and some documentation. It used to be put in Public documents, but it might be put in the installing users documents folder.
I assume you know that you use BDC-Comm to load the firmware onto the jaguars? They need to be running version 92 to be used with Image v25 on the cRIO. |
|
#5
|
||||
|
||||
|
Re: CAN Installation Details
Thank you. That makes more sense.
We updated the Jaguars to v92 and the cRio is using v25. What is left is which CAN vi's we should be using. I get the idea that we are using last years vi's because they are in the "User Library" section of the LabView. We need to figure out where the correct VIs to use are. Right now we are just trying to do basic a SetSpeed on the Jaguars. Not driving yet. Suggestions? |
|
#6
|
||||
|
||||
|
Re: CAN Installation Details
As I said, i don't know much about labview but it would make sense to me that, the VIs in the user section are what you've added to the project. Given that, it would seem that they are the old version of the library. Try switching all the Can VI's for the ones from WPILib.
|
|
#7
|
|||
|
|||
|
Re: CAN Installation Details
Quote:
You should find them in the Robotics Library palette. Robot Drive and Actuators/Motor Control have integrated CAN support now. -Joe |
|
#8
|
||||
|
||||
|
Re: CAN Installation Details
Quote:
There are no errors indications. The error connections do not indicate any errors. The single Jaguar is still blinking yellow. :-( I'm looking for suggestions on diagnosing the problem. We'll spend some more time on this tomorrow. An example posted vi would be great to ensure that we are doing everything correctly. Without examples we are in the blind. Thanks for your help! |
|
#9
|
||||
|
||||
|
Re: CAN Installation Details
The easiest test of your CAN network is enumeration. If you can enumerate the Jaguars, then your cabling works. (You can test this with the cRIO or with BDC-comm. Enumeration is in the functions pallette under "WPI Robotics Library">Communications>CAN. The BDC-comm enumerates automatically when you open it up - the Jaguars you can select from the drop-down menu are the ones it enumerated.)
If enumeration works on the cRIO, then the issue is probably the Jaguar firmware; the Jaguar firmware must be updated (using the BDC-COMM) for using CAN in FRC. If enumeration works on the BDC-COMM, but not on your cRIO, then there's probably an issue with your CAN plugin, or your code. Now, it's entirely possible that your CAN network and code is working correctly, and you are simply not enabled or do not have DS communication. Make sure you have a "StartCommunication" on your block diagram. (This can be found in the DriverStation subpallette of the "WPI Robotics Library" functions.) EDIT: You asked for an example. I have a repository with a default project modified to CAN here: https://github.com/kamocat/ThunderTech_3213/tree/CAN If you'd like something specific, you can upload your code or state exactly what you're testing. Last edited by kamocat : 22-01-2011 at 02:26. |
|
#10
|
||||
|
||||
|
Re: CAN Installation Details
Quote:
Why is the DS communication required? We have a StartCommunication in the vi, but have not turned on or connected the DriverStation. We're just trying to see if we can control a single motor. Seems like this should be pretty easy. :-) Thank you for the examples, we'll give them a look. I'm concerned that the example expects an entire set of motors, etc. All we have connected to the cRio is one Jaguar and one motor. The idea was to demonstrate the minimum requirements for using the Jaguar. |
|
#11
|
|||
|
|||
|
Re: CAN Installation Details
Quote:
-Joe |
|
#12
|
||||
|
||||
|
Re: CAN Installation Details
Somehow, I didn't remember requiring the DS to be connected last year, but that was last year. Better notes this year for next year.
We had some success today and we have discovered at least one problem with the cRio. Ethernet port 2 does not work on the cRio. We cannot connect both the DS and the LabView computer at the same time. We have since connected Ethernet Port 1 to a hub and connected the both computers to the hub. We can now download and run code from the LabView system after the robot is enabled with the DS. However we are still having trouble with CAN. We can only address the first CAN Node. That is whatever CAN device is attached to the serial port works just fine. The other devices are not recognized (they continue to blink yellow). Addressing the devices is a problem even with the BDC-COMM program. So it seems like wiring. We have gone through every possible combination of Jaguar, wire connection, and terminator. We've swapped all the different components (save the Jaguars) with parts from last years robot. It seems like the serial to CAN translation is not occurring. The serial interface is working but the next device does not see any signal. Is there any way to verify that the signal is on the bus? We can get one Jaguar to work. Last year we had 10 all on CAN. I know this works. I must be missing something. |
|
#13
|
|||
|
|||
|
Re: CAN Installation Details
Port 2 on the cRIO is a separate NIC, and is on a separate subnet from port 1. You normally attach the camera to port 2, although if you have other devices that are supposed to be isolated to the robot, they can be connected via a hub. Port 1 is the outside port, and you should be able to have both the programming and DS laptops join the wireless AP on the robot. You can also wire both computer to the AP which is connected to port 1.
Greg McKaskle |
|
#14
|
|||
|
|||
|
Re: CAN Installation Details
Quote:
Quote:
Quote:
Sure, if you have a scope or a differential DAQ system. -Joe |
![]() |