Another thing to add that issue our driver station always reads 0 voltages whenever we are connected to robot.
Does someone know how to fix this problem? |
|
#2
|
|||||
|
|||||
|
Re: Incorrect voltage readout on Driver Station
Quote:
The jumper should be installed on the outside two pins of the 3 pin header. The Analog Breakout requires 12V power from the Power Distribution board in order to run. The Analog Breakout Datasheet provides more detail if you need it: http://www.usfirst.org/uploadedFiles...out%281%29.pdf |
|
#3
|
||||
|
||||
|
Re: Incorrect voltage readout on Driver Station
Ours is reading zero also. I have swapped analog modules and breakouts and the jumper is in the correct position. We are playing with custom dashboard code at the moment and getting message errors. Could that be messing it up?
TIA |
|
#4
|
|||||
|
|||||
|
Re: Incorrect voltage readout on Driver Station
It would greatly help us help you if you could take a clear photo of your analog breakout while the problem is occurring and post it here, showing the jumper and the wiring connected to it.
|
|
#5
|
||||
|
||||
|
Re: Incorrect voltage readout on Driver Station
photo attached - sure looks correct
Last edited by wireties : 05-03-2012 at 12:16. |
|
#6
|
|||||
|
|||||
|
Re: Incorrect voltage readout on Driver Station
It looks okay...except for the lack of any indication that there is actually power applied. There's a green LED that ought to be lit. What voltage do you see using a meter on the white Wago connector?
|
|
#7
|
||||
|
||||
|
Re: Incorrect voltage readout on Driver Station
Quote:
TIA Last edited by wireties : 21-02-2011 at 16:24. |
|
#8
|
|||
|
|||
|
Re: Incorrect voltage readout on Driver Station
Customizing a dashboard will not break the robot battery voltage communications. They are very independent.
Greg McKaskle |
|
#9
|
|||||
|
|||||
|
Re: Incorrect voltage readout on Driver Station
The problem became obvious once I realized what to look for.
Keith, your NI 9201 module is in Slot 8 of the cRIO chassis. It needs to be in Slot 1, at the end nearest the Ethernet ports and power connector. |
|
#10
|
||||
|
||||
|
Re: Incorrect voltage readout on Driver Station
Quote:
Hmmm - I'll check it tomorrow. I thought it was in slot 1. Thanks |
|
#11
|
||||
|
||||
|
Re: Incorrect voltage readout on Driver Station
Quote:
All is good now! |
![]() |