Go to Post ChiefDelphi is talking about women's clothing. What a time to be alive. - Karibou [more]
Unread 14-03-2016, 16:07
Oblarg Oblarg is offline
AKA: Eli Barnett
Velocity PID control and setpoint ramping
For the first time, 449 is running a drive with velocity PID control (well, actually P control with a simple integrator on the output).
On the whole we are quite happy with it, but various people have noticed that driving with it can be a bit "jerky" and violent compared to standard controls. Namely, if the driver lets go of the joystick while the robot is moving full speed, the control loop will (as it should) stop the robot as fast as possible (which is actually pretty close to instantaneously, it seems). This is not something we're used to, and has caused some concern, though it has gotten better with additional driver practice.
Additionally, we managed to shear all the teeth off of the 14-tooth gear in one of our WCP SS gearboxes at our last event. We're replacing these with steel gears, but we're also concerned that the sudden stops are placing additional stress on the drive, and as we only have steel replacements for the 14-tooth gears (and not for the 60-tooth gears meshing with them) we'd like to err on the side of caution.
So, we're looking at potentially implementing a setpoint ramp to tame it a bit. I was wondering if other teams have had any experience with this, and if they found setpoint ramping to be a necessary/helpful addition and, if so, what ramp rates they found to work best.
EDIT: We're handling our PIDs using the PIDSubsystem object in WPILib.
"The breakfast of champions!"
Unread 14-03-2016, 16:33
Pault's Avatar
Pault Pault is offline
FRC #0246 (Overclocked)
Pault has a reputation beyond reputePault has a reputation beyond reputePault has a reputation beyond reputePault has a reputation beyond reputePault has a reputation beyond reputePault has a reputation beyond reputePault has a reputation beyond reputePault has a reputation beyond reputePault has a reputation beyond reputePault has a reputation beyond reputePault has a reputation beyond repute
Re: Velocity PID control and setpoint ramping
If the problem is just when the robot stops, I would actually recommend that you use a smaller proportional value whenever the commanded speed is close to zero. This will make the drivetrain drift more if your drivers want it to. It should also stop ruining your gears; they are probably being worn down by constantly oscillating back and forth when trying to stop, but when PIDing to a non-zero value they shouldn't see any abnormal loads.
Unread 14-03-2016, 16:36
Hitchhiker 42's Avatar
Hitchhiker 42 Hitchhiker 42 is offline
Roboter
AKA: Mark Lavrentyev
FRC #4557 (FullMetal Falcons)
Rookie Year: 2015
Hitchhiker 42 is a splendid one to beholdHitchhiker 42 is a splendid one to beholdHitchhiker 42 is a splendid one to beholdHitchhiker 42 is a splendid one to beholdHitchhiker 42 is a splendid one to beholdHitchhiker 42 is a splendid one to beholdHitchhiker 42 is a splendid one to beholdHitchhiker 42 is a splendid one to behold
I am pretty sure that there is a velocity ramp function for Talon SRX, where you can make a max ramp steepness, so that there is less jerkiness.
2016 - NE District Championship Entrepreneurship Award
2016 - Hartford District Industrial Design Award
2016 - Waterbury District Engineering Inspiration Award
Unread 14-03-2016, 16:37
AKA: Eli Barnett
Is there any convenient way to do this using the standard WPILib PIDSubsystem object?
We're doing our PID on the RoboRio, not on the motor controllers. Since our PID output is integrated we can implement a voltage ramp rate using the default setOutputRange() function, but I've heard that input ramping is a better way of handling this than output ramping.
Unread 14-03-2016, 16:48
Roboter
Rookie Year: 2015
We use LabVIEW, and this VI is probably what does the trick.
I am sure that this method is available in Java and C++.
Pault's Avatar
Inside of the execute method of the command running your drivetrain:
if(commandedSetpoint < some value that is close to 0) {
   yourSubsystem.getPIDController().setPID(small kP, kI, kD);
} else {
   yourSubsystem.getPIDController().setPID(normal kP, kI, kD);
Unread 14-03-2016, 16:49
AKA: Eli Barnett
} else {
Ah, didn't know there was a method to change the PID values after instantiating the object. Thanks! We'll give this a look, too.
Unread 14-03-2016, 17:02
MrNick's Avatar
MrNick MrNick is offline
FRC #0088 (TJ^2)
MrNick is an unknown quantity at this point
Are you using TalonSRX's with their built in PID control? If so, I highly recommend following the procedure for tuning PID in the Talon user guide. We have been doing things in a way similar to you (mostly P) and had similar results. Then we got the great advice to try things "by the book". That means starting with 0's all around for PID and upping the F, feed forward, term until you get the speed you expect based on your input. Then use PID to tune that. Drive is much smoother now.
2016 Granite State District Event Winner
Unread 14-03-2016, 17:05
AKA: Eli Barnett
We're not using the TalonSRX PID, we're handling it all using code available from the Command-based framework in WPILib.
Since we're using an integrator on our output, we can't really use the supported feedforward term. We could implement our own, but I'm not sure the lack of a feedforward term is what's causing problems.
Unread 14-03-2016, 20:01
]Since we're using an integrator on our output, we can't really use the supported feedforward term. We could implement our own, but I'm not sure the lack of a feedforward term is what's causing problems.
Consider what would happen if you added feedforward and took the output of the FPID directly to control the motor rather than integrating it.
Unread 14-03-2016, 20:20
AKA: Eli Barnett
This would certainly be another way of doing velocity control. I don't think I can guess exactly what the differences in performances would be without having an actual robot to test it on - naively, I suspect that doing this could yield faster response times than integrating the output (since the F term provides an immediate approximation of any desired output, while we have to wait for the integrated output to reach it) but we're not really worried about response lag.
It's worth noting that we're not seeing any problems with oscillations or overshoot, we're more worried about the taxing effect on the drive components from the (correct) behavior of the motors fighting the robot's forward momentum to come to a stop quickly.
Unread 14-03-2016, 21:16
Jared's Avatar
Jared Jared is offline
I would set up something that limits how quickly your velocity setpoint can change when you are slowing down. You could put this in the part of your code where you're mapping joystick position to desired velocity.
For example, you could have something like:
//set currentSetpoint here
if(currentSetpoint - lastSetpoint > .1){
    currentSetpoint = lastSetpoint - .1;
//set your PID controller here
lastSetpoint = currentSetpoint;
You could replace .1 by how much you want the maximum change in velocity setpoint per 20ms to be. You'd also need to do something clever for when you're going in reverse and slowing down, but the idea is the same.
Unread 14-03-2016, 21:27
Originally Posted by Jared View Post
Let's test that code.
inputs:
currentSetpoint = .1
lastSetpoint = 1
output:
currentSetpoint is not updated
Unread 14-03-2016, 21:34
Jared's Avatar
inputs:
lastSetpoint = 1
output:
I'm not sure why currentSetpoint wouldn't be updated.
currentSetpoint is updated before the if statement, so the condition for the if statement isn't met, it will use the value of currentSetpoint set in the first line.
It does only work in one direction though - if you wanted it to work in both directions for only decelerations, you'd need to know which way you were going.
Unread 14-03-2016, 21:37
The large step in setpoint is allowed through without being ramped.
.1 - 1 = -.9 which is not > .1, so the logic does not prevent a jump in setpoint from 1 to .1.
