  #1   Spotlight this post!  
Unread 27-02-2016, 05:32
Tristan Lall's Avatar
Tristan Lall Tristan Lall is offline
Registered User
FRC #0188 (Woburn Robotics)
 
Join Date: Aug 2001
Rookie Year: 1999
Location: Toronto, ON
Posts: 2,484
Tristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond repute
Re: Pneumatic Regulators from Automation Direct

I'm inclined to continue using the past interpretation of the rule to resolve the Norgren issue in favour of legality. Since a Norgren R07-100-RNEA regulator can frequently1 be adjusted above 50 lb/in2 (the manufacturer's operating limit2) and even above 60 lb/in2 (the R77-I limit) using the provided control knob, and FIRST should know this, I would interpret the "maximum outlet pressure" to mean the maximum non-transient pressure at the outlet given a certain user-adjusted setting, rather than the manufacturer's published operating limits or proof limits. This also permits R75 to be read without conflict: the "working pressure" referenced there should be interpreted in terms of the possible range of input pressures, not the adjustment range of the outlet.

Using that logic, the AutomationDirect valve, the Nitra AR-213 is also legal. For R77-I, you must adjust its outlet to 60 lb/in2 or less, and the datasheet states this is possible. For R75, the "working pressure" at the inlet should be no more than 145 lb/in2 if like the Norgren, you may operate it in excess of recommendations, or no more than 130 lb/in2 if you must stay within the manufacturer's range. Either figure satisfies R75.

Also, for anyone concerned about unsafe failure of the regulator, Nitra conveniently provides proof limits: below 215 lb/in2, you should not expect the regulator to fail catastrophically.

For better or worse, guidance provided to LRIs is not inherently a rule, and cannot be enforced.

1I don't know what the production variation is on the physical limit of adjustment, so perhaps I'm relying on outliers to reach that impression.
2 For regular customers at least. I seem to recall, but can't document, a Q&A from the early 2000s alluding to Norgren telling FIRST that operating this regulator up to 60 lb/in2 was acceptable.

Last edited by Tristan Lall : 27-02-2016 at 05:35.
  #2   Spotlight this post!  
Unread 29-02-2016, 10:00
martin417's Avatar
martin417 martin417 is offline
Opinionated old goat
AKA: Martin Wilson
no team
Team Role: Mentor
 
Join Date: Feb 2008
Rookie Year: 2008
Location: Buford, GA
Posts: 718
martin417 has a reputation beyond reputemartin417 has a reputation beyond reputemartin417 has a reputation beyond reputemartin417 has a reputation beyond reputemartin417 has a reputation beyond reputemartin417 has a reputation beyond reputemartin417 has a reputation beyond reputemartin417 has a reputation beyond reputemartin417 has a reputation beyond reputemartin417 has a reputation beyond reputemartin417 has a reputation beyond repute
Re: Pneumatic Regulators from Automation Direct

Has anybody submitted a Q&A on this topic? Would be nice to get clarification before the next event.
__________________
Former Mentor Team 1771
Former mentor Team 4509
  #3   Spotlight this post!  
Unread 29-02-2016, 10:06
Holtzman's Avatar
Holtzman Holtzman is offline
Sometimes...
AKA: Tyler Holtzman
FRC #2056 (OP Robotics)
Team Role: Engineer
 
Join Date: Apr 2003
Rookie Year: 2003
Location: St. Catharines
Posts: 178
Holtzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond repute
Send a message via MSN to Holtzman
Re: Pneumatic Regulators from Automation Direct

Quote:
Originally Posted by martin417 View Post
Has anybody submitted a Q&A on this topic? Would be nice to get clarification before the next event.
Yes.
__________________
"making the simple complicated is commonplace; making the complicated simple, awesomely simple, that's creativity." - Charles Mingus
  #4   Spotlight this post!  
Unread 29-02-2016, 11:43
FrankJ's Avatar
FrankJ FrankJ is offline
Robot Mentor
FRC #2974 (WALT)
Team Role: Mentor
 
Join Date: Feb 2011
Rookie Year: 2009
Location: Marietta GA
Posts: 1,875
FrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond repute
Re: Pneumatic Regulators from Automation Direct

Quote:
Originally Posted by Holtzman View Post
Yes.
It might be good to point out to the Q&A people that the recommended regulator can be adjusted to above 60 PSI.
__________________
If you don't know what you should hook up then you should read a data sheet
  #5   Spotlight this post!  
Unread 29-02-2016, 11:46
Holtzman's Avatar
Holtzman Holtzman is offline
Sometimes...
AKA: Tyler Holtzman
FRC #2056 (OP Robotics)
Team Role: Engineer
 
Join Date: Apr 2003
Rookie Year: 2003
Location: St. Catharines
Posts: 178
Holtzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond reputeHoltzman has a reputation beyond repute
Send a message via MSN to Holtzman
Re: Pneumatic Regulators from Automation Direct

Quote:
Originally Posted by FrankJ View Post
It might be good to point out to the Q&A people that the recommended regulator can be adjusted to above 60 PSI.
Ya, the original question was quite a bit longer and pointed out all the important details touched on in this thread. There is a character limit on q and a's that made adding more details impossible though.

I could have linked this thread, but I suspect the deciding parties are already aware of whats been stated here.
__________________
"making the simple complicated is commonplace; making the complicated simple, awesomely simple, that's creativity." - Charles Mingus

Last edited by Holtzman : 29-02-2016 at 11:56.
  #6   Spotlight this post!  
Unread 29-02-2016, 13:55
AllenGregoryIV's Avatar
AllenGregoryIV AllenGregoryIV is offline
Engineering Coach
AKA: Allen "JAG" Gregory
FRC #3847 (Spectrum)
Team Role: Coach
 
Join Date: Jul 2008
Rookie Year: 2003
Location: Texas
Posts: 2,545
AllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond repute
Send a message via AIM to AllenGregoryIV
Re: Pneumatic Regulators from Automation Direct

Quote:
Originally Posted by Holtzman View Post
Ya, the original question was quite a bit longer and pointed out all the important details touched on in this thread. There is a character limit on q and a's that made adding more details impossible though.

I could have linked this thread, but I suspect the deciding parties are already aware of whats been stated here.
Yeah I've been trying to get them to remove or at least liberally increase the character limit for a couple years. I think they made it a bit larger last year but still not good enough. VEX Q&A forum is still better at this, they can post photos and things to help communicate their questions.
__________________

Team 647 | Cyber Wolf Corps | Alumni | 2003-2006 | Shoemaker HS
Team 2587 | DiscoBots | Mentor | 2008-2011 | Rice University / Houston Food Bank
Team 3847 | Spectrum | Coach | 2012-20... | St Agnes Academy
LRI | Alamo Regional | 2014-20...
"Competition has been shown to be useful up to a certain point and no further, but cooperation, which is the thing we must strive for today, begins where competition leaves off." - Franklin D. Roosevelt
  #7   Spotlight this post!  
Unread 01-03-2016, 11:19
FrankJ's Avatar
FrankJ FrankJ is offline
Robot Mentor
FRC #2974 (WALT)
Team Role: Mentor
 
Join Date: Feb 2011
Rookie Year: 2009
Location: Marietta GA
Posts: 1,875
FrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond reputeFrankJ has a reputation beyond repute
Re: Pneumatic Regulators from Automation Direct

Q & A has spoken with much appreciated clarity.

Quote:
Q. Is the intent of R77I to limit teams to only using Pressure regulators with a published operating range of less than 60 PSI, or is this meant to allow regulators with an operating range above 60 PSI provided they are adjusted such that the working pressure is at or below 60PSI?
2016-02-27 by FRC2056
A. The meaning of R77-I was unclear, sorry about that. It will be revised in Team Update 14 to allow pressure regulators with the outlet pressure adjusted to 60 psi or less. Regulators with an operating range above 60 psi will be allowed provided they are adjusted to no more than 60 psi.
__________________
If you don't know what you should hook up then you should read a data sheet
  #8   Spotlight this post!  
Unread 01-03-2016, 11:29
Jon Stratis's Avatar
Jon Stratis Jon Stratis is offline
Electrical/Programming Mentor
FRC #2177 (The Robettes)
Team Role: Mentor
 
Join Date: Feb 2007
Rookie Year: 2006
Location: Minnesota
Posts: 3,717
Jon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond reputeJon Stratis has a reputation beyond repute
Re: Pneumatic Regulators from Automation Direct

And that just made inspecting pneumatic systems a lot easier than it was looking over the past week!
__________________
2007 - Present: Mentor, 2177 The Robettes
LRI: North Star 2012-2016; Lake Superior 2013-2014; MN State Tournament 2013-2014, 2016; Galileo 2016; Iowa 2017
2015: North Star Regional Volunteer of the Year
2016: Lake Superior WFFA
  #9   Spotlight this post!  
Unread 01-03-2016, 11:36
Unsung FIRST Hero
Karthik Karthik is offline
VEX Robotics GDC Chairman
no team
Team Role: Mentor
 
Join Date: Apr 2002
Rookie Year: 1998
Location: Toronto, Ontario, Canada
Posts: 2,339
Karthik has a reputation beyond reputeKarthik has a reputation beyond reputeKarthik has a reputation beyond reputeKarthik has a reputation beyond reputeKarthik has a reputation beyond reputeKarthik has a reputation beyond reputeKarthik has a reputation beyond reputeKarthik has a reputation beyond reputeKarthik has a reputation beyond reputeKarthik has a reputation beyond reputeKarthik has a reputation beyond repute
Re: Pneumatic Regulators from Automation Direct

Quote:
Originally Posted by Jon Stratis View Post
And that just made inspecting pneumatic systems a lot easier than it was looking over the past week!
Indeed. This was a smart answer fueled by common sense on the part of the GDC. Definitely helpful to teams and volunteers alike.
__________________
:: Karthik Kanagasabapathy ::
"Enthusiasm is one of the most powerful engines of success. When you do a thing, do it with all your might. Put your whole soul into it. Stamp it with your own personality. Be active, be energetic, be enthusiastic and faithful and you will accomplish your object. Nothing great was ever achieved without enthusiasm" -- R.W. Emerson
My TEDx Talk - The Subtle Secrets of Success
Full disclosure: I work for IFI and VEX Robotics, and am the Chairman of the VEX Robotics and VEX IQ Game Design Committees
.
  #10   Spotlight this post!  
Unread 01-03-2016, 11:38
Paul Copioli's Avatar Unsung FIRST Hero Woodie Flowers Award
Paul Copioli Paul Copioli is offline
President, VEX Robotics, Inc.
FRC #3310 (Black Hawk Robotics)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 2000
Location: Rockwall, TX
Posts: 1,381
Paul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond repute
Re: Pneumatic Regulators from Automation Direct

Once again the GDC under Frank Merrick's leadership is the most professional and most reasonable during all my years of participating in FRC.

The practical and team centric approach that FRC has been taking during the "Frank Era" of FRC is very much appreciated.

What a courteous and professional response.

Paul
__________________
In full disclosure I am the President of VEX Robotics, a division of Innovation First International.
  #11   Spotlight this post!  
Unread 01-03-2016, 11:53
Ryan Dognaux's Avatar
Ryan Dognaux Ryan Dognaux is offline
FRC Video Review - Change is Coming
FRC #4329 (Lutheran Roboteers)
Team Role: Coach
 
Join Date: Apr 2002
Rookie Year: 2001
Location: St. Charles, MO
Posts: 2,673
Ryan Dognaux has a reputation beyond reputeRyan Dognaux has a reputation beyond reputeRyan Dognaux has a reputation beyond reputeRyan Dognaux has a reputation beyond reputeRyan Dognaux has a reputation beyond reputeRyan Dognaux has a reputation beyond reputeRyan Dognaux has a reputation beyond reputeRyan Dognaux has a reputation beyond reputeRyan Dognaux has a reputation beyond reputeRyan Dognaux has a reputation beyond reputeRyan Dognaux has a reputation beyond repute
Send a message via AIM to Ryan Dognaux
Re: Pneumatic Regulators from Automation Direct

Are there any other 'less used but legal' pneumatics components that Automation Direct sells? We have a ton of old dials, regulators, brass fittings, etc. and I'd like to know some of the parts you guys have found to be better for FRC applications. Thanks for posting this to the Q&A!
__________________
Ryan Dognaux :: Last Name Pronounced 'Doane Yo'
Team 234 Alum: 2002 - 2005 :: Purdue FIRST Member: 2006 - 2009
Team 1646 Mentor: 2007 - 2009 :: Team 357 Mentor: 2009 - 2012
Team 4329 Mentor: Current
STL Off-Season Event: www.gatewayroboticschallenge.com
  #12   Spotlight this post!  
Unread 01-03-2016, 12:42
AllenGregoryIV's Avatar
AllenGregoryIV AllenGregoryIV is offline
Engineering Coach
AKA: Allen "JAG" Gregory
FRC #3847 (Spectrum)
Team Role: Coach
 
Join Date: Jul 2008
Rookie Year: 2003
Location: Texas
Posts: 2,545
AllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond reputeAllenGregoryIV has a reputation beyond repute
Send a message via AIM to AllenGregoryIV
Re: Pneumatic Regulators from Automation Direct

Quote:
Originally Posted by Ryan Dognaux View Post
Are there any other 'less used but legal' pneumatics components that Automation Direct sells? We have a ton of old dials, regulators, brass fittings, etc. and I'd like to know some of the parts you guys have found to be better for FRC applications. Thanks for posting this to the Q&A!
Inline regulators and gauges could be useful if you need weight or space.

Quick exhaust valves are legal for the first time this year.

3 Way exhaust valves are also legal this year for closing off sections of pneumatics

Not from automation direct but McMaster and other sources carry tiny gauges (paintball sized) that are lighter. You can also get aluminum and plastic manifolds as well.
__________________

Team 647 | Cyber Wolf Corps | Alumni | 2003-2006 | Shoemaker HS
Team 2587 | DiscoBots | Mentor | 2008-2011 | Rice University / Houston Food Bank
Team 3847 | Spectrum | Coach | 2012-20... | St Agnes Academy
LRI | Alamo Regional | 2014-20...
"Competition has been shown to be useful up to a certain point and no further, but cooperation, which is the thing we must strive for today, begins where competition leaves off." - Franklin D. Roosevelt
  #13   Spotlight this post!  
Unread 01-03-2016, 13:05
bachster's Avatar
bachster bachster is offline
Registered User
AKA: Katie Bach
FRC #2052 (KnightKrawler)
Team Role: Mentor
 
Join Date: Jan 2009
Rookie Year: 2008
Location: Minneapolis
Posts: 61
bachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant future
Re: Pneumatic Regulators from Automation Direct

If using these, just remember that you still must meet R89:

Quote:
Originally Posted by R89
Any pressure vent plug must be:

A. connected to the pneumatic circuit such that, when manually operated, it will vent to the atmosphere to relieve all stored pressure in a reasonable amount of time, and

B. placed on the ROBOT so that it is visible and easily accessible.

If the compressor is not used on the ROBOT, then an additional pressure vent plug must be connected to the high-pressure portion of the pneumatic circuit off-board the ROBOT with the
compressor (see R80).
Does anyone have an example of a useful application for the 3-way exhaust valve?
__________________
Mentor, FRC 2052 KnightKrawler: 2008 - Present
Robot Inspector: 2013 - Present
LRI, Minnesota 10,000 Lakes Regional: 2016
  #14   Spotlight this post!  
Unread 01-03-2016, 12:24
bachster's Avatar
bachster bachster is offline
Registered User
AKA: Katie Bach
FRC #2052 (KnightKrawler)
Team Role: Mentor
 
Join Date: Jan 2009
Rookie Year: 2008
Location: Minneapolis
Posts: 61
bachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant futurebachster has a brilliant future
Re: Pneumatic Regulators from Automation Direct

Quote:
Originally Posted by Paul Copioli View Post
The practical and team centric approach that FRC has been taking during the "Frank Era" of FRC is very much appreciated.

What a courteous and professional response.

Paul
100% agreed. Thanks also to all of the professional comments in this thread which helped to provide well-reasoned technical insight. This is a great update which benefits teams, RI's and LRI's. Now we can go back to worrying about more exciting things like bumpers and bagging two "robots."
__________________
Mentor, FRC 2052 KnightKrawler: 2008 - Present
Robot Inspector: 2013 - Present
LRI, Minnesota 10,000 Lakes Regional: 2016
  #15   Spotlight this post!  
Unread 01-03-2016, 12:36
Kellen Hill's Avatar
Kellen Hill Kellen Hill is offline
Strategist
AKA: The user formerly known as 'hill'
FRC #1746 (OTTO)
Team Role: Mentor
 
Join Date: Mar 2005
Rookie Year: 2005
Location: Cumming, GA
Posts: 479
Kellen Hill has a reputation beyond reputeKellen Hill has a reputation beyond reputeKellen Hill has a reputation beyond reputeKellen Hill has a reputation beyond reputeKellen Hill has a reputation beyond reputeKellen Hill has a reputation beyond reputeKellen Hill has a reputation beyond reputeKellen Hill has a reputation beyond reputeKellen Hill has a reputation beyond reputeKellen Hill has a reputation beyond reputeKellen Hill has a reputation beyond repute
Re: Pneumatic Regulators from Automation Direct

Great news! We used the setup below for our robot last year and really liked it compared to massive regulators involving brass and large gauges.



Regulator

Pressure Gauge
__________________
1625 Winnovation Member: 2005-07
1625 College Mentor: 2007-11
525 Swartdogs Mentor: 2011-12
1746 OTTO Lead Mentor: 2013-Present
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 17:31.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi