Re: Jaguars not passing CAN communications
Terminating resistor has nothing to do with the RS232 bus. It terminates the RS422 bus that is in the same plug. The other terminating resistor is in the unused port on the last Jag in the daisy chain (making a total of 2). The bus will mostly run without the terminating resisters, but will be subject to noise. It will also be the first troubleshooting question.
I found to get all the Jags to communicate that I had to power up the jags with them all connected & then restart the BCD-COMM com. A little concerning because it seems to me that the new jags should be recognized as they are plugged in. |
|
#2
|
|||
|
|||
|
Re: Jaguars not passing CAN communications
Quote:
Oliver |
|
#3
|
||||
|
||||
|
Re: Jaguars not passing CAN communications
Probably restating the obvious here, but make sure that you reprogram the CAN IDs on the Jags before plugging them into the bus. By default, the Jags all come with the same ID set. So, even if the termination is correct, you'll only see one of them. You can reprogram the IDs using the BDC_COMM application. Follow the getting started guide for details. BTW, you can get a complete set of working CAN cables w/ terminators and the RS-232 cable from http://www.estoprobotics.com/estore/ if you're interested.
HTH, Mike |
|
#4
|
|||
|
|||
|
Re: Jaguars not passing CAN communications
Quote:
|
|
#5
|
|||
|
|||
|
Re: Jaguars not passing CAN communications
Quote:
|
|
#6
|
||||
|
||||
|
Re: Jaguars not passing CAN communications
Quote:
|
|
#7
|
|||
|
|||
|
Re: Jaguars not passing CAN communications
I don't have one yet but I am trying to get one. What kind of diagnostics does it provide? It would give me some kind of indication of the quality of the network?
Also, other suggestions please in case I don't get the 2CAN for a few weeks. |
|
#8
|
||||
|
||||
|
Re: Jaguars not passing CAN communications
Quote:
In the mean time check your cabling, reduce your number of Jags on the BUS down to 1 until you are successful (I see you have already done this but this reduces the possibility that you have more than one jag on the bus with the same ID.) And yes the CAN bus will not operate without at least one 120 ohm termination resistor, although the BUS will work with only one you should have both in place at each end of the BUS as this is what CAN is designed around. If you are using 100 ohms that is fine as well. Even though the CAN spec and the TI data sheet for the CAN PHY both say it should be 120 ohms, using a 100 ohm resistor will probably work fine. Make sure you are not trying to write to Jags that are not present on the BUS as this will cause you pain and the -44087 timeout error. I hope this helps. |
![]() |