30A breakers for motor controllers?

Can anyone verify that there's no rule against running a victor-driven mini-cim on a 30A breaker circuit? The mini-cim is ~19A.

Thanks.
  #2   Spotlight this post!  
Unread 19-01-2014, 13:13
Gregor's Avatar
Gregor Gregor is offline
#StickToTheStratisQuo
AKA: Gregor Browning
no team
Team Role: College Student
 
Join Date: Jan 2012
Rookie Year: 2012
Location: Kingston, Ontario, Canada
Posts: 2,447
Gregor has a reputation beyond reputeGregor has a reputation beyond reputeGregor has a reputation beyond reputeGregor has a reputation beyond reputeGregor has a reputation beyond reputeGregor has a reputation beyond reputeGregor has a reputation beyond reputeGregor has a reputation beyond reputeGregor has a reputation beyond reputeGregor has a reputation beyond reputeGregor has a reputation beyond repute
Re: 30A breakers for motor controllers?

The table in R46 does indeed allow this, but any reason as to why you're not running it off a 40A breaker? I assume you're not out of 40A slots on the PDB.
__________________
What are nationals? Sounds like a fun American party, can we Canadians come?
“For me, insanity is super sanity. The normal is psychotic. Normal means lack of imagination, lack of creativity.” -Jean Dubuffet
"Insanity is doing the same thing over and over again and expecting different results." -Albert Einstein
FLL 2011-2015 Glen Ames Robotics-Student, Mentor
FRC 2012-2013 Team 907-Scouting Lead, Strategy Lead, Human Player, Driver
FRC 2014-2015 Team 1310-Mechanical, Electrical, Drive Captain
FRC 2011-xxxx Volunteer
How I came to be a FIRSTer
<Since 2011
  #3   Spotlight this post!  
Unread 19-01-2014, 13:45
VEI Dude's Avatar
VEI Dude VEI Dude is offline
Mentor 4024, 4013
AKA: Neil the Real Deal
FRC #4013 (Jokers & Clockwork Mania)
Team Role: Mentor
 
Join Date: Sep 2008
Rookie Year: 2008
Location: Orlando, FL
Posts: 54
VEI Dude has a spectacular aura aboutVEI Dude has a spectacular aura about
Re: 30A breakers for motor controllers?

Yep... we'll most likely be out of 40A slots.
Thanks.
  #4   Spotlight this post!  
Unread 20-01-2014, 07:30
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,785
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: 30A breakers for motor controllers?

Breakers are sized for the wire they feed. If you choose a smaller gauge wire then you may use a smaller breaker.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #5   Spotlight this post!  
Unread 20-01-2014, 12:50
Andy Brockway Andy Brockway is offline
Engineer
FRC #0716 (Who'sCTEKS)
Team Role: Engineer
 
Join Date: Apr 2002
Rookie Year: 2001
Location: Falls Village, CT
Posts: 459
Andy Brockway has a reputation beyond reputeAndy Brockway has a reputation beyond reputeAndy Brockway has a reputation beyond reputeAndy Brockway has a reputation beyond reputeAndy Brockway has a reputation beyond reputeAndy Brockway has a reputation beyond reputeAndy Brockway has a reputation beyond reputeAndy Brockway has a reputation beyond reputeAndy Brockway has a reputation beyond reputeAndy Brockway has a reputation beyond reputeAndy Brockway has a reputation beyond repute
Re: 30A breakers for motor controllers?

Quote:
Originally Posted by Al Skierkiewicz View Post
Breakers are sized for the wire they feed. If you choose a smaller gauge wire then you may use a smaller breaker.
I thought we could use the larger gauge wire with a smaller breaker. We have been using 10 gauge for the 40 amp. This is left over from when 10 gauge was required.

The rules (R47) specifiy a minimum wire size per breaker size.
__________________
Andy Brockway
Team 716, The Who'sCTEKS
  #6   Spotlight this post!  
Unread 20-01-2014, 13:23
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,785
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: 30A breakers for motor controllers?

Andy,
Yes you can, the wire size minimum is listed by the breaker feeding that branch. i.e. a 40 amp breaker can be used with #12 wire but I recommend #10 for CIM motors. The wire size is chosen for safety and voltage drop from the NEC handbook for open frame DC wiring. If #14 wire was used with the 40 amp breaker, it is possible to heat the wire to the point at which the insulation fails. #12 wire on the other hand may get warm but not to the point at which a failure would occur. A dead short of course, would be protected by the breaker. At 100 amps, the #12 drops ~0.2 volts per foot. In a typical robot wiring job I would expect to lose almost a volt at the motor input during starting and heavy loading with a fully charged battery.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #7   Spotlight this post!  
Unread 04-02-2014, 15:47
hiddenhobbit hiddenhobbit is offline
Registered User
FRC #1389
 
Join Date: Jan 2014
Location: Mars
Posts: 1
hiddenhobbit is an unknown quantity at this point
Re: 30A breakers for motor controllers?

Can we use CIMs from the 30A? Or any motor controller for that matter?

Thanks!
  #8   Spotlight this post!  
Unread 04-02-2014, 16:11
Ether's Avatar
Ether Ether is offline
systems engineer (retired)
no team
 
Join Date: Nov 2009
Rookie Year: 1969
Location: US
Posts: 8,091
Ether has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond repute
Re: 30A breakers for motor controllers?

Quote:
Originally Posted by Al Skierkiewicz View Post
Breakers are sized for the wire they feed. If you choose a smaller gauge wire then you may use a smaller breaker.
Isn't it the other way around?

If you choose a smaller gauge wire then you must use a smaller breaker.

Or maybe it's the ambiguity of the phrase "smaller gauge wire"...
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 22:42.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi