Re: Compressor not Receiving Voltage (Need quick help if possible, currently at regio
Try shorting the pressure switch inputs, then see if you get any voltage on the compressor outputs while the robot is enabled. Best way to do this is to unplug both the compressor and switch, then use a short wire to bridge the two inputs for the switch.
Also check on the driver station that the PCM version number shows up - if that isn't there, then there's something wrong with the CAN bus or the switch.
If the version number is there and shorting it doesn't work, then there's probably something wrong with the PCM.