Can't get pneumatics solenoids to work

Hey guys.

So, my team and I have been trying to get some solenoids working so that we can toggle a couple of pistons on and off. Unfortunately, we haven't been able to get the solenoids to work properly.

We're using, as of right now, one 12v double solenoid, P/N SY3240-5L0U. We have tried several units. We have also tried a single solenoid, P/N SY3140-5FU. They were/are connected to a block P/N SY3000-27-1.

We have gotten none of these to work. The code is working fine. The lights on the cRIO light up, and we can hear the solenoids clicking inside the housings. But the air still takes the same path, no matter what screwholes we put the tubes in nor what pressure we use.

We tested the electrical connections, and the solenoids are getting a little over 12v.

Does anyone have any ideas as to what the problem could be?

Thanks!
  #2   Spotlight this post!  
Unread 24-01-2014, 17:40
MetalJacket's Avatar
MetalJacket MetalJacket is offline
Has read the 2014 manual
AKA: Jesse Gibson
FRC #2068 (The Metal Jackets)
Team Role: CAD
 
Join Date: Oct 2012
Rookie Year: 2011
Location: Virginia
Posts: 164
MetalJacket has a spectacular aura aboutMetalJacket has a spectacular aura aboutMetalJacket has a spectacular aura about
Re: Can't get pneumatics solenoids to work

Hi, welcome to chiefdelphi!
A few questions/suggestions that might help ...
- You said that you could hear the solenoids clicking, could you see the little red lights on top toggling on and off?
- Just in case it is code, try firing the solenoids manually by pressing in the little blue buttons on top using a pen or something similar.
- Could you post a picture of the setup so we can see if some of the tubing is not going where it should be or something along those lines?
- Probably a dumb question but is any air at all going to the cylinder? Is it just locked in one position when the system is charged or does it move freely?

Jesse
__________________
Team Role = !artTeam
2011 - Logomotion
- Virginia Regional : Tournament Semi-Finalist, Gracious Professionalism Award
2012 - Rebound Rumble
- Chesapeake Regional : Tournament Finalist, Gracious Professionalism Award
2013 - Ultimate Ascent
- Virginia Regional : Gracious Professionalism Award
  #3   Spotlight this post!  
Unread 24-01-2014, 17:53
kevin.li.rit's Avatar
kevin.li.rit kevin.li.rit is offline
Imaginary Friend
AKA: Kevin Li
FRC #0596 (SciClones)
Team Role: Student
 
Join Date: Jan 2003
Rookie Year: 2001
Location: Hopkinton, Massachusetts
Posts: 936
kevin.li.rit has a reputation beyond reputekevin.li.rit has a reputation beyond reputekevin.li.rit has a reputation beyond reputekevin.li.rit has a reputation beyond reputekevin.li.rit has a reputation beyond reputekevin.li.rit has a reputation beyond reputekevin.li.rit has a reputation beyond reputekevin.li.rit has a reputation beyond reputekevin.li.rit has a reputation beyond reputekevin.li.rit has a reputation beyond reputekevin.li.rit has a reputation beyond repute
Send a message via Yahoo to kevin.li.rit
Re: Can't get pneumatics solenoids to work

Isn't the SY3240-5L0U and SY3140-5FU a 24V solenoid?
__________________
Kevin Li

596 - Sciclones
1405 - Finney Falcons
2262 - Holliston Panthers
  #4   Spotlight this post!  
Unread 24-01-2014, 19:33
DonRotolo's Avatar
DonRotolo DonRotolo is offline
Back to humble
FRC #0832
Team Role: Mentor
 
Join Date: Jan 2005
Rookie Year: 2005
Location: Atlanta GA
Posts: 7,011
DonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond repute
Re: Can't get pneumatics solenoids to work

Quote:
Originally Posted by Fej View Post
But the air still takes the same path, no matter what screwholes we put the tubes in nor what pressure we use.
You definitely need to use the correct screw holes to connect things up, or it won't work.

There's a side with 3 holes, and a side with 2 holes. The 2 holes go to the cylinder's two ports. The middle hole on the 3-hole side is the air input. Leave the other 2 ports open (not plugged).

Use at least 30 PSI input.
__________________

I am N2IRZ - What's your callsign?
  #5   Spotlight this post!  
Unread 24-01-2014, 23:34
Bill_B Bill_B is offline
You cannot not make a difference
FRC #2170
 
Join Date: Jan 2010
Rookie Year: 2004
Location: Connecticut
Posts: 1,099
Bill_B has a reputation beyond reputeBill_B has a reputation beyond reputeBill_B has a reputation beyond reputeBill_B has a reputation beyond reputeBill_B has a reputation beyond reputeBill_B has a reputation beyond reputeBill_B has a reputation beyond reputeBill_B has a reputation beyond reputeBill_B has a reputation beyond reputeBill_B has a reputation beyond reputeBill_B has a reputation beyond repute
Re: Can't get pneumatics solenoids to work

I think Kevin has a good point. Is your solenoid breakout board's Wago connector wired correctly to a 24v spot on the power distribution board? Make sure the polarity is correct.

There is one other thing that is tricky. I'm not sure how the manual override for the SMC valves works. Your part number did not include the code that specifies what type there is. so maybe your valves don't have the override. But if they do I think it is a blue button sometimes that has a small slot in it. If you push it when the air pressure is available, the valve will be activated. The Festo equivalents allow a quarter turn of that slotted button which disables the solenoid completely. If it is turned on the Festo rig, the valve will not respond to electrical signals on either side.
__________________
Nature's Fury FLL team 830 - F L eLements
FRC team 2170 - Titanium Tomahawks
  #6   Spotlight this post!  
Unread 25-01-2014, 12:14
jfitz0807 jfitz0807 is offline
Registered User
FRC #2877 (Ligerbots)
Team Role: Parent
 
Join Date: Jan 2009
Rookie Year: 2009
Location: Newton, MA
Posts: 67
jfitz0807 is an unknown quantity at this point
Re: Can't get pneumatics solenoids to work

This has been a big help. We have been having a similar problem. We are using the Festo double solenoid. We had no idea about the blue buttons.

Our problem turned out to be that we had 12V to our solenoid breakout, but the solenoids needed 24V. The Festo VUVG-L10-B52-T-M7-5P3 is a 12V solenoid per the AndyMark website. We happened to have VUVG-L10-B52-T-M7-1P3. Note the "1P3". This is a 24V solenoid. Once we connected 24V to our solenoid breakout, it worked.

Note also that the "M7" denotes the size of the air holes. We also have a bunch of "M5"s which have a smaller opening.
  #7   Spotlight this post!  
Unread 25-01-2014, 16:25
Tem1514 Mentor's Avatar
Tem1514 Mentor Tem1514 Mentor is offline
Registered User
FRC #1514
Team Role: Mentor
 
Join Date: Feb 2010
Rookie Year: 2010
Location: Toronto
Posts: 239
Tem1514 Mentor is a splendid one to beholdTem1514 Mentor is a splendid one to beholdTem1514 Mentor is a splendid one to beholdTem1514 Mentor is a splendid one to beholdTem1514 Mentor is a splendid one to beholdTem1514 Mentor is a splendid one to beholdTem1514 Mentor is a splendid one to beholdTem1514 Mentor is a splendid one to behold
Re: Can't get pneumatics solenoids to work

Just a little note on the manual blue buttons is that they may enabled to always on if you turn the slot 90 degrees. If happen to miss the fact that the solenoid has been locked on it make for a real bad day of troubleshooting.
  #8   Spotlight this post!  
Unread 25-01-2014, 20:55
InsanesTheName's Avatar
InsanesTheName InsanesTheName is offline
Registered User
AKA: Tommy
FRC #1672 (Robo T-Birds)
Team Role: Programmer
 
Join Date: Jan 2014
Rookie Year: 2013
Location: New Jersey
Posts: 1
InsanesTheName is an unknown quantity at this point
Re: Can't get pneumatics solenoids to work

Hello everyone! I am also on Fej's team.

After some more work this morning, I figured out that it was the lack of pressure that was causing the solenoids to not work properly. While the air canister had plenty of pressure, there was nothing connected to the output tube in the solenoid; therefore, the solenoid itself wasn't actually pressurized at all. As soon as we connected a piston to the output tube, the solenoids worked perfectly since they were now pressurized enough.

Thanks for all the responses! Hopefully this can help anyone else having this same issue not make the same silly mistakes we did.
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 11:26.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi