PRESSURE SWITCH

Quoted from the FIRST Pneumatics Manual:
Quote:
We have included a pressure switch manufactured by The Nason Company. These switches are normally closed. The switches will open at approximately 115psi and will not close again until the pressure drops to approximately 95psi. This will allow you to turn off the compressor once you are up to 115psi, saving power in the battery. It should be wired directly to the robot controller digital input bank with PWM type cable. No specific Digital Input Port is designated for the pressure switch. The Robot Controller must be programmed to react to the Input Port that is connected to the pressure switch The Robot Controller will activate the designated Spike Relay to turn the Compressor “on” and “off”. There is no default program in the Robot Controller to control the Compressor power. Do not put the pressure switch in series with the power supply to the compressor.
Maybe I am missing something, but how is this of any use to us. The highest we can run our pneumatic system is at 60psi, so how is a sensor that measures 95/115 psi be of any use?

Am I just way off track?
  #2   Spotlight this post!  
Unread 01-02-2005, 21:14
cabbagekid2 cabbagekid2 is offline
Registered User
#0368 (Kika Mana)
 
Join Date: Jun 2001
Rookie Year: 2000
Location: Honolulu, HI
Posts: 85
cabbagekid2 has a spectacular aura aboutcabbagekid2 has a spectacular aura aboutcabbagekid2 has a spectacular aura about
Re: PRESSURE SWITCH

Quote:
Originally Posted by Mr. Steve
Quoted from the FIRST Pneumatics Manual:


Maybe I am missing something, but how is this of any use to us. The highest we can run our pneumatic system is at 60psi, so how is a sensor that measures 95/115 psi be of any use?

Am I just way off track?
The highest you can run the pneumatic system is 60psi (to solenoids, pistons, etc) but you can store up to 115 psi in the two pneumatic tanks that are connected before the main 60 psi regulator. I guess this is so you can charge up the tanks to 115 psi and run the pistons numerous times before charging the tank up again (since charging the air tanks takes longer than using the air in them).
  #3   Spotlight this post!  
Unread 01-02-2005, 21:47
Mr. Steve's Avatar
Mr. Steve Mr. Steve is offline
No relation to Mrs. Steve
#1626 (Falcon Robotics)
 
Join Date: Nov 2004
Rookie Year: 2005
Location: NJ
Posts: 34
Mr. Steve is an unknown quantity at this point
Re: PRESSURE SWITCH

Quote:
Originally Posted by cabbagekid2
you can store up to 115 psi in the two pneumatic tanks that are connected before the main 60 psi regulator.
Thanks for the reply, is there a rule number for this? I couldn't find anything regarding 115psi in pneumatic part of section 5 in the manual.
  #4   Spotlight this post!  
Unread 01-02-2005, 21:49
Kyle's Avatar
Kyle Kyle is offline
Mike Wade, RIP You will be missed
AKA: Kyle Rice
FRC #0365 (MOE)
Team Role: Alumni
 
Join Date: Jan 2003
Rookie Year: 2002
Location: Wilmington, Delaware
Posts: 1,387
Kyle has a reputation beyond reputeKyle has a reputation beyond reputeKyle has a reputation beyond reputeKyle has a reputation beyond reputeKyle has a reputation beyond reputeKyle has a reputation beyond reputeKyle has a reputation beyond reputeKyle has a reputation beyond reputeKyle has a reputation beyond reputeKyle has a reputation beyond reputeKyle has a reputation beyond repute
Send a message via AIM to Kyle
Re: PRESSURE SWITCH

I thought it was 120 psi in the system not 115?
__________________
2007 Championship Chairmans!!!!! 8 years in the making GO MOE!


Facebook
  #5   Spotlight this post!  
Unread 01-02-2005, 21:50
BoyWithCape195 BoyWithCape195 is offline
Registered User
AKA: Ben Gagne
FRC #0195
Team Role: Alumni
 
Join Date: Mar 2004
Rookie Year: 2003
Location: Connecticut
Posts: 410
BoyWithCape195 has a brilliant futureBoyWithCape195 has a brilliant futureBoyWithCape195 has a brilliant futureBoyWithCape195 has a brilliant futureBoyWithCape195 has a brilliant futureBoyWithCape195 has a brilliant futureBoyWithCape195 has a brilliant futureBoyWithCape195 has a brilliant futureBoyWithCape195 has a brilliant futureBoyWithCape195 has a brilliant futureBoyWithCape195 has a brilliant future
Send a message via AIM to BoyWithCape195
Re: PRESSURE SWITCH

It is 120...
__________________
#16
2007 UTC New England Regional Champions (1124 and 558)
2007 UTC GM Industrial Design
2006 International Championship Finalist (25 and 968)
2006 Newton Division Champions (25 and 968)
2006 Championship Innovation in Control Award
2006 UTC Quarterfinalist (236 and 230)
2006 UTC Innovation in Control Award
2005 Curie Division Quarterfinalists (703 and 234)
2005 UTC Semifinalist (228 and 236)
2004 UTC Entrepreneurship Award
2004 New Jersey Semifinalists (173 and 11)
2004 New Jersey Sportsmanship Award
  #6   Spotlight this post!  
Unread 01-02-2005, 22:09
Mr. Steve's Avatar
Mr. Steve Mr. Steve is offline
No relation to Mrs. Steve
#1626 (Falcon Robotics)
 
Join Date: Nov 2004
Rookie Year: 2005
Location: NJ
Posts: 34
Mr. Steve is an unknown quantity at this point
Re: PRESSURE SWITCH

Rule R02, finally found it. Thanks
  #7   Spotlight this post!  
Unread 01-02-2005, 22:53
Sscamatt's Avatar
Sscamatt Sscamatt is offline
Registered User
AKA: Matt Syska
FRC #0195 (Cyber Knights)
Team Role: Electrical
 
Join Date: Mar 2003
Rookie Year: 2003
Location: Southington, CT
Posts: 265
Sscamatt has much to be proud ofSscamatt has much to be proud ofSscamatt has much to be proud ofSscamatt has much to be proud ofSscamatt has much to be proud ofSscamatt has much to be proud ofSscamatt has much to be proud ofSscamatt has much to be proud ofSscamatt has much to be proud ofSscamatt has much to be proud of
Send a message via AIM to Sscamatt
Re: PRESSURE SWITCH

120 psi and 115psi are both correct....in a way:

The maximum allowed by the rules is 120psi. Your robot will be limited to 115 psi because the Nason Pressure Switch shuts off at 115psi.

"The switches will open at approximately 115psi and will not close again until the pressure drops to approximately 95psi."

from page 3 of : http://www2.usfirst.org/2005comp/Man...ticsManual.pdf
__________________
2006 Championship Finalist, Thanks 25 + 968!
2006 Newton Division Winner
2006 International Innovation In Control Award
2006 Radio Shack Innovation in Control Award, UTC Regional

RIT Class of 2011
  #8   Spotlight this post!  
Unread 01-02-2005, 23:41
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,766
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: PRESSURE SWITCH

Quote:
Originally Posted by Mr. Steve
Thanks for the reply, is there a rule number for this? I couldn't find anything regarding 115psi in pneumatic part of section 5 in the manual.
When your robot is inspected, you will need to demonstrate that the compressor turns of via software at a high side pressure of no more than 120 PSI. For that reason it is recommended you follow the system diagram at the bottom of page 20 of the robot manual and include a presuure guage at both the high side (120 PSI) and working pressure (60 PSI) side of the regulator.

"<R88> The Nason Co. pressure switch must be connected to the output end of one of the Clippard tanks to sense the tank’s pressure. The two wires from the pressure switch must be connected directly to a digital input and ground terminals on the Robot Controller, and the controller must be programmed to sense the state of the switch to operate the relay that powers the compressor."
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #9   Spotlight this post!  
Unread 01-02-2005, 23:51
Dave Flowerday Dave Flowerday is offline
Software Engineer
VRC #0111 (Wildstang)
Team Role: Engineer
 
Join Date: Feb 2002
Rookie Year: 1995
Location: North Barrington, IL
Posts: 1,366
Dave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond reputeDave Flowerday has a reputation beyond repute
Re: PRESSURE SWITCH

Quote:
Originally Posted by Al Skierkiewicz
When your robot is inspected, you will need to demonstrate that the compressor turns of via software at a high side pressure of no more than 120 PSI.
FIRST has indicated that it is legal to run the pump all the time and ignore the pressure switch:
Quote:
Originally Posted by FIRST Q&A
ID: 1350 Section: 5.3.10 Status: Answered Date Answered: 1/28/2005
Q: R88 indicates that the Nason pressure sw. is required if we use the pump, but it's not mentioned as a 'minimum' in R86. May we use the analog sensor instead? May we run the pump all the time and not install either sensor?
A: Part 1: You must use the pressure switch. You cannot use the analog sensor. Part 2: You may run the pump all the time; you can ignore the sensor BUT you MUST use the sensor. It is unwise to run your pump all the time as it uses power from your battery.
  #10   Spotlight this post!  
Unread 02-02-2005, 12:52
Mr. Lim Mr. Lim is offline
Registered User
AKA: Mr. Lim
no team
Team Role: Leadership
 
Join Date: Jan 2004
Rookie Year: 1998
Location: Toronto, Ontario
Posts: 1,125
Mr. Lim has a reputation beyond reputeMr. Lim has a reputation beyond reputeMr. Lim has a reputation beyond reputeMr. Lim has a reputation beyond reputeMr. Lim has a reputation beyond reputeMr. Lim has a reputation beyond reputeMr. Lim has a reputation beyond reputeMr. Lim has a reputation beyond reputeMr. Lim has a reputation beyond reputeMr. Lim has a reputation beyond reputeMr. Lim has a reputation beyond repute
Re: PRESSURE SWITCH

Good info on this thread!

To follow-up:

I'm sure teams are going to want to push the limit and get exactly 120 psi into their Clippards. 115 wont cut it - whether it be for practical reasons, or just out of principle =).

I see two options here:

1) use only the Nason pressure switch, and code a timer that causes the compressor to run just long enough after the 115 psi cut-off to get roughly 120 psi.

2) connect both the Nason pressure switch AND the analog pressure sensor. Ignore the output from the pressure SWITCH, and use only the reading from the pressure sensor to dictate compressor shutoff at exactly 120 psi.

Seems a littleweird to me, but are there other options here to get 120psi legally?

-SlimBoJones...
  #11   Spotlight this post!  
Unread 02-02-2005, 13:14
Steve W Steve W is offline
Grow Up? Why?
no team
 
Join Date: Feb 2003
Rookie Year: 2002
Location: Toronto,Ontario Canada
Posts: 2,523
Steve W has a reputation beyond reputeSteve W has a reputation beyond reputeSteve W has a reputation beyond reputeSteve W has a reputation beyond reputeSteve W has a reputation beyond reputeSteve W has a reputation beyond reputeSteve W has a reputation beyond reputeSteve W has a reputation beyond reputeSteve W has a reputation beyond reputeSteve W has a reputation beyond reputeSteve W has a reputation beyond repute
Re: PRESSURE SWITCH

Quote:
Originally Posted by SlimBoJones
2) connect both the Nason pressure switch AND the analog pressure sensor. Ignore the output from the pressure SWITCH, and use only the reading from the pressure sensor to dictate compressor shutoff at exactly 120 psi.
-SlimBoJones...
Unfortunately this year there is also a rule (or in Q&A) that states that you cannot use the pressure sensor to shut off the compressor .
__________________
We do not stop playing because we grow old;
we grow old because we stop playing.
  #12   Spotlight this post!  
Unread 02-02-2005, 13:17
phillutz phillutz is offline
Registered User
FRC #0851 (The Froggers)
Team Role: Mentor
 
Join Date: Nov 2004
Rookie Year: 2004
Location: El Segundo,CA
Posts: 28
phillutz is on a distinguished road
Re: PRESSURE SWITCH

Quote:
Originally Posted by Steve W
Unfortunately this year there is also a rule (or in Q&A) that states that you cannot use the pressure sensor to shut off the compressor .
Can we use the Pressure Sensor to turn ON the compressor?
We don't like the idea that we need to run the compressor at 95psi when only 60 is passed beyond the next gauge.
If we code the "Start compressor with the Analog, we can run down the pressure to 60-65 and use the battery less... I think

Last edited by phillutz : 02-02-2005 at 13:20. Reason: Additional text added
  #13   Spotlight this post!  
Unread 02-02-2005, 14:14
ttedrow's Avatar
ttedrow ttedrow is offline
Herding electrons
AKA: Tim Tedrow
FRC #0281 (EnTech)
Team Role: Mentor
 
Join Date: Jan 2002
Rookie Year: 2000
Location: Greenville, SC
Posts: 165
ttedrow will become famous soon enoughttedrow will become famous soon enough
Re: PRESSURE SWITCH

Quote:
Originally Posted by phillutz
Can we use the Pressure Sensor to turn ON the compressor?
We don't like the idea that we need to run the compressor at 95psi when only 60 is passed beyond the next gauge.
If we code the "Start compressor with the Analog, we can run down the pressure to 60-65 and use the battery less... I think
Running the high side at about 115 psi gives your system more air volume to work with. If you run the high side at 65 psi your compressor may not be able to keep up with the cycles or speed that are need during competition.
__________________
Sr. Design Engineer
Caterpillar Inc.
Greenville, SC

KD4EGM

FRC 281 Greenvillains
Infected with the FIRST virus in 2000

Yes, Chute Door!!!
  #14   Spotlight this post!  
Unread 02-02-2005, 14:54
phillutz phillutz is offline
Registered User
FRC #0851 (The Froggers)
Team Role: Mentor
 
Join Date: Nov 2004
Rookie Year: 2004
Location: El Segundo,CA
Posts: 28
phillutz is on a distinguished road
Re: PRESSURE SWITCH

Quote:
Originally Posted by ttedrow
Running the high side at about 115 psi gives your system more air volume to work with. If you run the high side at 65 psi your compressor may not be able to keep up with the cycles or speed that are need during competition.
Looking toward using the Nason as the high side (115psi) and the Analog as the low side so that we can detect when the pressure drops to say 60-65 psi.
  #15   Spotlight this post!  
Unread 02-02-2005, 15:06
Paul Copioli's Avatar Unsung FIRST Hero Woodie Flowers Award
Paul Copioli Paul Copioli is offline
President, VEX Robotics, Inc.
FRC #3310 (Black Hawk Robotics)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 2000
Location: Rockwall, TX
Posts: 1,382
Paul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond reputePaul Copioli has a reputation beyond repute
Re: PRESSURE SWITCH

Remember, you must connect the pressure relief valve when using the pump. This valve relieves pressure at around 120psi, no matter what! This is why it is legal to run your pump continuously.

Why pump up to 120 psi when you only use 60psi? That is a matter of "pressure volume". Let's say I have a cylinder that uses the exact volume of air that is in the tanks. If the pressure of the tank is only 60psi, then when I fire the cylinder once I expel all of the air in the tanks. If the pressure in the tanks is 120psi, then I have double the available air to use at 60psi. Air is compressible, which means as you increase the pressure the volume the same mass of air takes up gets smaller. Since the air tanks are a constant volume, when you increase the pressure then the amount of usable air increases. For this reason, you should try to maximize the pressure you have in the tanks.
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Pneumatic pressure switch M. Hicken Programming 9 29-01-2005 23:35
Pressure Switch: Ordering a Spare Bduggan04 Pneumatics 4 22-03-2004 20:15
connecting pressure switch kingpin3787 Pneumatics 2 19-02-2004 21:01
spike for pressure switch? Rob Colatutto Rules/Strategy 4 23-02-2003 15:42
Error found in programming for the pump and pressure switch sjharobotics Programming 4 06-02-2002 17:46


All times are GMT -5. The time now is 22:31.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi