<R55> relay 20A

the updated rule 55 says
Rule <R55>
-Each relay module must be protected with one and only one 20A circuit
breaker.

can someone clarify???
the yellow thing in a spike relay module is a fuse, correct?
when used with a compressor, you change the yellow fuse to the 20amp auto reset breaker correct?

so, if there is one 20A circuit breaker in the Spike and there has to be a breaker in the Fuse Panel also right? this equals 2 circuit breakers!

can someone explain how you use only one 20A breaker with the Spike Relay?

thnks.
  #2   Spotlight this post!  
Unread 05-02-2008, 20:38
Miner Miner is offline
Registered User
AKA: Jacob Miner
FRC #2077 (Laser Robotics)
Team Role: Leadership
 
Join Date: Feb 2008
Rookie Year: 2007
Location: Dousman, WI
Posts: 85
Miner is on a distinguished road
Re: <R55> relay 20A

Quote:
the yellow thing in a spike relay module is a fuse, correct?
Correct

Quote:
so, if there is one 20A circuit breaker in the Spike and there has to be a breaker in the Fuse Panel also right? this equals 2 circuit breakers!
The yellow thing in the Spike is a fuse. You cant put a breaker into that slot. The fuse must stay in the Spike. There is no Fuse Panel. There is a Breaker Panel and a Maxi block. The breaker panel is what the 20 and 30 amp auto reset breakers go into. It powers things like Spikes and the RC.

The Spikes must be powered through the breaker panel. You are correct, that does have 2 20 amp breaker/fuses in it, but the rule only applies to breakers. IF THIS IS CONFUSING AT ALL, ASK AGAIN.

The Spike will be plugged into the breaker panel on a 20 amp breaker. This just gives it double protection. Normally it is annoying to replace fuses and that is why they us the auto reset breakers. Like I said, if you need more clarification, ask again.

Good Luck
Jacob
__________________
Do what you like... Like what you do!
Jake, the Life Is Good guy
  #3   Spotlight this post!  
Unread 05-02-2008, 20:56
holty531 holty531 is offline
Registered User
FRC #2441
Team Role: Electrical
 
Join Date: Jan 2008
Rookie Year: 2008
Location: hawaii
Posts: 15
holty531 is an unknown quantity at this point
Re: <R55> relay 20A

so to clarify..

compressor>spike[20ampAutobreaker]>breakerpanel[20amp autobreaker]

thats two 20amp breakers?...or do we put the fuse in the breakerpanel instead?
  #4   Spotlight this post!  
Unread 05-02-2008, 21:00
Miner Miner is offline
Registered User
AKA: Jacob Miner
FRC #2077 (Laser Robotics)
Team Role: Leadership
 
Join Date: Feb 2008
Rookie Year: 2007
Location: Dousman, WI
Posts: 85
Miner is on a distinguished road
Re: <R55> relay 20A

The fuse is what is inside the Spike. It can be replaced if blown. The fuse will look black and the connection will be broken.

Starting at the power source (positive lead):

Battery
Breaker Panel
20 amp auto reset breaker (in the breaker panel)
Spike (positive lead)
20 amp fuse (in the Spike)
Compressor

The power first goes through a breaker, and then through a fuse in the Spike, then on to the Compressor.
__________________
Do what you like... Like what you do!
Jake, the Life Is Good guy
  #5   Spotlight this post!  
Unread 05-02-2008, 21:10
holty531 holty531 is offline
Registered User
FRC #2441
Team Role: Electrical
 
Join Date: Jan 2008
Rookie Year: 2008
Location: hawaii
Posts: 15
holty531 is an unknown quantity at this point
Re: <R55> relay 20A

i have previously heard that the compressor frequently blows the yellow fuse, so people have took out the yellow fuse and put in a 20amp auto breaker;to save money...

so is this new rule outlawing this?
  #6   Spotlight this post!  
Unread 05-02-2008, 21:12
Vikesrock's Avatar
Vikesrock Vikesrock is offline
Team 2175 Founder
AKA: Kevin O'Connor
no team
Team Role: Engineer
 
Join Date: Mar 2006
Rookie Year: 2007
Location: Manchester, NH
Posts: 3,305
Vikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond repute
Send a message via AIM to Vikesrock Send a message via MSN to Vikesrock Send a message via Yahoo to Vikesrock
Re: <R55> relay 20A

The fuse in the Spike may be replaced with a breaker for and ONLY FOR the compressor.
__________________


2007 Wisconsin Regional Highest Rookie Seed & Regional Finalists (Thanks 930 & 2039)
2008 MN Regional Semifinalists (Thanks 2472 & 1756)
2009 Northstar Regional Semifinalists (Thanks 171 & 525)
  #7   Spotlight this post!  
Unread 05-02-2008, 21:15
Miner Miner is offline
Registered User
AKA: Jacob Miner
FRC #2077 (Laser Robotics)
Team Role: Leadership
 
Join Date: Feb 2008
Rookie Year: 2007
Location: Dousman, WI
Posts: 85
Miner is on a distinguished road
Re: <R55> relay 20A

Quote:
The fuse in the Spike may be replaced with a breaker for and ONLY FOR the compressor.
I have not heard that, or read it either. Is that in the rules? If it is allowed it could save a great deal of money. Cool.
__________________
Do what you like... Like what you do!
Jake, the Life Is Good guy
  #8   Spotlight this post!  
Unread 05-02-2008, 21:21
Vikesrock's Avatar
Vikesrock Vikesrock is offline
Team 2175 Founder
AKA: Kevin O'Connor
no team
Team Role: Engineer
 
Join Date: Mar 2006
Rookie Year: 2007
Location: Manchester, NH
Posts: 3,305
Vikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond reputeVikesrock has a reputation beyond repute
Send a message via AIM to Vikesrock Send a message via MSN to Vikesrock Send a message via Yahoo to Vikesrock
Re: <R55> relay 20A

Yes, this in the rules, here you go:

Quote:
Originally Posted by FRC Manual
<R67> The control system is provided to allow wireless control of the ROBOTS. The Operator
Interface, Robot Controller, speed controllers, relay modules, radio modems, batteries,
battery charger, AC adapter, and 9-pin cables shall not be tampered with, modified, or
adjusted in any way (tampering includes drilling, cutting, machining, gluing, rewiring, etc.),
with the following exceptions:
 Dip switches on the Operator Interface may be set as appropriate.
 User programmable code in the Robot Controller may be customized.
 Speed controllers may be calibrated as described in owner's manuals.
 The fuse on the Spike relay for the air compressor may be replaced with a 20 Amp Snap-
Action circuit breaker.
__________________


2007 Wisconsin Regional Highest Rookie Seed & Regional Finalists (Thanks 930 & 2039)
2008 MN Regional Semifinalists (Thanks 2472 & 1756)
2009 Northstar Regional Semifinalists (Thanks 171 & 525)
  #9   Spotlight this post!  
Unread 05-02-2008, 21:25
Miner Miner is offline
Registered User
AKA: Jacob Miner
FRC #2077 (Laser Robotics)
Team Role: Leadership
 
Join Date: Feb 2008
Rookie Year: 2007
Location: Dousman, WI
Posts: 85
Miner is on a distinguished road
Re: <R55> relay 20A

Quote:
The fuse on the Spike relay for the air compressor may be replaced with a 20 Amp Snap-
Action circuit breaker.
Thank you much.
__________________
Do what you like... Like what you do!
Jake, the Life Is Good guy
  #10   Spotlight this post!  
Unread 05-02-2008, 23:55
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,798
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: <R55> relay 20A

Holty et al,
The 20 amp breaker that must feed each Spike is in place to protect the wiring that runs to the Spike. Should that wire short, the breaker trips to protect the wire from self destruction. The 20 amp fuse on the Spike itself is to protect the contacts of the relays inside the Spike from destruction. The fuse on the Spike that feeds the compressor may be changed to a 20 amp self resetting breaker as shown in the rules quoted above. The compressor has a start current of 25 amps while it only has a run current of 10.5 amps. If you don't change the fuse to a breaker, you will most definetly be changing the fuse often. Remember this rule only applies to the compressor Spike and no others.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #11   Spotlight this post!  
Unread 11-02-2008, 10:58
sabruce01 sabruce01 is offline
Registered User
FRC #2389
 
Join Date: Jan 2008
Location: Drumright, Oklahoma
Posts: 22
sabruce01 will become famous soon enough
Re: <R55> relay 20A

Are we required to use the same type of auto reset fuse that came in the KOP, or can we just obtain another type of auto reset type fuse from our local parts store?
  #12   Spotlight this post!  
Unread 11-02-2008, 11:03
vhcook's Avatar
vhcook vhcook is offline
Reader of Things
AKA: Victoria
FRC #1939 (Kuh-nig-its)
Team Role: Mentor
 
Join Date: Feb 2007
Rookie Year: 2006
Location: Kansas City, MO
Posts: 546
vhcook has a reputation beyond reputevhcook has a reputation beyond reputevhcook has a reputation beyond reputevhcook has a reputation beyond reputevhcook has a reputation beyond reputevhcook has a reputation beyond reputevhcook has a reputation beyond reputevhcook has a reputation beyond reputevhcook has a reputation beyond reputevhcook has a reputation beyond reputevhcook has a reputation beyond repute
Re: <R55> relay 20A

You are required to use the exact same type of snap-action circuit breaker as in the KOP. See the third bullet on <R45> for details.
__________________


  #13   Spotlight this post!  
Unread 11-02-2008, 11:06
Alan Anderson's Avatar
Alan Anderson Alan Anderson is offline
Software Architect
FRC #0045 (TechnoKats)
Team Role: Mentor
 
Join Date: Feb 2004
Rookie Year: 2004
Location: Kokomo, Indiana
Posts: 9,113
Alan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond reputeAlan Anderson has a reputation beyond repute
Re: <R55> relay 20A

The Manual Is Your Friend.

Quote:
Originally Posted by <R45>
Items specifically PROHIBITED from use on the ROBOT include:...Circuit breakers different from those provided in the Kit Of Parts. Note: the Snap Action brand circuit breakers provided have unique “trip” characteristics. No substitute brands are permitted.
Quote:
Originally Posted by <R55>
All active circuit breaker / power distribution panel branch circuits shall be protected from overload with an appropriate value auto resetting Snap Action circuit breaker from the Kit Of Parts.
  #14   Spotlight this post!  
Unread 11-02-2008, 11:59
sabruce01 sabruce01 is offline
Registered User
FRC #2389
 
Join Date: Jan 2008
Location: Drumright, Oklahoma
Posts: 22
sabruce01 will become famous soon enough
Re: <R55> relay 20A

Oh well, guess I'll place another order!

Last edited by sabruce01 : 11-02-2008 at 12:15.
  #15   Spotlight this post!  
Unread 11-02-2008, 12:54
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,798
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: <R55> relay 20A

Be sure to read R55 in both Team Update 8 & 9 for the latest info on this question.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Relay program? team877 Programming 11 04-02-2008 11:11
Solenoids + 20A breakers. Joel J Electrical 9 23-01-2008 11:22
Relay Commands Matt Krass Programming 6 18-02-2006 23:03
20A breaker sources Rickertsen2 Electrical 2 24-02-2003 21:06
Our 20A and 30A and 40A breakers . . . Frank(Aflak) Technical Discussion 8 01-02-2003 08:36


All times are GMT -5. The time now is 21:05.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi