Spike fuse
Our team discovered that u can use the auto reset fuse for the spikes. wut u think?
|
|
#2
|
|||
|
|||
|
Re: Spike fuse
Only for the air compressors, any other use is against the rules.
|
|
#3
|
|||||
|
|||||
|
Re: Spike fuse
This is specifically allowed for the compressor spike. I'm not sure about the other ones; they may need their fuses.
|
|
#4
|
|||||
|
|||||
|
Re: Spike fuse
The fuse in the Spike that controls the compressor is the only fuse that may be changed to a 20 amp breaker. The fuse is there to protect the Spike contacts from damage. However, the start current on the compressor is higher than 20 amps for a few milliseconds. That is why this Spike only may have the fuse replaced with a breaker.
|
![]() |