Re: solenoid problems
no, no lights come on until a button is pushed
|
|
#2
|
|||
|
|||
|
Re: solenoid problems
Do you have enough pressure? Solenoids need about 30-40 psi to actuate.
|
|
#3
|
|||||
|
|||||
|
Re: solenoid problems
You say you have a 24v solenoid. From where are you providing power to the Solenoid Breakout?
|
|
#4
|
|||
|
|||
|
Re: solenoid problems
yes we do have enough pressure we are using about 60psi
and the solenoid breakout is being powered 20 amp breaker spot on the power distribution board. is this where we need to have it or do we need it to be pluged in somewhere else? |
|
#5
|
||||
|
||||
|
Re: solenoid problems
The 20 amp breaker spot is 12v.
|
|
#6
|
|||
|
|||
|
Re: solenoid problems
ok where do we need to hook it up to? thanks for letting me know.
|
|
#7
|
||||
|
||||
|
Re: solenoid problems
To the same place where the cRIO is wired on the PDB. There is 2 positive and 2 negative 24V terminals.
|
|
#8
|
|||
|
|||
|
ok i will try that tomorrow with some spare parts thanks for the advise i hope this fixes it
|
![]() |