philso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond repute
PDB question for Inspectors

This is a question for those of you who work as inspectors.

We have a tightly packed electronics panel. There is about a one inch gap between the power distribution board and a line of 4-5 motor controllers installed on each side. We have a bundle of PWM wires running through that gap that can obscure the LED's along the sides of the PDB from being viewed directly. If one of the LED's is on, we can still see a red glow between the wires. Would this pass inspection or should we re-route the wires now while we still can? The power wires to and from the motor controllers and the snap-action breakers are all clearly visible.

I can post a picture tomorrow evening if necessary.

Thanks.

Phil
  #2   Spotlight this post!  
Unread 10-02-2014, 01:13
Andy A. Andy A. is offline
Getting old
FRC #0095
Team Role: Coach
 
Join Date: Jun 2001
Rookie Year: 2001
Location: New Hampshire
Posts: 1,017
Andy A. has a reputation beyond reputeAndy A. has a reputation beyond reputeAndy A. has a reputation beyond reputeAndy A. has a reputation beyond reputeAndy A. has a reputation beyond reputeAndy A. has a reputation beyond reputeAndy A. has a reputation beyond reputeAndy A. has a reputation beyond reputeAndy A. has a reputation beyond reputeAndy A. has a reputation beyond reputeAndy A. has a reputation beyond repute
Re: PDB question for Inspectors

Visibility of the red 'open breaker' lights is not regulated by any rule, nor is it a inspection item. As long as the PDB (including status lights and 24v/12v/5v supply headers) and breakers are easily visible you're fine from a rules/inspection standpoint.
  #3   Spotlight this post!  
Unread 10-02-2014, 22:13
DonRotolo's Avatar
DonRotolo DonRotolo is offline
Back to humble
FRC #0832
Team Role: Mentor
 
Join Date: Jan 2005
Rookie Year: 2005
Location: Atlanta GA
Posts: 7,019
DonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond repute
Re: PDB question for Inspectors

I agree, we are inspecting for circuit breaker and wire visibility, not those little LEDs.

Of course, imagine you need to replace a motor controller: Can you? If not, you may benefit from some reconfiguration, otherwise you should be OK.
__________________

I am N2IRZ - What's your callsign?
  #4   Spotlight this post!  
Unread 11-02-2014, 07:29
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,798
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: PDB question for Inspectors

Phil,
The edge mounted LEDs are really bright and not a problem if you can't see them direct. Please post a picture, we love to look into other robots.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #5   Spotlight this post!  
Unread 12-02-2014, 00:52
philso philso is offline
Mentor
FRC #2587
 
Join Date: Jan 2011
Rookie Year: 2011
Location: Houston, Tx
Posts: 940
philso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond repute
Re: PDB question for Inspectors

Thanks for the feedback. We will probably add some cable ties to make the LED's more visible.

I just posted a link to some photos in another thread.

http://www.chiefdelphi.com/forums/sh...d.php?t=126291
  #6   Spotlight this post!  
Unread 12-02-2014, 07:45
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,798
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: PDB question for Inspectors

Phil,
Those photos don't look bad to me.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #7   Spotlight this post!  
Unread 12-02-2014, 13:46
MrRoboSteve MrRoboSteve is offline
Mentor
AKA: Steve Peterson
FRC #3081 (Kennedy RoboEagles)
Team Role: Mentor
 
Join Date: Mar 2012
Rookie Year: 2011
Location: Bloomington, MN
Posts: 582
MrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond repute
Re: PDB question for Inspectors

For PWM and other signal routing, I suggest avoiding the neighborhood of high current DC wiring (powerful motors, compressor), or crossing that wiring at right angles. You won't get dinged for that at inspection, but it improves the reliability of your robot.
__________________
2016-17 events: 10000 Lakes Regional, Northern Lights Regional, FTC Burnsville Qualifying Tournament

2011 - present · FRC 3081 Kennedy RoboEagles mentor
2013 - present · event volunteer at 10000 Lakes Regional, Northern Lights Regional, North Star Regional, Lake Superior Regional, Minnesota State Tournament, PNW District 4 Glacier Peak, MN FTC, CMP
http://twitter.com/MrRoboSteve · www.linkedin.com/in/speterson
  #8   Spotlight this post!  
Unread 12-02-2014, 14:30
MrRoboSteve MrRoboSteve is offline
Mentor
AKA: Steve Peterson
FRC #3081 (Kennedy RoboEagles)
Team Role: Mentor
 
Join Date: Mar 2012
Rookie Year: 2011
Location: Bloomington, MN
Posts: 582
MrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond reputeMrRoboSteve has a reputation beyond repute
Re: PDB question for Inspectors

One more thing: throw one of these in your toolbox.

http://www.amazon.com/s/ref=nb_sb_ss...ental%20mirror
__________________
2016-17 events: 10000 Lakes Regional, Northern Lights Regional, FTC Burnsville Qualifying Tournament

2011 - present · FRC 3081 Kennedy RoboEagles mentor
2013 - present · event volunteer at 10000 Lakes Regional, Northern Lights Regional, North Star Regional, Lake Superior Regional, Minnesota State Tournament, PNW District 4 Glacier Peak, MN FTC, CMP
http://twitter.com/MrRoboSteve · www.linkedin.com/in/speterson
  #9   Spotlight this post!  
Unread 12-02-2014, 14:34
philso philso is offline
Mentor
FRC #2587
 
Join Date: Jan 2011
Rookie Year: 2011
Location: Houston, Tx
Posts: 940
philso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond reputephilso has a reputation beyond repute
Re: PDB question for Inspectors

While it is best to not mix signal and power wiring, it is difficult, if not impossible to do when wiring devices that have both so one has to follow some common practices used in the Electrical and Electronics industries.

The least coupling that one can get between two wires IS when they cross at right angles. What one should avoid is running "sensitive" wires susceptible to external interference PARALLEL to wires likely to emit interference.
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 19:27.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi