wire size on the motors

The wire on the CIM motors is 14 guage, but regulations require 12 guage wire for anything connected to a 40 amp breaker? What should I do if I want to use these motors on a 40 amp breaker? Currently I'm just connecting the wire that came with the motors to the victor.
__________________
"You do realize that most of the substances that you are inhaling right now are considered toxic in the state of California"
-Paolo to me while I am covered in Teflon and soldering.
"Stupid Chinese 6011 Alloy is stronger than we thought."
"Comrade, your sacrifice brings honor to the motherbot."
  #2   Spotlight this post!  
Unread 01-03-2007, 18:57
bjimster1's Avatar
bjimster1 bjimster1 is offline
Registered User
AKA: Jimmy Bourne
FRC #1029 (Wolvcats)
Team Role: Mentor
 
Join Date: Mar 2005
Rookie Year: 2004
Location: Miami, FL
Posts: 117
bjimster1 is just really nicebjimster1 is just really nicebjimster1 is just really nicebjimster1 is just really nice
Send a message via AIM to bjimster1
Re: wire size on the motors

thats fine. but if you need to "make an extension" then you're gonna have to use the 12 gauge wire.
__________________
-2006 UCF Quarterfinalists w/ 1345 & 21
-2005 Peachtree Quarterfinalists w/ 1180 & 462
-2005 UCF Quarterfinalists w/ 1694 & 348

CMU '11
  #3   Spotlight this post!  
Unread 01-03-2007, 19:25
Arille's Avatar
Arille Arille is offline
Registered User
FRC #2135
Team Role: Leadership
 
Join Date: Jan 2007
Rookie Year: 2007
Location: California
Posts: 33
Arille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to behold
Send a message via AIM to Arille
Re: wire size on the motors

so you would use the given 14 gauge wire from the CIMS to the victors .. would that mean 14 or 12 gauge going from power +/- to power distribution block/circuit breaker?

Also, is that the same for other motors (e.g. keyang window)?

we kind of used what we had around (14 awg). hopefully theres enough time for us to make corrections in the morning of competition......
__________________
Team 2135: Presentation Invasion

Silicon Valley Regional 2007 Rookie Inspiration Award!
  #4   Spotlight this post!  
Unread 01-03-2007, 20:32
Arille's Avatar
Arille Arille is offline
Registered User
FRC #2135
Team Role: Leadership
 
Join Date: Jan 2007
Rookie Year: 2007
Location: California
Posts: 33
Arille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to behold
Send a message via AIM to Arille
Re: wire size on the motors

Sorry, I think I just found an answer to one of my questions:

<R87> 12 AWG or larger diameter wire must be used for all circuits protected by a 40A circuit breaker.

.. Looks like someone's going to be working morning of competition

Or maybe the CIMS can work off the 30A circuit breakers?? So much for the Maxi style breakers then.. Hmm.. we'll see.

(there was no prior electronics knowledge on our team .. almost everything was trial and error, mostly with some reasoning behind it , dont worry, we were being safe!)
__________________
Team 2135: Presentation Invasion

Silicon Valley Regional 2007 Rookie Inspiration Award!
  #5   Spotlight this post!  
Unread 01-03-2007, 21:41
sanddrag sanddrag is offline
On to my 16th year in FRC
FRC #0696 (Circuit Breakers)
Team Role: Teacher
 
Join Date: Jul 2002
Rookie Year: 2002
Location: Glendale, CA
Posts: 8,517
sanddrag has a reputation beyond reputesanddrag has a reputation beyond reputesanddrag has a reputation beyond reputesanddrag has a reputation beyond reputesanddrag has a reputation beyond reputesanddrag has a reputation beyond reputesanddrag has a reputation beyond reputesanddrag has a reputation beyond reputesanddrag has a reputation beyond reputesanddrag has a reputation beyond reputesanddrag has a reputation beyond repute
Re: wire size on the motors

Quote:
Originally Posted by Arille View Post
Or maybe the CIMS can work off the 30A circuit breakers?? So much for the Maxi style breakers then.. Hmm.. we'll see.
In most situations you will want to run the CIMs with the 40 amp breakers.
__________________
Teacher/Engineer/Machinist - Team 696 Circuit Breakers, 2011 - Present
Mentor/Engineer/Machinist, Team 968 RAWC, 2007-2010
Technical Mentor, Team 696 Circuit Breakers, 2005-2007
Student Mechanical Leader and Driver, Team 696 Circuit Breakers, 2002-2004
  #6   Spotlight this post!  
Unread 01-03-2007, 21:44
Arille's Avatar
Arille Arille is offline
Registered User
FRC #2135
Team Role: Leadership
 
Join Date: Jan 2007
Rookie Year: 2007
Location: California
Posts: 33
Arille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to beholdArille is a splendid one to behold
Send a message via AIM to Arille
Re: wire size on the motors

Yeah, that's what I thought, but I wasn't so sure of myself .. thanks for confirming it!
__________________
Team 2135: Presentation Invasion

Silicon Valley Regional 2007 Rookie Inspiration Award!
  #7   Spotlight this post!  
Unread 02-03-2007, 08:05
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,795
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: wire size on the motors

Although the Chalupa motors come with #14 wire, they are relatively short and so have little series resistance to cause heating. It is a good idea to move the Victors feeding your Chalupas (both the large and small) close enough to the motor so you can use the supplied motor leads without additional wire. As pointed out, if you are using these motors for drive they are best fed with a 40 amp breaker. I would go further and make the wiring to the Victor with #10 following the suggestions found in the Tips and Guidelines for wiring.
If you must add wire, then use approved splicing technique or add smaller connectors to the wire. We use the smaller Anderson Power Products connectors. They are polarized and do not require additional insulation.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Wire Size Limit? (InsrtNameHere) Electrical 2 15-02-2006 20:20
pic: Why the mechanical team shouldnt wire the robot late at night. Andrew Rudolph Robot Showcase 4 15-02-2005 01:15
Converting to Metric Wire Size or yaniv Electrical 1 18-01-2005 10:52
schematics or wire diagrams for van door motors tml240 Technical Discussion 9 04-02-2004 18:23
Can We Wire Two Motors to a Victor? archiver 2001 4 24-06-2002 00:07


All times are GMT -5. The time now is 06:48.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi