Is there any reason why we could not attach a CIM motor to a spike? If we can, what should be the rating on the breaker on the power distribution panel?
Thanks in advanced! |
|
#2
|
||||
|
||||
|
Re: Spike to CIM Motor
<R55-A> is a pretty good reason.
|
|
#3
|
|||||
|
|||||
|
Re: Spike to CIM Motor
A spike cannot be used on a CIM as shown in the rule Joe pointed but more importantly, the relay in the Spike can only handle 20 amps. The stall current of a CIM is 129 amps. Stall current is drawn everytime the motor starts or is held in place while power is applied. That amount of current will cause catastrophic damage to the Spike. Like wise the rule applies to other motors as well. The FP has a stall current rating more than three times the rated current of the Spike.
Last edited by Al Skierkiewicz : 03-02-2010 at 19:58. |
|
#4
|
||||
|
||||
|
Re: Spike to CIM Motor
Something that seems new this year is, as best I we can determine, you are allowed to have multiple smaller motors on one speed controller per <R55>. For example you can gang up the two wimpy RS555 motors on one Jaguar. This seems different than previous years but maybe we've always been overly conservative.
Does anyone have a different interpretation? |
|
#5
|
|||||
|
|||||
|
Re: Spike to CIM Motor
I have a different rule instead. <R49> prohibits the scenario you suggest. Multiple solenoids on a single Spike is the only multiple load, single controller configuration allowed.
|
|
#6
|
||||
|
||||
|
Re: Spike to CIM Motor
Ahh, right you are. Thanks for that.
|
|
#7
|
|||
|
|||
|
Re: Spike to CIM Motor
Thanks everyone!
|
![]() |
| Thread Tools | |
| Display Modes | Rate This Thread |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| your thoughts on the FP CIM/2.5 CIM motor drive setup versus 2 2.5 CIM motors | waialua359 | Motors | 11 | 14-12-2007 04:29 |
| dewalt motor VS. CIM motor | John Gutmann | Motors | 12 | 10-01-2007 18:57 |
| Globe motor to spike controller | stephenthe1 | Motors | 25 | 19-02-2006 23:03 |
| Motor Question- Victor/Spike? | 1166 | Motors | 10 | 16-02-2004 16:57 |
| Window Motor With Spike/Victor | supergrover | Control System | 9 | 30-01-2004 15:38 |