lukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond repute
Send a message via AIM to lukevanoort
in need of another 40A

Ok, so I was "discussing" a six motor drivetrain with my team. Then, one team member pointed out that that we only have six 40A breakers available, and that if we have a high draw motorized arm, we'll have a power problem. Personally I think our arm shouldn't draw that much, but anyway, is it legal to wire a pair of 20A breakers to act as a single 40A?
__________________
Team 1219: 2009 - Mentor
Team 587: 2005 - Animator, 2006-2008 - Team Captain
  #2   Spotlight this post!  
Unread 06-12-2005, 20:05
Tristan Lall's Avatar
Tristan Lall Tristan Lall is offline
Registered User
FRC #0188 (Woburn Robotics)
 
Join Date: Aug 2001
Rookie Year: 1999
Location: Toronto, ON
Posts: 2,484
Tristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond repute
Re: in need of another 40A

You have 40 A breakers for all of the motors that need them, that is to say, the CIMs and F-Ps.

For competition purposes, it certainly isn't legal to run breakers in parallel (or series, for that matter, excepting the 20 A breaker on the compressor spike), and you have to use an equal- or lower-rated breaker for the motors.

Actually, unless it was updated/Q&A'd and not incorporated, the 2004 rule to only use CIMs and (the discontinued) drills on 40 A breakers wasn't specifically listed in the 2005 rules. Nevertheless, an inspector wouldn't likely let you get away with using a 40 A (or even a 30 A) on a little Mabuchi, Globe or a window motor, because of the low current ratings—it would allow the motor to stall and overheat, without tripping the breaker. The van door is a little trickier to judge; it stalls somewhere between 40 and 60 A, depending on the spec sheet consulted. That's too close for comfort, in my estimation, to use a 40 A.*

This rule needs to be put back in the book, for safety reasons. Unfortunately, it's easy to miss this, because all of the breakers look essentially the same, at a glance.

*A little clarification: the 60 A end of the scale should be fine, but there was a little bit of controversy early in the season as to whether or not all the van door motors were identical. Published specs for the Tiagene van door motors in previous years listed stall torque at 40 A, while the current one lists it at 59.4 A (at 12 V). If the specs are right, then a 40 could work, because it will interrupt it before stall; if a team recieved any old stock from FIRST (and some motors had strange markings on them, like "bad" stickers, and different part numbers), they might end up with a motor that will stall before the breaker is triggered. Also note that breakers don't trip instantly at their rated current; the time to trip scales with the overcurrent.

Last edited by Tristan Lall : 06-12-2005 at 20:47.
  #3   Spotlight this post!  
Unread 06-12-2005, 20:31
Andrew Blair's Avatar
Andrew Blair Andrew Blair is offline
SAE Formula is FIRST with Gasoline.
FRC #0306 (CRT)
Team Role: Alumni
 
Join Date: Feb 2005
Rookie Year: 2004
Location: Corry
Posts: 1,193
Andrew Blair has a reputation beyond reputeAndrew Blair has a reputation beyond reputeAndrew Blair has a reputation beyond reputeAndrew Blair has a reputation beyond reputeAndrew Blair has a reputation beyond reputeAndrew Blair has a reputation beyond reputeAndrew Blair has a reputation beyond reputeAndrew Blair has a reputation beyond reputeAndrew Blair has a reputation beyond reputeAndrew Blair has a reputation beyond reputeAndrew Blair has a reputation beyond repute
Send a message via AIM to Andrew Blair Send a message via Yahoo to Andrew Blair
Re: in need of another 40A

Well, as was said, I don't think we have more than six motors that are really capable of pulling more than 40 amps, or 30 for that matter. I haven't looked at all the specs, but generally speaking, when we have motors like a window or globe on a 30 amp breaker, they stall before the breaker trips, indicating to me that they can't pull 30 amps at stall.
__________________
Reading makes a full man, conference a ready man, and writing an exact man.
-Sir Francis Bacon

"Any intelligent fool can make things bigger, more complex, and more violent. It takes a touch of genius -- and a lot of courage -- to move in the opposite direction."
-Albert Einstein
  #4   Spotlight this post!  
Unread 06-12-2005, 21:02
coastertux coastertux is offline
Penn State Class of 2010!
AKA: Steve
FRC #1640 (sab-BOT-age)
Team Role: Mentor
 
Join Date: Jan 2005
Rookie Year: 2005
Location: Downingtown, PA
Posts: 264
coastertux is just really nicecoastertux is just really nicecoastertux is just really nicecoastertux is just really nicecoastertux is just really nice
Send a message via AIM to coastertux
Re: in need of another 40A

You could also buy 40A breakers from IFI for $7.95 each.

http://www.ifirobotics.com/accessories.shtml
  #5   Spotlight this post!  
Unread 06-12-2005, 21:04
Billfred's Avatar
Billfred Billfred is offline
...and you can't! teach! that!
FRC #5402 (Iron Kings); no team (AndyMark)
Team Role: Mentor
 
Join Date: Feb 2004
Rookie Year: 2004
Location: The Land of the Kokomese, IN
Posts: 8,552
Billfred has a reputation beyond reputeBillfred has a reputation beyond reputeBillfred has a reputation beyond reputeBillfred has a reputation beyond reputeBillfred has a reputation beyond reputeBillfred has a reputation beyond reputeBillfred has a reputation beyond reputeBillfred has a reputation beyond reputeBillfred has a reputation beyond reputeBillfred has a reputation beyond reputeBillfred has a reputation beyond repute
Re: in need of another 40A

Quote:
Originally Posted by Tristan Lall
Actually, unless it was updated/Q&A'd and not incorporated, the 2004 rule to only use CIMs and (the discontinued) drills on 40 A breakers wasn't specifically listed in the 2005 rules.
I can't pull up the section in the manual right now (so much time and so little to do...wait a second), but I believe they regulated the breaker size by the wire gauge this year.
__________________
William "Billfred" Leverette - Gamecock/Jessica Boucher victim/Marketing & Sales Specialist at AndyMark

2004-2006: FRC 1293 (D5 Robotics) - Student, Mentor, Coach
2007-2009: FRC 1618 (Capital Robotics) - Mentor, Coach
2009-2013: FRC 2815 (Los Pollos Locos) - Mentor, Coach - Palmetto '09, Peachtree '11, Palmetto '11, Palmetto '12
2010: FRC 1398 (Keenan Robo-Raiders) - Mentor - Palmetto '10
2014-2016: FRC 4901 (Garnet Squadron) - Co-Founder and Head Bot Coach - Orlando '14, SCRIW '16
2017-: FRC 5402 (Iron Kings) - Mentor

94 events (more than will fit in a ChiefDelphi signature), 14 seasons, over 61,000 miles, and still on a mission from Bob.

Rule #1: Do not die. Rule #2: Be respectful. Rule #3: Be safe. Rule #4: Follow the handbook.
  #6   Spotlight this post!  
Unread 06-12-2005, 21:31
lukevanoort lukevanoort is offline
in between teams
AKA: Luke Van Oort
no team
 
Join Date: Oct 2005
Rookie Year: 2005
Location: Waterloo, ON, Canada
Posts: 1,873
lukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond repute
Send a message via AIM to lukevanoort
Re: in need of another 40A

Clarification, I wanted to try and make a six motor drivetrain this year, and our only surviving member who did electrical mentioned that these breaker panels only take six 40A breakers, which he didn't want all used. We have plenty of the breakers. (I think the exact words were "No way, Luke.") I had a vague memory of reading a rule that the old FPs were required to be on a thirty, so I thought "if those worked on thiries, ehy can't these", but given my inexperience with doing the electrical, I said nothing and continued my gearbox lecture. I decided that I would check CD for what you guys thought before I disagreed with a more senior member about a subject I've never worked on before. Thanks.
__________________
Team 1219: 2009 - Mentor
Team 587: 2005 - Animator, 2006-2008 - Team Captain
  #7   Spotlight this post!  
Unread 06-12-2005, 22:01
Tristan Lall's Avatar
Tristan Lall Tristan Lall is offline
Registered User
FRC #0188 (Woburn Robotics)
 
Join Date: Aug 2001
Rookie Year: 1999
Location: Toronto, ON
Posts: 2,484
Tristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond repute
Re: in need of another 40A

Quote:
Originally Posted by Billfred
I can't pull up the section in the manual right now (so much time and so little to do...wait a second), but I believe they regulated the breaker size by the wire gauge this year.
You're right that the wire size was tied to the breaker used, but that would just allow a team to put 12 AWG on a Globe motor, and to connect it to a 40 A breaker—it only specified minimum gauges, not maximums.

I've been informed that there was in fact an incident at the Championship last year where this occurred, and, though the inspector noted the hazard, after consulting the lead inspector, it was determined that since the 2005 rules didn't prohibit it specifically, the inspector couldn't reject it at that stage. (Only if some unsafe operation occurred during a match, could the referees then have had the robot disabled, under <S01>.) As hazards go, this one has the potential to turn ugly.

The 2004 rule was more conservative, and is likely the one that Luke recalls.
  #8   Spotlight this post!  
Unread 07-12-2005, 08:25
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,795
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: in need of another 40A

First, you may not tie breakers in parallel. The breaker size is related to wire size so that we don't have robots flaming on the field, but the rules specify branch circuit design on a motor by motor basis. The smaller motors may not have tripped breakers at stall because they are a temperature controlled device capable of maintaining circuit continuity for up to a few seconds when the current exceeds the breaker by as much as 400%. They would have eventually tripped if the stall conditio9n remained. Please remember that with the autoresetting feature, breakers can open and close very fast producing a buzzing sound and the results will be extremely high temperatures at the breaker. If a breaker is warm or hot, believe it was tripping even if there was no other obvious evidence that it was tripping.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #9   Spotlight this post!  
Unread 07-12-2005, 10:18
Richard Wallace's Avatar
Richard Wallace Richard Wallace is offline
I live for the details.
FRC #3620 (Average Joes)
Team Role: Engineer
 
Join Date: Jan 2003
Rookie Year: 1996
Location: Southwestern Michigan
Posts: 3,665
Richard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond reputeRichard Wallace has a reputation beyond repute
Re: in need of another 40A

Quote:
Originally Posted by Al Skierkiewicz
.... Please remember that with the autoresetting feature, breakers can open and close very fast producing a buzzing sound and the results will be extremely high temperatures at the breaker. If a breaker is warm or hot, believe it was tripping even if there was no other obvious evidence that it was tripping.
Big Al, you know whereof you speak. Those who participated in Stack Attack (FRC 2003) may recall that many robots had problems with overheating 40A breakers when they climbed the ramp. This was often accompanied by a buzzing noise coming from the breakers. Breakers that saw this type of overloading eventually degraded and would no longer sustain high (>50A) peak currents; this caused some robots to veer off intended course when the problem was more severe on one side. Extra 40A breakers were a very popular bartering item in the pits that year.
__________________
Richard Wallace

Mentor since 2011 for FRC 3620 Average Joes (St. Joseph, Michigan)
Mentor 2002-10 for FRC 931 Perpetual Chaos (St. Louis, Missouri)
since 2003

I believe in intuition and inspiration. Imagination is more important than knowledge. For knowledge is limited, whereas imagination embraces the entire world, stimulating progress, giving birth to evolution. It is, strictly speaking, a real factor in scientific research.
(Cosmic Religion : With Other Opinions and Aphorisms (1931) by Albert Einstein, p. 97)
  #10   Spotlight this post!  
Unread 10-12-2005, 10:50
Sparks333's Avatar
Sparks333 Sparks333 is offline
Robotics Engineer
AKA: Dane B.
FRC #1425 (Wilsonville Robotics)
Team Role: Alumni
 
Join Date: Feb 2004
Rookie Year: 2003
Location: Wilsonville, Oregon
Posts: 184
Sparks333 is a glorious beacon of lightSparks333 is a glorious beacon of lightSparks333 is a glorious beacon of lightSparks333 is a glorious beacon of lightSparks333 is a glorious beacon of lightSparks333 is a glorious beacon of light
Send a message via AIM to Sparks333
Re: in need of another 40A

This may be redundant...
Once a breaker has tripped once, it will trip much more easily the second time.
In the 2004 competition, our robot found it difficut to climb. If we popped our breakers getting up the step the first time, we were screwed: the breaker would pop early when we would try again.

Sparks
__________________
ICs do weird things when voltage is run out of spec.

I love to take things apart. The fact that they work better when I put them back together it just a bonus.

http://www.ravenblack.net/random/surreal.html
  #11   Spotlight this post!  
Unread 10-12-2005, 23:46
TimCraig TimCraig is offline
Registered User
AKA: Tim Craig
no team
 
Join Date: Aug 2004
Rookie Year: 2003
Location: San Jose, CA
Posts: 221
TimCraig is a splendid one to beholdTimCraig is a splendid one to beholdTimCraig is a splendid one to beholdTimCraig is a splendid one to beholdTimCraig is a splendid one to beholdTimCraig is a splendid one to beholdTimCraig is a splendid one to behold
Re: in need of another 40A

Most circuit breakers work thermally. So the first time, the breaker is starting out from dead cold. Once it trips, it's gotten to the critical temperature. It doesn't reset until it cools to the reset temperature which is well above dead cold. So next time it takes less energy to heat up to the trip temperature.
  #12   Spotlight this post!  
Unread 10-12-2005, 23:56
lukevanoort lukevanoort is offline
in between teams
AKA: Luke Van Oort
no team
 
Join Date: Oct 2005
Rookie Year: 2005
Location: Waterloo, ON, Canada
Posts: 1,873
lukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond reputelukevanoort has a reputation beyond repute
Send a message via AIM to lukevanoort
Re: in need of another 40A

Quote:
Originally Posted by TimCraig
Most circuit breakers work thermally. So the first time, the breaker is starting out from dead cold. Once it trips, it's gotten to the critical temperature. It doesn't reset until it cools to the reset temperature which is well above dead cold. So next time it takes less energy to heat up to the trip temperature.
That makes sense. I wonder if muffin fans or another cooling method directed at or near the breaker panel would help? Or watercooling using the water from this year's water game.
__________________
Team 1219: 2009 - Mentor
Team 587: 2005 - Animator, 2006-2008 - Team Captain
  #13   Spotlight this post!  
Unread 11-12-2005, 01:11
Unsung FIRST Hero
Mike Betts Mike Betts is offline
Electrical Engineer
no team
Team Role: Engineer
 
Join Date: Dec 2001
Rookie Year: 1995
Location: Homosassa, FL
Posts: 1,442
Mike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond repute
Re: in need of another 40A

Quote:
Originally Posted by lukevanoort
That makes sense. I wonder if muffin fans or another cooling method directed at or near the breaker panel would help? Or watercooling using the water from this year's water game.
Luke,

Changing your gear ratio is the best solution. 40A is a LOT of current on a continuous basis.

JMHO.

Mike
__________________
Mike Betts

Alumnus, Team 3518, Panthrobots, 2011
Alumnus, Team 177, Bobcat Robotics, 1995 - 2010
LRI, Connecticut Regional, 2007-2010
LRI, WPI Regional, 2009 - 2010
RI, South Florida Regional, 2012 - 2013

As easy as 355/113...
  #14   Spotlight this post!  
Unread 11-12-2005, 09:20
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,795
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: in need of another 40A

Quote:
Originally Posted by lukevanoort
That makes sense. I wonder if muffin fans or another cooling method directed at or near the breaker panel would help? Or watercooling using the water from this year's water game.
I have seen teams use a variety of ways to cool the breakers, from fans to cool spray right before a match. The thing to remember is the metal inside the sealed breaker is at temperature and there is very little thermal conduction to/from the case. I should point out that breakers that trip under load (motors) will arc at the contacts. Over time, repetitive trips cause pitting and therefore high resistance which just adds to the heating problem. Not to mention the role of the arc in local heating of the contact area.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
40a connectors scifi3018 Electrical 2 08-02-2005 07:57
Bad 40A Breaker Richard Wallace Electrical 3 18-02-2003 21:42
40A Breakers popping when using CIMs galewind Electrical 9 13-02-2003 10:30
Our 20A and 30A and 40A breakers . . . Frank(Aflak) Technical Discussion 8 01-02-2003 08:36
40A Breakers at Innovation First InnovationFirst Kit & Additional Hardware 2 21-01-2003 13:06


All times are GMT -5. The time now is 04:46.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi