PWM Signal

We are running a 6 CIM Drive for the first time this year. We want the security of running each speed controller to a separate PWM port on the DSC but we don't have 6 to spare. Can we create a 3 way splitter cable to attach to each speed controller, and on the other end wire two PWM connectors in Parallel and attach it to 2 PWM ports? This photo should help clarify. That way we save 2 PWM ports and we have some redundancy in the electronics.

Is this a good, or horrible idea?
  #2   Spotlight this post!  
Unread 01-02-2014, 18:22
Dale's Avatar
Dale Dale is offline
Head Coach & Mentor
AKA: Dale Yocum
FRC #1540 (Flaming Chickens)
Team Role: Coach
 
Join Date: Feb 2005
Rookie Year: 2005
Location: Portland, OR
Posts: 502
Dale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud of
Re: PWM Signal

Teams do that all the time. AndyMark even sells a Y cable for doing two at a time. I'm sure doing three Talons would be fine as well.
__________________
2016 PNW Championship Chairman's; 2016 Winner Oregon City District, 2015 PNW Championship Chairman's; 2015 PNW District Engineering Inspiration; 2015 PNW District Finalist; 2014 PNW Championship Chairman's; 2014 Championship Innovation in Controls; 2013 Chairman's (Oregon); 2013 Finalist (OKC); 2012 Winner (OKC); 2012 Chairman's (OKC); 2012 Woody Flowers (Oregon); 2011 Volunteer of the Year (Oregon); 2011 Finalist & Captain (San Diego); 2011 Innovation in Control (San Diego); 2010 & 2007 Chairman's (Oregon); 2010 Regional Champions (Colorado); 2010 Innovation in Control (Colorado); 2009 & 2008 Engineering Inspiration (Oregon); 2008 Regional Champions (Oregon); 2007 Regional Finalist (Oregon); 2005 Rookie Inspiration (PNW)
  #3   Spotlight this post!  
Unread 01-02-2014, 18:44
Ether's Avatar
Ether Ether is offline
systems engineer (retired)
no team
 
Join Date: Nov 2009
Rookie Year: 1969
Location: US
Posts: 8,074
Ether has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond repute
Re: PWM Signal

Quote:
Originally Posted by Dale View Post
Teams do that all the time. AndyMark even sells a Y cable for doing two at a time. I'm sure doing three Talons would be fine as well.
Did you notice that he is proposing to connect the two DSC outputs together?

see attached sketch

Attached Thumbnails
Click image for larger version

Name:	PWM cable.jpg
Views:	64
Size:	58.6 KB
ID:	16057  

Last edited by Ether : 02-02-2014 at 01:01.
  #4   Spotlight this post!  
Unread 01-02-2014, 19:20
Kevin Selavko's Avatar
Kevin Selavko Kevin Selavko is offline
Registered User
AKA: Voltonless
FRC #3260 (SHARP)
Team Role: Electrical
 
Join Date: Jan 2012
Rookie Year: 2008
Location: Beaver PA USA
Posts: 155
Kevin Selavko is on a distinguished road
Re: PWM Signal

Find it highly unlikely that only one port on your sidecar will fail and in a way that it would not interfere with the signal from a second. I also don't know how well the controllers would like having two signals sent to it all the time, Im guessing that the signals would not be exactly the same. Also I think it to be more likely for your pwm y cable to fail more than any port on the DSC, and adding to the number of pwms connected to each other will increase the probability of a connection coming loose.
__________________
Team SHARP
Pittsburgh Regional Champions 2014
Vex Pittsburgh Excellence Award 2014
Vex Pittsburgh Champions 2014
Vex Maryland Champions 2014
Pittsburgh Regional Finalists 2013
Buckeye Regional Finalists 2013
  #5   Spotlight this post!  
Unread 01-02-2014, 19:24
Dale's Avatar
Dale Dale is offline
Head Coach & Mentor
AKA: Dale Yocum
FRC #1540 (Flaming Chickens)
Team Role: Coach
 
Join Date: Feb 2005
Rookie Year: 2005
Location: Portland, OR
Posts: 502
Dale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud of
Re: PWM Signal

I didn't catch that you were connecting multiple outputs of the DSC together. Just run the three Talons from a single DSC output and you'll be fine,.
__________________
2016 PNW Championship Chairman's; 2016 Winner Oregon City District, 2015 PNW Championship Chairman's; 2015 PNW District Engineering Inspiration; 2015 PNW District Finalist; 2014 PNW Championship Chairman's; 2014 Championship Innovation in Controls; 2013 Chairman's (Oregon); 2013 Finalist (OKC); 2012 Winner (OKC); 2012 Chairman's (OKC); 2012 Woody Flowers (Oregon); 2011 Volunteer of the Year (Oregon); 2011 Finalist & Captain (San Diego); 2011 Innovation in Control (San Diego); 2010 & 2007 Chairman's (Oregon); 2010 Regional Champions (Colorado); 2010 Innovation in Control (Colorado); 2009 & 2008 Engineering Inspiration (Oregon); 2008 Regional Champions (Oregon); 2007 Regional Finalist (Oregon); 2005 Rookie Inspiration (PNW)
  #6   Spotlight this post!  
Unread 01-02-2014, 19:54
Ether's Avatar
Ether Ether is offline
systems engineer (retired)
no team
 
Join Date: Nov 2009
Rookie Year: 1969
Location: US
Posts: 8,074
Ether has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond repute
Re: PWM Signal

Quote:
Originally Posted by Dale View Post
Just run the three Talons from a single DSC output and you'll be fine,.
I think you're probably right Dale. But this post by EricVanWyk from 4 years ago does seem to suggest that the number that can be supported is different for different models of controller.

Maybe Mike Copioli could weigh in here and let us know if he believes that 3 Talons will be OK being driven off one DSC PWM port.



Last edited by Ether : 02-02-2014 at 00:23. Reason: Thanks Don
  #7   Spotlight this post!  
Unread 01-02-2014, 20:32
Dale's Avatar
Dale Dale is offline
Head Coach & Mentor
AKA: Dale Yocum
FRC #1540 (Flaming Chickens)
Team Role: Coach
 
Join Date: Feb 2005
Rookie Year: 2005
Location: Portland, OR
Posts: 502
Dale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud ofDale has much to be proud of
Re: PWM Signal

It's feeding into an optoisolator in each Talon out of a 330 ohm resistor in the DSC. The PWM output can source or sink 15ma. Most optoisolators turn on around 1.6ma. We've driven three Talons before with no issue but Mike might have thoughts about whether it's likely to be on the hairy edge.
__________________
2016 PNW Championship Chairman's; 2016 Winner Oregon City District, 2015 PNW Championship Chairman's; 2015 PNW District Engineering Inspiration; 2015 PNW District Finalist; 2014 PNW Championship Chairman's; 2014 Championship Innovation in Controls; 2013 Chairman's (Oregon); 2013 Finalist (OKC); 2012 Winner (OKC); 2012 Chairman's (OKC); 2012 Woody Flowers (Oregon); 2011 Volunteer of the Year (Oregon); 2011 Finalist & Captain (San Diego); 2011 Innovation in Control (San Diego); 2010 & 2007 Chairman's (Oregon); 2010 Regional Champions (Colorado); 2010 Innovation in Control (Colorado); 2009 & 2008 Engineering Inspiration (Oregon); 2008 Regional Champions (Oregon); 2007 Regional Finalist (Oregon); 2005 Rookie Inspiration (PNW)
  #8   Spotlight this post!  
Unread 01-02-2014, 21:26
Ether's Avatar
Ether Ether is offline
systems engineer (retired)
no team
 
Join Date: Nov 2009
Rookie Year: 1969
Location: US
Posts: 8,074
Ether has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond repute
Re: PWM Signal

Quote:
Originally Posted by Dale View Post
It's feeding into an optoisolator in each Talon
Most likely so*. If there's a schematic, I haven't been able to find it.


Quote:
out of a 330 ohm resistor in the DSC
Yes. There's a schematic for this.


Quote:
The PWM output can source or sink 15ma.
With a dead short, yes.

Quote:
Most optoisolators turn on around 1.6ma
The spec is available for the Jag, and it is guaranteed to turn on with 1.6 ma.. Since there's a 150ohm series resistance and a voltage drop across the LED, it requires about 1 volt to push that 1.6 ma through the LED.

So if you drive 3 Jaguars being driven by one DSC PWM port:

5 - 330*i - (150/3)*i - 0.7 = 0 . . . => .. i=11ma .. => .. 3.8ma per Jag

So it should work for 3 Jags... but I'm not sure about that 0.7 number; couldn't find a spec.


Quote:
We've driven three Talons before with no issue but Mike might have thoughts about whether it's likely to be on the hairy edge.
If you're reading this Mike, any info you'd be willing to provide would be appreciated. Don't want to speculate.


* http://www.chiefdelphi.com/forums/showpost.php?p=1127215&postcount=3
  #9   Spotlight this post!  
Unread 02-02-2014, 00:50
tStano tStano is offline
Registered User
AKA: Sparks
no team
Team Role: Electrical
 
Join Date: Jan 2014
Rookie Year: 2012
Location: Madison, WI
Posts: 177
tStano will become famous soon enough
Re: PWM Signal

With this fix, you're using 2 slots anyway, so why don't you just use a y-cable and a normal PWM for each side? As mentioned above, I can't see one port failing and not the other, although I'm sure its possible; just not likely enough really to worry about.

That is, If you don't just want to run the three PWMs off one port, which probably would work just fine, as discussed above.

Last edited by tStano : 02-02-2014 at 00:54. Reason: Added bit about one failing and not the other.
  #10   Spotlight this post!  
Unread 02-02-2014, 09:52
DonRotolo's Avatar
DonRotolo DonRotolo is offline
Back to humble
FRC #0832
Team Role: Mentor
 
Join Date: Jan 2005
Rookie Year: 2005
Location: Atlanta GA
Posts: 6,998
DonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond repute
Re: PWM Signal

Quote:
Originally Posted by tStano View Post
That is, If you don't just want to run the three PWMs off one port, which probably would work just fine, as discussed above.
I agree.
IF YOU DO run 3 off a single port, PLEASE post your results here so everyone else will know whether this will work or not. Thanks!
__________________

I am N2IRZ - What's your callsign?
  #11   Spotlight this post!  
Unread 02-02-2014, 10:33
Sh1ine Sh1ine is offline
Registered User
FRC #2791
Team Role: Leadership
 
Join Date: Jan 2009
Rookie Year: 2009
Location: Albany NY
Posts: 96
Sh1ine is on a distinguished road
Re: PWM Signal

Currently we are running three off of one port. It is working fine, I hope that it continues to work fine. We will post an update later in the season.

Thanks all.
  #12   Spotlight this post!  
Unread 02-02-2014, 10:57
Ether's Avatar
Ether Ether is offline
systems engineer (retired)
no team
 
Join Date: Nov 2009
Rookie Year: 1969
Location: US
Posts: 8,074
Ether has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond repute
Re: PWM Signal

Quote:
Originally Posted by Sh1ine View Post
Currently we are running three off of one port. It is working fine, I hope that it continues to work fine.
My guess is that it will.

Does your team have access to an oscilloscope? If you want to be on the safe side, you can measure the voltage waveform (and magnitude) on the signal line in your PWM cable. It can give you some assurance that you've got adequate operating margin.

FWIW, I just found this note in the spec for the H11L1M optocoupler used in the Jaguar.


Attached Thumbnails
Click image for larger version

Name:	guard band.png
Views:	24
Size:	32.4 KB
ID:	16061  
  #13   Spotlight this post!  
Unread 02-02-2014, 13:37
dvanvoorst dvanvoorst is offline
Registered User
FRC #2771 (Code Red)
Team Role: Mentor
 
Join Date: Jan 2012
Rookie Year: 2012
Location: Grand Rapids, MI
Posts: 61
dvanvoorst is an unknown quantity at this point
Re: PWM Signal

We've been running three Talons from one cable this season and haven't noticed anything unusual. It would be good to know if we're living on the edge, or are well within the normal operating capabilities.
  #14   Spotlight this post!  
Unread 02-02-2014, 14:33
Ether's Avatar
Ether Ether is offline
systems engineer (retired)
no team
 
Join Date: Nov 2009
Rookie Year: 1969
Location: US
Posts: 8,074
Ether has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond reputeEther has a reputation beyond repute
Re: PWM Signal

Quote:
Originally Posted by dvanvoorst View Post
We've been running three Talons from one cable this season and haven't noticed anything unusual. It would be good to know if we're living on the edge, or are well within the normal operating capabilities.
The evidence is starting to mount that doing this should be OK, but yes you are wise to want to confirm that. I will trying sending a PM to Mike Copioli to alert him to this thread and see if he can help.


Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 10:21.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi