Pneumatic assistance

We need help. We have turned everywhere and no one has been able to help us. The compressor comes on but none of the solenoids are working. We have had the code checked out and that is fine. How do we test it? We bought a new PCM and put it in, it has changed nothing. Thanks!
  #2   Spotlight this post!  
Unread 02-03-2016, 22:11
Brian662 Brian662 is offline
Registered User
FRC #0662 (Rocky Mountain Robotics)
Team Role: College Student
 
Join Date: Feb 2016
Rookie Year: 2009
Location: Colorado
Posts: 4
Brian662 is an unknown quantity at this point
Re: Pneumatic assistance

Are you specifying the PCM ID in the code? Our team had a similar problem but we weren't specifying a PCM ID.
  #3   Spotlight this post!  
Unread 02-03-2016, 22:15
Kyle Heaton's Avatar
Kyle Heaton Kyle Heaton is offline
I like volunteering.
FRC #0045 (TechnoKats)
Team Role: Leadership
 
Join Date: May 2014
Rookie Year: 2014
Location: Indiana, USA
Posts: 23
Kyle Heaton will become famous soon enough
Re: Pneumatic assistance

Is your PCM connected with CAN wires properly?

Are you correctly opening and setting values for the solenoids?
Are your solenoids single or double, as that will change what values you need to send to them for them to trigger.
__________________
Software Lead Student 2014-2015
Student Technical Lead 2015-2016


Tippecanoe District Winner - Perry Meridian District Winner - District Champs Semifinalists

Kokomo District Quarterfinalists - Dean's List Indiana District Finalist

Arkansas Regional Quarterfinalists - Boilermaker Regional Quarterfinalists
  #4   Spotlight this post!  
Unread 02-03-2016, 22:30
Peyton Yeung's Avatar
Peyton Yeung Peyton Yeung is offline
45 Alumni
AKA: Peyton Yeung
FRC #0461 (Westside Boiler Invasion)
Team Role: Coach
 
Join Date: Mar 2010
Rookie Year: 2009
Location: Kokomo, IN
Posts: 810
Peyton Yeung has a reputation beyond reputePeyton Yeung has a reputation beyond reputePeyton Yeung has a reputation beyond reputePeyton Yeung has a reputation beyond reputePeyton Yeung has a reputation beyond reputePeyton Yeung has a reputation beyond reputePeyton Yeung has a reputation beyond reputePeyton Yeung has a reputation beyond reputePeyton Yeung has a reputation beyond reputePeyton Yeung has a reputation beyond reputePeyton Yeung has a reputation beyond repute
Re: Pneumatic assistance

Is your PCM set to the same voltage that your solenoids are?
__________________
461 Westside Boiler Invasion
2016 Tippy Quarter finalist, Warren Finalist, IN State Semi Finalist,B^3 Double Finalist
2015 Indy Semi finalist, Purdue Quarter Finalist, IN State Quarter Finalist, CORI QF, R2OC Finalist, RAGE Winner
2014 Boilermaker Semi finalist, Crossroads Quarter Finalist, & CAGE Quarter Finalist
45 Technokats
2013 Boilermaker Quarter finalist
2012 CAGE Semi finalist & Queen City Champion
2011 CAGE Quarter finalist & Midwest Semi finalist
2010 CAGE Quarter finalist, Boilermaker Champion, & Washington DC Quarter Finalist
  #5   Spotlight this post!  
Unread 03-03-2016, 00:37
Jaxom Jaxom is offline
Registered User
AKA: Michael Hartwig
FRC #1986 (Team Titanium)
Team Role: Mentor
 
Join Date: Apr 2010
Rookie Year: 2008
Location: Lee's Summit, MO
Posts: 378
Jaxom has a brilliant futureJaxom has a brilliant futureJaxom has a brilliant futureJaxom has a brilliant futureJaxom has a brilliant futureJaxom has a brilliant futureJaxom has a brilliant futureJaxom has a brilliant futureJaxom has a brilliant futureJaxom has a brilliant futureJaxom has a brilliant future
Re: Pneumatic assistance

Do your solenoids work if you trigger them manually?
__________________


Mentor http://www.teamtitanium.org/
  #6   Spotlight this post!  
Unread 03-03-2016, 06:35
DaveL DaveL is offline
Registered User
FRC #2976
 
Join Date: Jan 2013
Location: WA
Posts: 173
DaveL is a jewel in the roughDaveL is a jewel in the roughDaveL is a jewel in the roughDaveL is a jewel in the rough
Re: Pneumatic assistance

Are you powering the working part of the system with over 30 psi?
Some valves need this to work.

Are you giving the valves the correct voltage?
There are 12v and 24v valves.

Are you sending pressure to one or both sides of the cylinder?
Try testing with tubing connected to both extend and retract sides of the cylinder.

Install manual dump valves and use these to verify that air is getting to the valve ports.

There is an input and an output side to most valves. Find the valve part number and look up the part to verify.

You can always call that valve's distributor, for info about the valve.
Dave

Last edited by DaveL : 03-03-2016 at 06:35. Reason: wording
  #7   Spotlight this post!  
Unread 03-03-2016, 09:16
GeeTwo's Avatar
GeeTwo GeeTwo is offline
Technical Director
AKA: Gus Michel II
FRC #3946 (Tiger Robotics)
Team Role: Mentor
 
Join Date: Jan 2014
Rookie Year: 2013
Location: Slidell, LA
Posts: 3,555
GeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond reputeGeeTwo has a reputation beyond repute
Re: Pneumatic assistance

A complete set of pictures of how you're wired and plumbed would help.

I suggest adding a pressure valve close to the inlet of a valve to ensure that you have pilot pressure. Due to some strange plumbing, on our first iteration, once we made the initial switch from initial to "gameplay" configuration, we were dumping air so fast that we lost pilot pressure.

Watch all of your diagnostic lights (most solenoid valves have these) to see if the solenoids are getting the signal; this will tell you if your problem is on the electrical side or pneumatic side.

Some solenoid valves have polarized inputs. Reverse voltage will usually not damage them, but they won't function. Check this out. (IIRC, we have at least one solenoid valve which, if wired backwards, will light the LED but not actuate the valve; seems really strange, but there it is.)

Try the manual switch buttons/levers (most solenoid valves have these). This will also help you figure out whether you have an electrical or pneumatic side problem. (If things work with the manual, it's almost certainly electrical; if they don't, it's almost certainly pneumatic.)
__________________

If you can't find time to do it right, how are you going to find time to do it over?
If you don't pass it on, it never happened.
Robots are great, but inspiration is the reason we're here.
Friends don't let friends use master links.
  #8   Spotlight this post!  
Unread 03-03-2016, 09:31
Mark McLeod's Avatar
Mark McLeod Mark McLeod is online now
Just Itinerant
AKA: Hey dad...Father...MARK
FRC #0358 (Robotic Eagles)
Team Role: Engineer
 
Join Date: Mar 2003
Rookie Year: 2002
Location: Hauppauge, Long Island, NY
Posts: 8,713
Mark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond reputeMark McLeod has a reputation beyond repute
Re: Pneumatic assistance

Divide the problem into code vs electrical/pneumatic.

Correct code: The PCM individual solenoid LEDs light up red when your code functions, and the lights are properly matched, e.g., one side of a double solenoid is off while the opposing side is on, then your code is operating properly. Get this working first.
__________________
"Rationality is our distinguishing characteristic - it's what sets us apart from the beasts." - Aristotle
  #9   Spotlight this post!  
Unread 09-03-2016, 11:17
JOomkes JOomkes is offline
Registered User
FRC #4967
 
Join Date: Jan 2016
Location: Grand Rapids
Posts: 1
JOomkes is an unknown quantity at this point
Re: Pneumatic assistance

You may want to check that you are not overloading the PCM. If you are using too many valves at 12 volts with to high an amperage, you can replace them with a 24 volt and a lower amperage that will do the same thing but not overload the PCM. Running on either 12 or 24 volts you need to also make sure that all of the solenoids are that same voltage. We had a problem with this on our robot.
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 22:20.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi