Re: Air Compressor Will Not Initiate
Quote:
|
|
#2
|
|||||
|
|||||
|
Re: Air Compressor Will Not Initiate
For a switch input to be read by the program, you need to use the signal pin and the ground (-) pin. The Digital Sidecar inputs are already at +5 volts when nothing is connected to them. You have to pull them low in order to register a change.
|
|
#3
|
||||
|
||||
|
Re: Air Compressor Will Not Initiate
Ok so you fixed the pins now we have one wire going to the signal and one to the negative. But it will still not start when we enable the robot.
|
|
#4
|
|||||
|
|||||
|
Re: Air Compressor Will Not Initiate
Quote:
Disconnect the pressure switch from the Digital Sidecar and measure continuity between the contacts. They should be shorted together when the pressure is too low. If there is an open circuit, replace the switch. Check the Digital Sidecar and look to see whether the relay is being asked to turn on (there should be a green LED lit next to the pins for relay #1). If it is, look at the LED on the Spike (it should change from yellow to green when the robot is enabled). |
![]() |