Wiring the Compressor

Twice now, over the course of the past week, we've managed to blow the 20 amp spike fuse with the compressor. We've triple-chcked our wiring, according to this year's power distribution diagram. The Spike's power does go through a 20 amp breaker before it gets to the spike, and the spike is hooked up to a relay. The RC is programmed to run the compressor automatically when the pressure switch, which is wired to a digital input, is released, and turn it off when the switch is triggered.

My first guess is that the spike is bad, especially considering how the plug for the "PWM cable" on the spike itself seemed to be faulty; if I jiggled it a bit, the signal tended to be cut (as in the LED turned off completely, which is only supposed to happen when the fuse blows). We switched out for a different spike, but haven't really had enough time to see if the problem is fixed. We think it has been, after measuring the current and running it a bit, but I figured to be sure, I'd ask if anyone else can see something we're not or has had a problem similar.
__________________
Code:
void function(void)
 {
  function();
 }
  #2   Spotlight this post!  
Unread 23-01-2007, 23:41
Uberbots's Avatar
Uberbots Uberbots is offline
Mad Programmer
AKA: Billy Sisson
FRC #1124 (ÜberBots)
Team Role: College Student
 
Join Date: Jan 2006
Rookie Year: 2005
Location: Avon
Posts: 739
Uberbots has a reputation beyond reputeUberbots has a reputation beyond reputeUberbots has a reputation beyond reputeUberbots has a reputation beyond reputeUberbots has a reputation beyond reputeUberbots has a reputation beyond reputeUberbots has a reputation beyond reputeUberbots has a reputation beyond reputeUberbots has a reputation beyond reputeUberbots has a reputation beyond reputeUberbots has a reputation beyond repute
Re: Wiring the Compressor

maybe your digital input is in backwards?

seeing as you switched the spike, it was probably a bad spike. please do inform us if the problem comes up again.

(perhaps that code in your signature is the problem (= )
__________________
A few of my favorite numbers:
175 176 177 195 230 558 716 1024 1071 1592 1784 1816
RPI 2012
BREAKAWAY
  #3   Spotlight this post!  
Unread 24-01-2007, 00:03
Phalanx's Avatar
Phalanx Phalanx is offline
Formerly Team 1089 (Mercury)
AKA: Michael Reffler
FRC #5431 (Titan Robotics)
Team Role: Mentor
 
Join Date: Jun 2005
Rookie Year: 1999
Location: Lewisville, TX (previously NJ)
Posts: 384
Phalanx has a reputation beyond reputePhalanx has a reputation beyond reputePhalanx has a reputation beyond reputePhalanx has a reputation beyond reputePhalanx has a reputation beyond reputePhalanx has a reputation beyond reputePhalanx has a reputation beyond reputePhalanx has a reputation beyond reputePhalanx has a reputation beyond reputePhalanx has a reputation beyond reputePhalanx has a reputation beyond repute
Re: Wiring the Compressor

From the 2007 FRC Pneumatics Manual See page 3
http://www2.usfirst.org/2007comp/oth...s%20Manual.pdf

A spike relay must be used to control the power to the compressor using a 20amp breaker, not a fuse.

We have done this in the past, replacing the fuse with a 20amp snap action breaker in the spike module.
__________________
Don't just ask the experts, become one!
Leadership is not about ability. It's about responsibility!
Diagonally Parked in a Parallel Universe. It's okay we do Quantum Physics



Last edited by Phalanx : 24-01-2007 at 00:20.
  #4   Spotlight this post!  
Unread 24-01-2007, 01:00
Unsung FIRST Hero
Mike Betts Mike Betts is offline
Electrical Engineer
no team
Team Role: Engineer
 
Join Date: Dec 2001
Rookie Year: 1995
Location: Homosassa, FL
Posts: 1,442
Mike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond repute
Re: Wiring the Compressor

Jake,

Mike (Phalanx) is correct. It is also stated in <R65>:

Quote:
The fuse on the Spike relay for the air compressor may be replaced with a 20 Amp Snap-Action circuit breaker.
The issue is the inrush current on the Thomas Compressor.

Note that this is the only Spike that can be modified in this manner...

Regards,

Mike
__________________
Mike Betts

Alumnus, Team 3518, Panthrobots, 2011
Alumnus, Team 177, Bobcat Robotics, 1995 - 2010
LRI, Connecticut Regional, 2007-2010
LRI, WPI Regional, 2009 - 2010
RI, South Florida Regional, 2012 - 2013

As easy as 355/113...
  #5   Spotlight this post!  
Unread 24-01-2007, 14:26
Jake M Jake M is offline
void* Jake;
FRC #1178 (DURT)
Team Role: Programmer
 
Join Date: Jan 2006
Rookie Year: 2005
Location: Missouri
Posts: 118
Jake M has a spectacular aura aboutJake M has a spectacular aura about
Re: Wiring the Compressor

Well, that would do it. We haven't used any pneumatics in the past three years. That might be how we missed it. Thanks guys.
__________________
Code:
void function(void)
 {
  function();
 }
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
[OCCRA]: Problem with the compressor, pressure switch, or Bosch relay. BrittanyV OCCRA 3 16-10-2006 15:42
Running just the compressor (was: free compressor) sciguy125 Pneumatics 15 06-02-2006 18:23
Default code and the Compressor Matthew_H Programming 16 07-02-2005 07:19
programming the compressor archiver 2001 4 23-06-2002 23:19
Wiring Compressor DakotaFox Electrical 3 05-02-2002 16:52


All times are GMT -5. The time now is 12:06.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi