Re: Circuit Breakers

I follow what you are both saying and I agree that the CIMs are 40amps. But is there a clear cut rule written down that matches motors to the appropriate ckt bkr? Is every team just going by past experience?

How would you go by wire size? Do we know what size wire is required for each motor?
__________________

Last edited by Teammax : 31-01-2009 at 13:09.
  #2   Spotlight this post!  
Unread 31-01-2009, 13:18
Tristan Lall's Avatar
Tristan Lall Tristan Lall is offline
Registered User
FRC #0188 (Woburn Robotics)
 
Join Date: Aug 2001
Rookie Year: 1999
Location: Toronto, ON
Posts: 2,484
Tristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond reputeTristan Lall has a reputation beyond repute
Re: Circuit Breakers

Quote:
Originally Posted by Teammax View Post
I follow what you are both saying and I agree that the CIMs are 40amps. But is there a clear cut rule written down that matches motors to the appropriate ckt bkr? Is every team just going by past experience?

How would you go by wire size? Do we know what size wire is required for each motor?
Years ago, the rules required certain breakers for different motors. Nowadays, FIRST considers the function of the circuit breaker to be protection of the wiring. Teams supply excessive current to the motors at their own risk. Therefore, for general robot wiring, circuit breakers correspond to wire gauges only.

To protect the motor, which is optional, you've got to figure out how much current the motor can draw, and for how long, before failure. The motor's specification sheet is a good starting point for this, because it will tell you what the maximum (stall) current of a motor is. The actual time to failure is not specified—so make an educated guess. Then, you consult the circuit breaker's specification sheet, and determine if it will trip before the motor fails.
  #3   Spotlight this post!  
Unread 31-01-2009, 14:15
Teammax's Avatar
Teammax Teammax is offline
30 Members 6 Weeks 1 Dream
AKA: Rob Cormier
FRC #1071 (Team MAX)
Team Role: Mentor
 
Join Date: Jan 2007
Rookie Year: 2000
Location: Wolcott, Connecticut
Posts: 165
Teammax is just really niceTeammax is just really niceTeammax is just really niceTeammax is just really nice
Re: Circuit Breakers

If this is the official stand then it makes sense. We are planning on using a 20amp breaker with 18gauge wire for the RS545 motor but I did not want to fail inspection because of this. I do think both are adequate.

Thanks for your help
__________________
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Circuit breakers? k4r3n2 Electrical 7 28-01-2008 03:36
circuit breakers.... archiver 2001 2 23-06-2002 23:58
Circuit breakers archiver 2000 8 23-06-2002 23:30
Circuit Breakers: Tripping Al Skierkiewicz Electrical 7 10-04-2002 12:40
Circuit Breakers ark_1230 Electrical 28 09-04-2002 23:16


All times are GMT -5. The time now is 10:51.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi