DEFECTIVE NASON PRESSURE SWITCH... NEED REPLACEMENT ASAP!!!
Hi, After several days of trying to figure out why our pnuematics does not work (the compressor will not shut off) - rewring, programming, ect. we have determined that our Nason pressure switch was defective. We called Nason, and they have a 4-6 week lead time, because apparently, these things are custom made. We have less than a week to complete our robot, and we can't even see our hard work in action. We are a rookie team, and we are in dire need of assitance. PLEASE PLEASE PLEASE PLEASE if anyone ANYONE has a pressure switch they could spare (we can even return it once we get our replacement) you don't know how much we would APPRECIATE this guesture. We'll glady pay for whatever it costs to ship it overnight express, we just need it ASAP!!!!! PLEASE!!!!!! If you have one or know someone who does, please contact us immediatly. Thank you in advance, Jason, Team Leader 1656 |
|
#2
|
||||
|
||||
|
Re: Urgent need for Nason pressure switch!! PLEASE HELP!
make sure everything is in the right direction (see the arrows on all the regulators)
also make sure that your system matches that in the pneumatics manual, keep in mind that the compressor usual cuts out around 120 psi |
|
#3
|
||||
|
||||
|
Re: Urgent need for Nason pressure switch!! PLEASE HELP!
Have you checked that all of your pressure gauges are in the right place and that you have no leaks. There should be approx 120 in Clippards and 60 down line of the regulator. I would check all of these out first. The rest is wiring and programming. Check were you made your inputs and that your wires are good then check with the programming.
|
|
#4
|
|||
|
|||
|
Re: Urgent need for Nason pressure switch!! PLEASE HELP!
Quote:
|
|
#5
|
||||
|
||||
|
Re: Urgent need for Nason pressure switch!! PLEASE HELP!
Have you gotten it to work off of the robot
we have had all of our pneumatics working fine off the robot, but as soon as everything is on the robot almost all pneumatics are not working our pressure switch also seems to be not working but we are not going to drill it apart worst comes to worst u can just run the compressor on a timer or something cause it will always vent at about 125 IF anyone can help with problems with the pressure sensor please pm me |
|
#6
|
|||
|
|||
|
Re: Urgent need for Nason pressure switch!! PLEASE HELP!
Quote:
We are really looking for someone who can send us a pressure switch, even if its from prior years or anything... If we have to, for the time being we can hard code it like you said, but it would be nice to have the autoshutoff feature =) Thanks! |
|
#7
|
|||
|
|||
|
Re: Urgent need for Nason pressure switch!! PLEASE HELP!
It is illegal to not use the Nason Pressure Switch. You must have this wired correctly, if it wasn’t there, your compressor would probably burn out.
|
|
#8
|
||||
|
||||
|
Re: Urgent need for Nason pressure switch!! PLEASE HELP!
Quote:
|
|
#9
|
|||
|
|||
|
Re: Urgent need for Nason pressure switch!! PLEASE HELP!
Quote:
Thanks for your help though! |
|
#10
|
|||
|
|||
|
Re: Urgent need for Nason pressure switch!! PLEASE HELP!
Quote:
EDIT: From your latest post, it sounds like you 'tested' it with something other than the RC. Even if you only connect the switch that way during testing, it would be permanently destroyed. NEVER connect it to anything besides a digital input. If you _really_ want to test it, you can use an ohmmeter across the terminals without worrying about damaging it. It should go to 'zero' when the switch is closed. Last edited by dan_h : 02-17-2005 at 12:10 PM. |
|
#11
|
|||||
|
|||||
|
Re: Urgent need for Nason pressure switch!! PLEASE HELP!
If you still need one, we have a spare. Send me a PM with contact info and address, and we can send it to you tomorrow (but ya gotta promise not to connect it to the battery!
)-dave |
|
#12
|
|||||
|
|||||
|
Re: Urgent need for Nason pressure switch!! PLEASE HELP!
If you want to send a driver out to NJ we have the whole pneumatics set not in use and you can pick what you want. We will be at the school all day for the next 4 days. We are in central NJ about 90 mins from you.
WC ![]() Last edited by Wayne C. : 02-18-2005 at 12:18 AM. |
|
#13
|
|||||
|
|||||
|
Re: Urgent need for Nason pressure switch!! PLEASE HELP!
Quote:
Quote:
|
![]() |
| Thread Tools | |
| Display Modes | Rate This Thread |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| PRESSURE SWITCH | Mr. Steve | Pneumatics | 20 | 12-01-2005 10:20 AM |
| Pressure Switch wiring diagram | robotjoe | Electrical | 1 | 02-08-2005 02:01 PM |
| connecting pressure switch | kingpin3787 | Pneumatics | 2 | 02-19-2004 09:01 PM |
| spike for pressure switch? | Rob Colatutto | Rules/Strategy | 4 | 02-23-2003 03:42 PM |
| Need help with 255 Variable | Joseph F | Programming | 18 | 02-26-2002 02:49 PM |