need help with power dist block & maxi bkr

I see a list of # of wires per block, like 1 #6, 3-#10s. I take it that means 3 #10s in the same hole on the same block?
About Maxi breaker panel: I have #6 from power block to one side of maxi breaker, the other side of maxi breaker has #6 to the other breaker panel. Is that allowed? or do I need #6 from power block to other panel?
  #2   Spotlight this post!  
Unread 07-02-2007, 10:44
Unsung FIRST Hero
Mike Betts Mike Betts is offline
Electrical Engineer
no team
Team Role: Engineer
 
Join Date: Dec 2001
Rookie Year: 1995
Location: Homosassa, FL
Posts: 1,442
Mike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond repute
Re: need help with power dist block & maxi bkr

Quote:
Originally Posted by steve d View Post
I see a list of # of wires per block, like 1 #6, 3-#10s. I take it that means 3 #10s in the same hole on the same block?
About Maxi breaker panel: I have #6 from power block to one side of maxi breaker, the other side of maxi breaker has #6 to the other breaker panel. Is that allowed? or do I need #6 from power block to other panel?
Steve,

Look at this drawing.

Mike
__________________
Mike Betts

Alumnus, Team 3518, Panthrobots, 2011
Alumnus, Team 177, Bobcat Robotics, 1995 - 2010
LRI, Connecticut Regional, 2007-2010
LRI, WPI Regional, 2009 - 2010
RI, South Florida Regional, 2012 - 2013

As easy as 355/113...
  #3   Spotlight this post!  
Unread 07-02-2007, 12:26
eugenebrooks eugenebrooks is offline
Team Role: Engineer
AKA: Dr. Brooks
no team (WRRF)
 
Join Date: Jan 2004
Rookie Year: 2001
Location: Livermore, CA
Posts: 601
eugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond reputeeugenebrooks has a reputation beyond repute
Re: need help with power dist block & maxi bkr

Quote:
Originally Posted by steve d View Post
I see a list of # of wires per block, like 1 #6, 3-#10s. I take it that means 3 #10s in the same hole on the same block?
About Maxi breaker panel: I have #6 from power block to one side of maxi breaker, the other side of maxi breaker has #6 to the other breaker panel. Is that allowed? or do I need #6 from power block to other panel?
All of the connections to the black ground block, and similarly the red 12 volt block, are equivalent. There is no input side, and output side. Your wiring of the #6 12 volt wire through a single power block to a #6 wire on the other side going to a breaker panel is correct, and smart, because it minimizes the voltage drop to the breaker panel. If you use a second breaker panel, you have to use a second red power block. Choose the breaker panel with the least load for this to minimize voltage drop on the yellow jumper.

For the ground power block, you can put multiple wires in a given terminal as long as you satisfy the wiring rules in the documentation that was provided by FIRST. FIRST provided (from the manufacturer) the power block documentation that indicates up to 3 #10 wires are allowed in the power block. Use the same strategy for the high current wiring as the positive side, arranging the high current connections so the amount of current across the jumper is minimized.

If you feel that there is a conflict between the power block documentation, provided by FIRST, and the written rules and the power distribution diagram, you can ask a question on the QandA.

<<<I have #6 from power block to one side of maxi breaker, the other side of maxi breaker has #6 to the other breaker panel. Is that allowed? or do I need #6 from power block to other panel?>>>
Power feed wires must go from the power block to the breaker panels, not through the breaker panels.

Eugene

Last edited by eugenebrooks : 07-02-2007 at 17:18. Reason: Miss-read an error in the post.
  #4   Spotlight this post!  
Unread 07-02-2007, 14:22
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,798
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: need help with power dist block & maxi bkr

Steve,
The original robot electrical diagram was incorrect. You have that early version. Please see the revised version in the link that Mike posted.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #5   Spotlight this post!  
Unread 07-02-2007, 18:07
steve d steve d is offline
Registered User
FRC #1277
 
Join Date: Jan 2007
Location: Groton, ma
Posts: 38
steve d is an unknown quantity at this point
Re: need help with power dist block & maxi bkr

Thanks to all and to all a good night!
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Modifying 40 Amp maxi fuse block kborer22 Electrical 18 23-01-2007 10:12
Do we need to use the gnd stud and MAXI fuse block Noah Melamed Electrical 14 03-03-2004 20:38
Anyone knowwhere to buy maxi block distribution block? BrianB Kit & Additional Hardware 0 23-01-2003 12:46


All times are GMT -5. The time now is 20:44.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi