Joel J has a reputation beyond reputeJoel J has a reputation beyond reputeJoel J has a reputation beyond reputeJoel J has a reputation beyond reputeJoel J has a reputation beyond reputeJoel J has a reputation beyond reputeJoel J has a reputation beyond reputeJoel J has a reputation beyond reputeJoel J has a reputation beyond reputeJoel J has a reputation beyond reputeJoel J has a reputation beyond repute
Solenoids + 20A breakers.

I was going to wire each of the needed solenoids on our robot this year to a spike, then each spike to its own 20A breaker, but then I saw a diagram on (the real) page 26 of the robot manual. It had the RC going to one 20A breaker, the compressor going to the other, and then Spike Relays going to a 20A breaker. So that leaves me with a question: are we allowed to wire multiple spikes to one 20A breaker? That is, 7 solenoids connected to 7 spikes, and then one 20A breaker taking all seven of the spike power connections.

Let me know. This would actually be really awesome.
__________________
Joel Johnson

Division By Zero (229) Alumni, 2003-2007
RAGE (173) Alumni, 1999-2003
  #2   Spotlight this post!  
Unread 27-01-2007, 21:51
Unsung FIRST Hero
Mike Betts Mike Betts is offline
Electrical Engineer
no team
Team Role: Engineer
 
Join Date: Dec 2001
Rookie Year: 1995
Location: Homosassa, FL
Posts: 1,442
Mike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond reputeMike Betts has a reputation beyond repute
Re: Solenoids + 20A breakers.

Joel,

From an electrical engineering perspective, wiring multiple Spikes to one 20A CB is OK as long as the total load is less than 20A. However, the 2007 Robot Power Distribution Diagram shows individual CBs to each Spike...

I would like to see someone post this question to the FIRST Q&A for a ruling clarification.

Regards,

Mike
__________________
Mike Betts

Alumnus, Team 3518, Panthrobots, 2011
Alumnus, Team 177, Bobcat Robotics, 1995 - 2010
LRI, Connecticut Regional, 2007-2010
LRI, WPI Regional, 2009 - 2010
RI, South Florida Regional, 2012 - 2013

As easy as 355/113...
  #3   Spotlight this post!  
Unread 23-01-2008, 00:51
Kat Kononov's Avatar
Kat Kononov Kat Kononov is offline
Registered User
AKA: artqny
FRC #2022 (Team IDK)
 
Join Date: Jan 2007
Rookie Year: 2007
Location: Illinois
Posts: 48
Kat Kononov is an unknown quantity at this point
Send a message via AIM to Kat Kononov
Re: Solenoids + 20A breakers.

I have a sort of related question: Am I allowed to wire two solenoids to the same spike relay if I need the two solenoids to act simultaneously?
I know the rules say I have to wire each electrical load to one Spike/Victor, but can I wire multiple loads to the same spike?
  #4   Spotlight this post!  
Unread 23-01-2008, 00:55
EricH's Avatar
EricH EricH is offline
New year, new team
FRC #1197 (Torbots)
Team Role: Engineer
 
Join Date: Jan 2005
Rookie Year: 2003
Location: SoCal
Posts: 19,814
EricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond repute
Re: Solenoids + 20A breakers.

Quote:
Originally Posted by Kat Kononov View Post
I have a sort of related question: Am I allowed to wire two solenoids to the same spike relay if I need the two solenoids to act simultaneously?
I know the rules say I have to wire each electrical load to one Spike/Victor, but can I wire multiple loads to the same spike?
Yep
Quote:
<R56> Each power regulating device (Victor speed controller or Spike relay) shall control one and only one electrical load (motor, actuator or compressor). Multiple low-load devices (e.g. pneumatic valves) may be connected to relay modules (but only one motor may be connected to each relay module).
There is also no rule about how many PWM Y-cables you can use. One Y-end to each spike (up to two) and the single end to the PWM output on the RC, and you're good.
__________________
Past teams:
2003-2007: FRC0330 BeachBots
2008: FRC1135 Shmoebotics
2012: FRC4046 Schroedinger's Dragons

"Rockets are tricky..."--Elon Musk


Last edited by EricH : 23-01-2008 at 01:12. Reason: Only read the first part of the rule...
  #5   Spotlight this post!  
Unread 23-01-2008, 01:00
Kat Kononov's Avatar
Kat Kononov Kat Kononov is offline
Registered User
AKA: artqny
FRC #2022 (Team IDK)
 
Join Date: Jan 2007
Rookie Year: 2007
Location: Illinois
Posts: 48
Kat Kononov is an unknown quantity at this point
Send a message via AIM to Kat Kononov
Re: Solenoids + 20A breakers.

Just to clarify, when it says
Quote:
Multiple low-load devices (e.g. pneumatic valves) may be connected to relay modules
Does "relay module" mean the Spike relay? And if so, then it is ok to connect two solenoid valves to one Spike, right?

Last edited by Kat Kononov : 23-01-2008 at 01:05.
  #6   Spotlight this post!  
Unread 23-01-2008, 01:06
EricRobodox's Avatar
EricRobodox EricRobodox is offline
Registered User
AKA: Eric... I think a lot
FRC #0599 (RoboDox)
Team Role: College Student
 
Join Date: Jan 2006
Rookie Year: 2001
Location: Northridge, CA
Posts: 335
EricRobodox has a brilliant futureEricRobodox has a brilliant futureEricRobodox has a brilliant futureEricRobodox has a brilliant futureEricRobodox has a brilliant futureEricRobodox has a brilliant futureEricRobodox has a brilliant futureEricRobodox has a brilliant futureEricRobodox has a brilliant futureEricRobodox has a brilliant futureEricRobodox has a brilliant future
Send a message via AIM to EricRobodox
Re: Solenoids + 20A breakers.

Why not plumb two actuators to the same solenoid if they need to go off at the same time?
__________________
My other car is being built to go to Mars in 2011.
Bet you aint got one of these...
  #7   Spotlight this post!  
Unread 23-01-2008, 01:11
EricH's Avatar
EricH EricH is offline
New year, new team
FRC #1197 (Torbots)
Team Role: Engineer
 
Join Date: Jan 2005
Rookie Year: 2003
Location: SoCal
Posts: 19,814
EricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond repute
Re: Solenoids + 20A breakers.

Quote:
Originally Posted by Kat Kononov View Post
Just to clarify, when it says

Does "relay module" mean the Spike relay? And if so, then it is ok to connect two solenoid valves to one Spike, right?
Quote:
Originally Posted by EricRobodox View Post
Why not plumb two actuators to the same solenoid if they need to go off at the same time?
I was wrong about what the rule said...

The Spike relay is the only allowed relay module. Therefore, two would be legal.
But Eric's solution would be more elegant. One solenoid, a tee shortly afterwards, and then the tubing to the actuator.
__________________
Past teams:
2003-2007: FRC0330 BeachBots
2008: FRC1135 Shmoebotics
2012: FRC4046 Schroedinger's Dragons

"Rockets are tricky..."--Elon Musk

  #8   Spotlight this post!  
Unread 23-01-2008, 01:14
Kat Kononov's Avatar
Kat Kononov Kat Kononov is offline
Registered User
AKA: artqny
FRC #2022 (Team IDK)
 
Join Date: Jan 2007
Rookie Year: 2007
Location: Illinois
Posts: 48
Kat Kononov is an unknown quantity at this point
Send a message via AIM to Kat Kononov
Re: Solenoids + 20A breakers.

That's a really good point, but I guess two separate solenoids would use two separate tubes, so the actuators can fill with air twice as fast. Otherwise, we can use one solenoid, but then both actuators would have to fill through one tube.

Please correct me if I'm wrong because we haven't tested this yet.
  #9   Spotlight this post!  
Unread 23-01-2008, 03:16
AdamHeard's Avatar
AdamHeard AdamHeard is offline
Lead Mentor
FRC #0973 (Greybots)
Team Role: Mentor
 
Join Date: Oct 2004
Rookie Year: 2004
Location: Atascadero
Posts: 5,509
AdamHeard has a reputation beyond reputeAdamHeard has a reputation beyond reputeAdamHeard has a reputation beyond reputeAdamHeard has a reputation beyond reputeAdamHeard has a reputation beyond reputeAdamHeard has a reputation beyond reputeAdamHeard has a reputation beyond reputeAdamHeard has a reputation beyond reputeAdamHeard has a reputation beyond reputeAdamHeard has a reputation beyond reputeAdamHeard has a reputation beyond repute
Send a message via AIM to AdamHeard
Re: Solenoids + 20A breakers.

Quote:
Originally Posted by Kat Kononov View Post
That's a really good point, but I guess two separate solenoids would use two separate tubes, so the actuators can fill with air twice as fast. Otherwise, we can use one solenoid, but then both actuators would have to fill through one tube.

Please correct me if I'm wrong because we haven't tested this yet.
yes, two separate systems should fill faster. Depending on what your using it for, and what size cylinder, it may not make a difference though.
  #10   Spotlight this post!  
Unread 23-01-2008, 11:22
Kat Kononov's Avatar
Kat Kononov Kat Kononov is offline
Registered User
AKA: artqny
FRC #2022 (Team IDK)
 
Join Date: Jan 2007
Rookie Year: 2007
Location: Illinois
Posts: 48
Kat Kononov is an unknown quantity at this point
Send a message via AIM to Kat Kononov
Re: Solenoids + 20A breakers.

ok. thank you everyone for your help.
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Solenoids Rohan_DHS Rules/Strategy 2 04-02-2006 00:11
20A breaker sources Rickertsen2 Electrical 2 24-02-2003 21:06
Our 20A and 30A and 40A breakers . . . Frank(Aflak) Technical Discussion 8 01-02-2003 08:36
Solenoids archiver 2001 9 23-06-2002 23:47
Solenoids turbidum Rules/Strategy 1 09-01-2002 21:26


All times are GMT -5. The time now is 06:55.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi