Re: Last Minute Pneumatics Programming Help

Regarding the Spike relay. The Users manual for a blue spike manual is located at:

http://www.ifirobotics.com/docs/spik...uide-sep05.pdf

The users manual indicates that the indicator is orange when both solenoids are off. When the Relay is set to the "forward" direction, the M+ is connected to the +12, and the indicator will be green (i.e when the indicator is green, the compressor should be running).

Here's what I would do:

1. Disconnect the power, ground, M+, M- wires from the Spike relay (leave the PWM/relay cable hooked up).
2. In LabVIEW, open the Relay Example vi.
3. Set the Relay Channel to the relay that you are using.
4. Set the Relay Direction to forward only (compressor only runs in "forward" direction).
5. Run the Relay Example VI and set the Relay Value to Off and then to Forward.
a. When you set the Relay Value to Off, the relay indicator should turn orange.
b. When you set the Relay Value to Forward, the indicator light should turn green.
6. Test the continuity between connections to see if they are what you expect. When Relay Value is Off, both M+ and M- should be connected with ground. When relay value is Forward, I would expect
a. continuity between Ground and M-
b. continuity between +12 and M+

If the above all works quit the Relay Example VI and test the pressure switch:

7. Open the Simple Digital Input Example vi.
8. Set the DIO channel to be the same as your pressure switch.
9. Run Simple Digital Input Example.vi to see if the pressure switch is really closed (it should be if there's no pressure).
10. If that's working, then stop and close the Simple Digital Input Example.vi

11. open the Solenoid with Compressor Example.vi
12. run the Solenoid with Compressor Example.vi
13. test for continuity as above in step 6.

If this is all working, then you should be able to hook up the power wires and the compressor wires, and it should work.

-Nate
Reply With Quote
 


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Last minute autonomous programming! ZP8892 Programming 7 16-03-2008 22:43
Last Minute Programmer - Need Help! burkey_turkey Programming 11 04-03-2008 23:16
pneumatics programming help diaperrash89 Programming 0 14-02-2008 17:19
Last Minute Programming Failures robobrain0101 Programming 3 11-02-2007 14:30
Last-Minute changes? Iain McLeod General Forum 9 09-04-2003 02:51


All times are GMT -5. The time now is 21:48.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi