Automation Direct double solenoid not working?

We recently acquired a couple of these solenoids http://www.automationdirect.com/adc/...)/AVS-3221-24D and have been having issues getting them to work. When we try to fire either side, the green indicator LED on the solenoid turns on and we hear a click but no air is let through. Our PCM is outputting 24V when it should and we have verified the rest of the pneumatic system works (everything works when we use a FESTO solenoid).

Does anyone who has used these solenoids before have an idea what we are doing wrong?
__________________
Team 8:
Paly Robotics
----------------
2016-present | Team Captain
2015-2016 | Build Captain
2014-2015 | Lab manager
2013-2014 | Build Team Member
----------------
  #2   Spotlight this post!  
Unread 09-12-2015, 23:57
orangemoore orangemoore is offline
Registered User
AKA: Roger Moore
FRC #3135 (Robotic Colonels)
Team Role: College Student
 
Join Date: Dec 2012
Rookie Year: 2013
Location: Chicago
Posts: 2,308
orangemoore has a reputation beyond reputeorangemoore has a reputation beyond reputeorangemoore has a reputation beyond reputeorangemoore has a reputation beyond reputeorangemoore has a reputation beyond reputeorangemoore has a reputation beyond reputeorangemoore has a reputation beyond reputeorangemoore has a reputation beyond reputeorangemoore has a reputation beyond reputeorangemoore has a reputation beyond reputeorangemoore has a reputation beyond repute
Re: Automation Direct double solenoid not working?

What pressure are you running them at?
__________________
Stronghold


Student 2013-2016
3135 -- Robotic Colonels
3507 -- Robotheosis (FTC)
  #3   Spotlight this post!  
Unread 10-12-2015, 00:03
Kenny Cheung Kenny Cheung is offline
Registered User
FRC #0008 (Team 8)
Team Role: Mechanical
 
Join Date: Jun 2015
Rookie Year: 2013
Location: California
Posts: 12
Kenny Cheung is an unknown quantity at this point
Re: Automation Direct double solenoid not working?

We are running them at 60 psi.
__________________
Team 8:
Paly Robotics
----------------
2016-present | Team Captain
2015-2016 | Build Captain
2014-2015 | Lab manager
2013-2014 | Build Team Member
----------------
  #4   Spotlight this post!  
Unread 10-12-2015, 00:03
ebarker's Avatar
ebarker ebarker is offline
Registered User
AKA: Ed Barker
FRC #1311 (Kell Robotics)
Team Role: Mentor
 
Join Date: Jan 2006
Rookie Year: 2006
Location: Kennesaw GA
Posts: 1,437
ebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond repute
Re: Automation Direct double solenoid not working?

Quote:
Originally Posted by Kenny Cheung View Post
We recently acquired a couple of these solenoids http://www.automationdirect.com/adc/...)/AVS-3221-24D and have been having issues getting them to work. When we try to fire either side, the green indicator LED on the solenoid turns on and we hear a click but no air is let through. Our PCM is outputting 24V when it should and we have verified the rest of the pneumatic system works (everything works when we use a FESTO solenoid).

Does anyone who has used these solenoids before have an idea what we are doing wrong?
I'm not an expert, which is a problem. But yes we bought the same solenoids and have the same problem.

The item you are looking for is the 52 series, not the 32 series. That will solve your problem.

Somewhere around here is an expert that can tell you the difference.
__________________
Ed Barker
  #5   Spotlight this post!  
Unread 10-12-2015, 00:05
Christopher149 Christopher149 is offline
Registered User
FRC #0857 (Superior Roboworks) FTC 10723 (SnowBots)
Team Role: Mentor
 
Join Date: Jan 2011
Rookie Year: 2007
Location: Houghton, MI
Posts: 1,100
Christopher149 has a reputation beyond reputeChristopher149 has a reputation beyond reputeChristopher149 has a reputation beyond reputeChristopher149 has a reputation beyond reputeChristopher149 has a reputation beyond reputeChristopher149 has a reputation beyond reputeChristopher149 has a reputation beyond reputeChristopher149 has a reputation beyond reputeChristopher149 has a reputation beyond reputeChristopher149 has a reputation beyond reputeChristopher149 has a reputation beyond repute
Re: Automation Direct double solenoid not working?

Quote:
Originally Posted by ebarker View Post
I'm not an expert, which is a problem. But yes we bought the same solenoids and have the same problem.

The item you are looking for is the 52 series, not the 32 series. That will solve your problem.

Somewhere around here is an expert that can tell you the difference.
Not an expert, but is the difference 5-port/2 way versus 3-port/2-way?
__________________
2015-present: FTC 10723 mentor
2012-present: 857 mentor
2008-2011: 857 student

2015: Industrial Design, Excellence in Engineering, District Finalist, Archimedes Division (#6 alliance captain)
2014: Judges Award, District Engineering Inspiration, District Finalist, Galileo Division

  #6   Spotlight this post!  
Unread 10-12-2015, 00:14
AllenGregoryIV's Avatar
AllenGregoryIV AllenGregoryIV is offline
Engineering Coach
AKA: Allen "JAG" Gregory
FRC #3847 (Spectrum)
Team Role: Coach
 
Join Date: Jul 2008
Rookie Year: 2003
Location: Texas
Posts: 2,551
AllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond repute
Send a message via AIM to AllenGregoryIV
Re: Automation Direct double solenoid not working?

A 3 way value can only control one side of a cylinder, they work for single acting spring return cylinders. It opens and exhausts a single line.

A 5 port or 4 way value is used for double acting cylinders.

This FAQ can help.
__________________

Team 647 | Cyber Wolf Corps | Alumni | 2003-2006 | Shoemaker HS
Team 2587 | DiscoBots | Mentor | 2008-2011 | Rice University / Houston Food Bank
Team 3847 | Spectrum | Coach | 2012-20... | St Agnes Academy
LRI | Alamo Regional | 2014-20...
"Competition has been shown to be useful up to a certain point and no further, but cooperation, which is the thing we must strive for today, begins where competition leaves off." - Franklin D. Roosevelt
  #7   Spotlight this post!  
Unread 10-12-2015, 00:34
Nebster's Avatar
Nebster Nebster is offline
Registered User
AKA: Ben Kishter
FRC #1306 (BadgerBOTS)
Team Role: Alumni
 
Join Date: Jan 2013
Rookie Year: 2012
Location: Madison, Wisconsin
Posts: 60
Nebster is an unknown quantity at this point
Re: Automation Direct double solenoid not working?

You might want these .
__________________
2015 Wisconsin Regional Chairman's Award - Carson Division

2013 Wisconsin Regional Chairman's Award - Curie Division
  #8   Spotlight this post!  
Unread 10-12-2015, 09:41
ebarker's Avatar
ebarker ebarker is offline
Registered User
AKA: Ed Barker
FRC #1311 (Kell Robotics)
Team Role: Mentor
 
Join Date: Jan 2006
Rookie Year: 2006
Location: Kennesaw GA
Posts: 1,437
ebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond repute
Re: Automation Direct double solenoid not working?

Quote:
Originally Posted by Nebster View Post
You might want these .
That's what we use, the 52 series
http://www.automationdirect.com/adc/Shopping/Catalog/Pneumatic_Components/Pneumatic_Valves_-a-_Accessories/General_Purpose_Solenoid_Directional_Control_Air_V alves/5-port_(4-way),_2-pos.,_Body_Ported_-z-_Manifold_(AVS-5,AM_Series)

we have both the single and double solenoid versions.,,, we generally use the single solenoid

love 'em
__________________
Ed Barker
  #9   Spotlight this post!  
Unread 10-12-2015, 10:23
FrankJ's Avatar
FrankJ FrankJ is offline
Robot Mentor
FRC #2974 (WALT)
Team Role: Mentor
 
Join Date: Feb 2011
Rookie Year: 2009
Location: Marietta GA
Posts: 1,923
FrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond repute
Re: Automation Direct double solenoid not working?

I expect they are pilot operated valve. The solenoid is basically a little valve that operates the spool. If you do not have pressure on the pressure port, they will not work.
__________________
If you don't know what you should hook up then you should read a data sheet
  #10   Spotlight this post!  
Unread 10-12-2015, 14:48
rfolea's Avatar
rfolea rfolea is offline
Registered User
AKA: Rick Folea
no team (Forsyth Alliance)
Team Role: Mentor
 
Join Date: May 2005
Rookie Year: 2005
Location: US
Posts: 210
rfolea has a brilliant futurerfolea has a brilliant futurerfolea has a brilliant futurerfolea has a brilliant futurerfolea has a brilliant futurerfolea has a brilliant futurerfolea has a brilliant futurerfolea has a brilliant futurerfolea has a brilliant futurerfolea has a brilliant futurerfolea has a brilliant future
Re: Automation Direct double solenoid not working?

Did this get resolved?

I work at AutomationDirect and would be happy to help you get up and running.
  #11   Spotlight this post!  
Unread 10-12-2015, 23:33
Kenny Cheung Kenny Cheung is offline
Registered User
FRC #0008 (Team 8)
Team Role: Mechanical
 
Join Date: Jun 2015
Rookie Year: 2013
Location: California
Posts: 12
Kenny Cheung is an unknown quantity at this point
Re: Automation Direct double solenoid not working?

Thanks for all the help! I think we have a solid theoretical understanding of what we did wrong. Unfortunately we won't have a chance to mess around with it for a while with finals and winter break coming up. If we continue to run into issues later on we will be sure to check back.
__________________
Team 8:
Paly Robotics
----------------
2016-present | Team Captain
2015-2016 | Build Captain
2014-2015 | Lab manager
2013-2014 | Build Team Member
----------------
  #12   Spotlight this post!  
Unread 11-12-2015, 10:11
GeeTwo's Avatar
GeeTwo GeeTwo is offline
Technical Director
AKA: Gus Michel II
FRC #3946 (Tiger Robotics)
Team Role: Mentor
 
Join Date: Jan 2014
Rookie Year: 2013
Location: Slidell, LA
Posts: 3,609
GeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond repute
Re: Automation Direct double solenoid not working?

If you have enough of them, as quick workaround, you can use two of the 32 series valves to simulate one 52 series valve. Cross the wires between the two valves so that when one is pressurized, the other is venting, and use one for each half of the cylinder(s).
__________________

If you can't find time to do it right, how are you going to find time to do it over?
If you don't pass it on, it never happened.
Robots are great, but inspiration is the reason we're here.
Friends don't let friends use master links.
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 17:11.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi