Power Distribution Block Grounding

We are planning on using 6 40AMP CIM motors, but the problem is that according to the wiring diagram we should be grounding the CIMs in the power distribution block. Also according to the wiring diagram (and common practice) we can only use the 4 ports that are on the opposite side of the battery port. Since we need to ground those 6 CIMs and our breaker panel I was wondering if we could use the other 7 ports on the power distribution block to ground with.
I wasn't able to post on the Q&A because I didn't have our teams account password. Feel free to post this on the Q&A if you can. Thanks for any help.
  #2   Spotlight this post!  
Unread 28-01-2007, 18:01
Daniel367's Avatar
Daniel367 Daniel367 is offline
Dan
AKA: Daniel Rahamim
FRC #0008 (Paly Robotics)
Team Role: Alumni
 
Join Date: Jan 2007
Rookie Year: 2005
Location: palo alto CA
Posts: 24
Daniel367 is on a distinguished road
Send a message via AIM to Daniel367
Re: Power Distribution Block Grounding

I think you can use the disto for a grounding post. thats what i did on my team's bot. Why would they have you ground everything direct when it is most likely that you will have more than 4 items to ground?

thats my two cents,
-Dan
  #3   Spotlight this post!  
Unread 28-01-2007, 18:54
Unsung FIRST Hero
Mike Betts Mike Betts is offline
Electrical Engineer
no team
Team Role: Engineer
 
Join Date: Dec 2001
Rookie Year: 1995
Location: Homosassa, FL
Posts: 1,442
Mike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond repute
Re: Power Distribution Block Grounding

Quote:
Originally Posted by Karma View Post
We are planning on using 6 40AMP CIM motors, but the problem is that according to the wiring diagram we should be grounding the CIMs in the power distribution block. Also according to the wiring diagram (and common practice) we can only use the 4 ports that are on the opposite side of the battery port. Since we need to ground those 6 CIMs and our breaker panel I was wondering if we could use the other 7 ports on the power distribution block to ground with.
I wasn't able to post on the Q&A because I didn't have our teams account password. Feel free to post this on the Q&A if you can. Thanks for any help.
Karma,

There should be no problem in using all 7 positions on the block. Also, you should find that the block accepts 6AWG wire. Connecting 2 (or 3) 10 or 12 AWG wires into one "port" should not be a problem.

Regards,

Mike
__________________
Mike Betts

Alumnus, Team 3518, Panthrobots, 2011
Alumnus, Team 177, Bobcat Robotics, 1995 - 2010
LRI, Connecticut Regional, 2007-2010
LRI, WPI Regional, 2009 - 2010
RI, South Florida Regional, 2012 - 2013

As easy as 355/113...
  #4   Spotlight this post!  
Unread 28-01-2007, 19:15
eugenebrooks eugenebrooks is offline
Team Role: Engineer
AKA: Dr. Brooks
no team (WRRF)
 
Join Date: Jan 2004
Rookie Year: 2001
Location: Livermore, CA
Posts: 601
eugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond repute
Re: Power Distribution Block Grounding

Quote:
Originally Posted by Mike Betts View Post
Karma,

There should be no problem in using all 7 positions on the block. Also, you should find that the block accepts 6AWG wire. Connecting 2 (or 3) 10 or 12 AWG wires into one "port" should not be a problem.

Regards,

Mike
From the battery power terminal strip documentation:

Maximum Wire Size and Max Quantity Allowed per 1492-J16xx Terminal

1 - #6 or
1 - #8 or
2 - #10 or
3 - #12 or
4 - #14 or
4 - #16

Don't mess up, the technical inspectors will no doubt be checking.

Also, you want to arrange the wiring to minimize the amount
of current that a given leg of the "jumper" will be carrying.

Have fun,
Eugene
  #5   Spotlight this post!  
Unread 28-01-2007, 21:36
DonRotolo's Avatar
DonRotolo DonRotolo is offline
Back to humble
FRC #0832
Team Role: Mentor
 
Join Date: Jan 2005
Rookie Year: 2005
Location: Atlanta GA
Posts: 7,011
DonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond repute
Re: Power Distribution Block Grounding

Quote:
Originally Posted by Karma View Post
We are planning on using 6 40AMP CIM motors, but the problem is that according to the wiring diagram we should be grounding the CIMs in the power distribution block.
Actually, you are connecting the fuse panel to the block, not the victors or the motors...

I hope that you are not going to use six of the same motor, because
Quote:
<R45> Items specifically permitted on 2007 FRC ROBOTS include:
<snip> One or two additional 2-1/2” CIM motors (part #FR801-001) in addition to those provided in the Kit Of Parts. This means that up to four, and no more, 2-1/2” CIM motors can be used on the ROBOT.

One additional 3” CIM “Minibike” motor (part #FR801-005). This means that up to two, and no more, 3” CIM “Minibike” motors can be used on the ROBOT.
<snip>
Now, four of one kind and two of the other would be just fine.

You would need two of the golden "Maxi" fuse panels in the case of 2 + 4 big motors.


There should be no concerns with using the SEVEN total available connection points on each part (red/black) of the power distribution block. Although one often sees installations where the inputs are on one side and the outputs on the other, that all changes when you install and use the yellow bus bar jumpers - that is exactly what they are made for!

Also, remember that in this case the term "grounding" is incorrect - when your motors are running in reverse, the black wire has a positive polarity. Victors reverse!

Don
__________________

I am N2IRZ - What's your callsign?
  #6   Spotlight this post!  
Unread 29-01-2007, 08:25
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,795
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: Power Distribution Block Grounding

Quote:
Originally Posted by Don Rotolo View Post
Actually, you are connecting the fuse panel to the block, not the victors or the motors...

Don
Don,
I think he is planning on using the black terminals on the distro block for the negative returns from the high current Victors per the updated electrical drawing and Tips and Guidelines. This is the preferred method for the high current returns.
As Mike and Gene have pointed out, once the jumper is in place, terminals on both sides of the block may be used for these connections.
Has anybody been able to find any data on max current spec for the jumper? I have searched a few manufacturers and have found no spec for this critical part.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #7   Spotlight this post!  
Unread 29-01-2007, 08:51
Unsung FIRST Hero
Mike Betts Mike Betts is offline
Electrical Engineer
no team
Team Role: Engineer
 
Join Date: Dec 2001
Rookie Year: 1995
Location: Homosassa, FL
Posts: 1,442
Mike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond repute
Re: Power Distribution Block Grounding

Quote:
Originally Posted by Al Skierkiewicz View Post
... Has anybody been able to find any data on max current spec for the jumper? I have searched a few manufacturers and have found no spec for this critical part.
Al,

The max allowable current is 85A (reference 1492-J16).

Note also that the nominal acceptable torque for screw terminals is 3 N*m.

Mike
__________________
Mike Betts

Alumnus, Team 3518, Panthrobots, 2011
Alumnus, Team 177, Bobcat Robotics, 1995 - 2010
LRI, Connecticut Regional, 2007-2010
LRI, WPI Regional, 2009 - 2010
RI, South Florida Regional, 2012 - 2013

As easy as 355/113...
  #8   Spotlight this post!  
Unread 29-01-2007, 09:11
MrForbes's Avatar
MrForbes MrForbes is offline
Registered User
AKA: Jim
FRC #1726 (N.E.R.D.S.)
Team Role: Mentor
 
Join Date: Feb 2006
Rookie Year: 2006
Location: Sierra Vista AZ
Posts: 6,022
MrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond repute
Re: Power Distribution Block Grounding

85A is the current rating for the whole block system, might we assume the jumper is the weakest link?
  #9   Spotlight this post!  
Unread 29-01-2007, 12:02
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,795
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: Power Distribution Block Grounding

I have done everything but back engineer the jumper. I am guessing that the jumper can handle far less the 200-300 amp intermittant current demands. I would like to hear from teams that are practicing as to the temp of the jumpers on their robot. Please PM me with details as they come about.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #10   Spotlight this post!  
Unread 29-01-2007, 14:56
Nitroxextreme's Avatar
Nitroxextreme Nitroxextreme is offline
Relation to Mrs. Steve
AKA: Jon
FRC #1626 (Falcon Robotics ; 190 (Gompei and The Herd))
Team Role: Mentor
 
Join Date: Jan 2005
Rookie Year: 2005
Location: Bedminster, NJ
Posts: 276
Nitroxextreme is a splendid one to beholdNitroxextreme is a splendid one to beholdNitroxextreme is a splendid one to beholdNitroxextreme is a splendid one to beholdNitroxextreme is a splendid one to beholdNitroxextreme is a splendid one to behold
Send a message via AIM to Nitroxextreme
Re: Power Distribution Block Grounding

Im not sure on the legality of this (actually tryin to find the answer myself)....
Couldnt you just run a ground from the distribution block to a smaller circuit board...the circuit boards have plenty of extra ground points on them.

This would also cut down on the size of the power distribution block.
__________________



"He needed a chuck norris lesson in FIRST"...."I will give him a round house kick to the face...with gracious professionalism"
  #11   Spotlight this post!  
Unread 29-01-2007, 15:19
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,795
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: Power Distribution Block Grounding

Quote:
Originally Posted by Nitroxextreme View Post
Im not sure on the legality of this (actually tryin to find the answer myself)....
Couldnt you just run a ground from the distribution block to a smaller circuit board...the circuit boards have plenty of extra ground points on them.

This would also cut down on the size of the power distribution block.
Jon,
I am guessing you are talking about the ground returns on the small Maxi fuse panels. And you would be correct that this would work. However, the Tips and Guidelines supported by a Team Update require that the negative leads of the high current loads be returned to the distro blocks. This is also a good practice as it shortens the length of the return wiring and places the connections in terminals better designed to handle the high current and larger wires.
My initial concern, though, is with the current capability of the jumper accessory (the four position, yellow piece with four screws). Since we will potentially have currents of 300 amps or more passing through the jumpers, I want to know exactly what they are capable of so that I can plan the load balance accordingly. I am guessing that for most robot designs, these will be fine. On those rare robots with six motor drives and lot's of accessories that the current might burn one open and take out part of the block in the process. Does anyone else think it odd that manufacturers do not spec this part in their literature. (Even German manufacturers do not.)
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #12   Spotlight this post!  
Unread 21-01-2008, 17:05
Ryank's Avatar
Ryank Ryank is offline
Registered User
FRC #2523
Team Role: Student
 
Join Date: Jan 2008
Rookie Year: 2008
Location: St Johnsbury
Posts: 18
Ryank is an unknown quantity at this point
Re: Power Distribution Block Grounding

Quote:
Originally Posted by eugenebrooks View Post
From the battery power terminal strip documentation:

Maximum Wire Size and Max Quantity Allowed per 1492-J16xx Terminal

1 - #6 or
1 - #8 or
2 - #10 or
3 - #12 or
4 - #14 or
4 - #16

Don't mess up, the technical inspectors will no doubt be checking.

Also, you want to arrange the wiring to minimize the amount
of current that a given leg of the "jumper" will be carrying.

Have fun,
Eugene
Can you still do this or have the rules changed? We have also been wanting to consolidate out victor returns without using both sides of the block.
__________________
If robots fail to conquer the world then Twinkies most certainly will, beware, they're smarter than you might think.
  #13   Spotlight this post!  
Unread 21-01-2008, 20:37
DonRotolo's Avatar
DonRotolo DonRotolo is offline
Back to humble
FRC #0832
Team Role: Mentor
 
Join Date: Jan 2005
Rookie Year: 2005
Location: Atlanta GA
Posts: 7,011
DonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond reputeDonRotolo has a reputation beyond repute
Re: Power Distribution Block Grounding

That's not a rule, it's the manufacturer's recommendation (which, I have to mention, really really should be followed. Not doing so is poor engineering practice, and you might get dinged at inspection for it).

Don
__________________

I am N2IRZ - What's your callsign?
  #14   Spotlight this post!  
Unread 21-01-2008, 22:21
Bleak's Avatar
Bleak Bleak is offline
Registered User
FRC #2016 (MuMuPsi)
Team Role: Electrical
 
Join Date: Jan 2008
Rookie Year: 2006
Location: EWING
Posts: 2
Bleak is an unknown quantity at this point
Re: Power Distribution Block Grounding

Quote:
Originally Posted by Mike Betts View Post
Karma,

There should be no problem in using all 7 positions on the block. Also, you should find that the block accepts 6AWG wire. Connecting 2 (or 3) 10 or 12 AWG wires into one "port" should not be a problem.
would it not be easier to wire the negatives from the victors to the excess negative terminals on the smaller fuse box.. its still creates the same circuit and the fuse block only has 6 positive terminals so why not put them to use
  #15   Spotlight this post!  
Unread 21-01-2008, 22:29
ebarker's Avatar
ebarker ebarker is offline
Registered User
AKA: Ed Barker
FRC #1311 (Kell Robotics)
Team Role: Mentor
 
Join Date: Jan 2006
Rookie Year: 2006
Location: Kennesaw GA
Posts: 1,437
ebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond reputeebarker has a reputation beyond repute
Re: Power Distribution Block Grounding

Quote:
Originally Posted by Bleak View Post
would it not be easier to wire the negatives from the victors to the excess negative terminals on the smaller fuse box.. its still creates the same circuit and the fuse block only has 6 positive terminals so why not put them to use
Watch out. Wire the motor +/- leads directly to the victor output terminals. Do not wire it any other way.

You have to understand how the victors work. It can apply progressively variable voltage to the motor for forward speed, or reverse the terminals progressively for reverse speed.

It is the reversal that will get you in a bucket of troubles if you try to move the 'ground' off the victor onto a block.
__________________
Ed Barker
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Question:Power Distribution Block Pavan Dave Electrical 35 20-03-2007 20:10
Power Distribution Block Wiring slimemonkey Electrical 11 04-02-2007 18:40
Power distribution Block? Pontchartrain Electrical 3 27-01-2006 07:30
Stinger Fuse Block and Power Distribution Block Don Wright Electrical 2 30-03-2004 10:45