Default code and the Compressor
We seem to be having a problem setting up the simple pressure switch and the compressor to allow the compressor to shut off when pressure reaches the 115psi. We have loaded the 2005 code and plugged in the the spike that controls the compressor to relay 8. The Pressure switch is placed on Digital IO 18 and it is set as input in the code. With this setup the compressor will not run even when there is no Pressure in the tanks.
We then loaded the 2004 default code we had from last year and the system worked. Can anyone please point us in the correct direction and are there any other teams having this same problem? |
|
#2
|
|||||
|
|||||
|
Re: Default code and the Compressor
Both the v2.2 and v2.4 default code have this line in Default_Routine:
Code:
relay8_fwd = !rc_dig_in18; /* Power pump only if pressure switch is off. */ |
|
#3
|
||||
|
||||
|
Re: Default code and the Compressor
Quote:
I have checked the code and it looks like the default values. I have even downloaded the default code and loaded the default hex into the controller. Is there an error in the code I am not aware of that I need to change. |
|
#4
|
||||
|
||||
|
Re: Default code and the Compressor
Your code is doing exactly what it is supposed to be doing....run when the switch is not set (i.e. pressure is below the threshold). It just so happens that the pressure switch has a cutoff of ~115 PSI. There's a discussion of this here.
If you really want to get your system pressure to 120 PSI, you can run the pump for a fixed number of cycles after the switch was set (i.e. pressure is above threshold) before giving it the command to shut off. We've used this method for the past few years, and it works just fine. |
|
#5
|
||||
|
||||
|
Re: Default code and the Compressor
Quote:
Our pump is not running when the pressure is below 115psi using the 2005 default code. We have gotten the pump to work with last years code which I can not find the difference. |
|
#6
|
||||
|
||||
|
Re: Default code and the Compressor
Misread your original post...I thought you weren't getting it charged up to 120...
So your code from last year works with your current compressor/switch setup, but your new code doesn't? And it is using the same dig in/relay? Just throwing some blind suggestions out.... Have you tried using printfs to see the value of the switch? Does it change when the pressure reaches 115? What happens if you hard code the value of relay8_fwd to 1? Does the compressor turn on? How far away from the default code are you? If you want, you can send me your C file and I can take a look for anything out of the ordinary. |
|
#7
|
||||
|
||||
|
Re: Default code and the Compressor
here is both this years default code (which doesn't work for us), and the default code from last year which does work.
|
|
#8
|
||||
|
||||
|
Re: Default code and the Compressor
Well, the code you posted should work. Strange...
Maybe you're reassigning relay8 in a different file, like user_routines_fast? Might do a search for relay8 in some other files, and see if you're setting it equal to something. |
|
#9
|
||||
|
||||
|
Re: Default code and the Compressor
We havent changed any of the other files, yet.
|
|
#10
|
||||
|
||||
|
Re: Default code and the Compressor
I diffed your 2005 code to the Default code released by FIRST and, as expected, it is identical.
This makes me believe that your compressor and/or pressure switch is wired incorrectly. Try making the following modification and see what you see Code:
relay5_rev = p1_sw_aux2;
relay6_fwd = p3_sw_aux1;
relay6_rev = p3_sw_aux2;
relay7_fwd = p4_sw_aux1;
relay7_rev = p4_sw_aux2;
relay8_fwd = !rc_dig_in18; /* Power pump only if pressure switch is off. */
relay8_rev = 0;
/******************/
/* THIS CODE IS ADDED */
printf("Switch %d Relay %d\r",(int)rc_digin18,(int)relay8_fwd);
/******************/
/*---------- PWM outputs Limited by Limit Switches ------------------------*/
If you see that the switch is always reading 1, then your compressor will never turn on. If that is the case, your switch may be wired incorrectly or defective. To verify this, remove the ! from the line that sets relay8_fwd. If the compressor runs and shuts off at 115 psi, then there's some weirdness on why your switch is returning an inverted value. If the compressor never shuts off, doublecheck all connections between the switch and the RC. Hopefully that helps... |
|
#11
|
||||
|
||||
|
Re: Default code and the Compressor
It DOES work with the 2004 code. but does not work with the 2005. same wiring for both. but we cant find any real diffrence between them other than the camera stuff.
|
|
#12
|
|||||
|
|||||
|
Re: Default code and the Compressor
Quote:
|
|
#13
|
||||
|
||||
|
Re: Default code and the Compressor
Matthew, et al,
I was planning to hook up a compressor this afternoon anyway. I will try the 2005 default code and report my observations. Mike |
|
#14
|
||||
|
||||
|
Re: Default code and the Compressor
Quote:
We finally got it to work. We changed this the code below and it worked. Please explain why this worked. Code:
relay8_fwd = !rc_dig_in18; /* Power pump only if pressure switch is off. */ relay8_rev = 0; Code:
relay8_rev = !rc_dig_in18; /* Power pump only if pressure switch is off. */ relay8_fwd = 0; |
![]() |
| Thread Tools | |
| Display Modes | Rate This Thread |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Help On Coding 2K1 Controller | GregTheGreat | Programming | 9 | 12-05-2003 06:35 PM |
| Chassis Material/Construction | sanddrag | Technical Discussion | 51 | 12-05-2003 12:59 PM |
| New software?? | mjt902 | Programming | 2 | 01-08-2003 10:40 AM |
| PBASIC 2.5 answer from Parallax | JasonS | Programming | 6 | 01-07-2003 07:21 PM |
| Team 237 unleashes a "Beast" | Elgin Clock | Robot Showcase | 5 | 03-27-2002 09:09 PM |