  #16   Spotlight this post!  
Unread 31-03-2010, 10:14
Racer26 Racer26 is offline
Registered User
no team
Team Role: Alumni
 
Join Date: Apr 2003
Rookie Year: 2003
Location: Beaverton, ON
Posts: 2,229
Racer26 has a reputation beyond reputeRacer26 has a reputation beyond reputeRacer26 has a reputation beyond reputeRacer26 has a reputation beyond reputeRacer26 has a reputation beyond reputeRacer26 has a reputation beyond reputeRacer26 has a reputation beyond reputeRacer26 has a reputation beyond reputeRacer26 has a reputation beyond reputeRacer26 has a reputation beyond reputeRacer26 has a reputation beyond repute
Re: 30a breaker for 40a spot on pdb

Literally thousands of teams have been using 4 CIM drivetrains with 40A breakers on each CIM for years. I doubt this is your issue.

Personally, my team has never tripped the 120A main breaker. We've had the 40A's in a 4CIM treaded tank drive stalled and popping, and never popping the main. I would look to something mechanical, or possibly a faulty main breaker.
  #17   Spotlight this post!  
Unread 31-03-2010, 10:19
Joe Ross's Avatar Unsung FIRST Hero
Joe Ross Joe Ross is offline
Registered User
FRC #0330 (Beachbots)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1997
Location: Los Angeles, CA
Posts: 8,602
Joe Ross has a reputation beyond reputeJoe Ross has a reputation beyond reputeJoe Ross has a reputation beyond reputeJoe Ross has a reputation beyond reputeJoe Ross has a reputation beyond reputeJoe Ross has a reputation beyond reputeJoe Ross has a reputation beyond reputeJoe Ross has a reputation beyond reputeJoe Ross has a reputation beyond reputeJoe Ross has a reputation beyond reputeJoe Ross has a reputation beyond repute
Re: 30a breaker for 40a spot on pdb

There was a team at the Los Angeles regional who's circuit breaker would trip when they had a hard impact. After repositioning it and shock mounting it, it still occurred. They were able to reproduce the problem on the practice field by running it into the wall or over a bump hard. They replaced it with a new breaker and it didn't happen again.

What was the position of the black lever on the circuit breaker when you lost power?
  #18   Spotlight this post!  
Unread 31-03-2010, 12:05
Bruceb's Avatar
Bruceb Bruceb is offline
Registered User
FRC #0706 (Cyberhawks)
Team Role: Mentor
 
Join Date: Jan 2008
Rookie Year: 2004
Location: Merton, wi
Posts: 620
Bruceb is a splendid one to beholdBruceb is a splendid one to beholdBruceb is a splendid one to beholdBruceb is a splendid one to beholdBruceb is a splendid one to beholdBruceb is a splendid one to beholdBruceb is a splendid one to behold
Re: 30a breaker for 40a spot on pdb

it was in the tripped....lever sticking out position. Just like it is when you push the red button.
Also for EricH. You say we have Wednesday night to get ready for competition but the rules I have read say uncrating only on Wednesday night. Doesn't even look like they want you setting up the pit or working on the robot at all. What am I missing?
Bruce
  #19   Spotlight this post!  
Unread 31-03-2010, 12:16
Kris Verdeyen's Avatar
Kris Verdeyen Kris Verdeyen is offline
LSR Emcee/Alamo Game Announcer
FRC #0118 (Robonauts)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 2001
Location: Houston, TX
Posts: 699
Kris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond reputeKris Verdeyen has a reputation beyond repute
Re: 30a breaker for 40a spot on pdb

The main breaker will run at 2x its rated current for at least ten and up to 40 seconds. That's 240 amps. If it tripped on the field, inspect your big wires and crimps (between the breaker and fuse panel) for shorts, and consider replacing the breaker itself. The big breaker is there to keep stuff from catching fire, it shouldn't trip in regular operation.
__________________
...Only a few people are awake and they live in a state of constant total amazement. -JP Shanley, Joe vs. the Volcano
  #20   Spotlight this post!  
Unread 31-03-2010, 12:53
EricH's Avatar
EricH EricH is offline
New year, new team
FRC #1197 (Torbots)
Team Role: Engineer
 
Join Date: Jan 2005
Rookie Year: 2003
Location: SoCal
Posts: 19,827
EricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond repute
Re: 30a breaker for 40a spot on pdb

Quote:
Originally Posted by Bruceb View Post
it was in the tripped....lever sticking out position. Just like it is when you push the red button.
Also for EricH. You say we have Wednesday night to get ready for competition but the rules I have read say uncrating only on Wednesday night. Doesn't even look like they want you setting up the pit or working on the robot at all. What am I missing?
Bruce
The FIRST email about the Championship is what you're missing.

They've been monkeying with the Championship schedule and similar things to allow the following on Wednesday night:
--Uncrating
--Pit setup
--Inspection
--work on robots (after all, you want to fix what you found out was illegal at inspection, right?)

They just haven't updated any Manual sections that cover this sort of thing--but all the info comes from Bill Miller and/or the FRC staff, so it's legit.
__________________
Past teams:
2003-2007: FRC0330 BeachBots
2008: FRC1135 Shmoebotics
2012: FRC4046 Schroedinger's Dragons

"Rockets are tricky..."--Elon Musk

  #21   Spotlight this post!  
Unread 31-03-2010, 14:44
Bruceb's Avatar
Bruceb Bruceb is offline
Registered User
FRC #0706 (Cyberhawks)
Team Role: Mentor
 
Join Date: Jan 2008
Rookie Year: 2004
Location: Merton, wi
Posts: 620
Bruceb is a splendid one to beholdBruceb is a splendid one to beholdBruceb is a splendid one to beholdBruceb is a splendid one to beholdBruceb is a splendid one to beholdBruceb is a splendid one to beholdBruceb is a splendid one to behold
Re: 30a breaker for 40a spot on pdb

Are they allowing more then 5 people in to do all that stuff Wednesday night?
Bruce
  #22   Spotlight this post!  
Unread 31-03-2010, 15:44
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,798
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: 30a breaker for 40a spot on pdb

Bruce,
There was another team in Milwaukee that also tripped the main breaker. They thought is was protected as well but what we found was a small crack in the case. The slight misalignment was enough to cause the breaker to let go. There is another known issue with the breaker. A few over the years have shown up with manufacturing defect. A simple tap on the red button is sufficient to trip the breaker. The test is to tap with your finger and see if it fails. Over the last four years I think I have seen a total of less than ten.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #23   Spotlight this post!  
Unread 31-03-2010, 16:33
EricH's Avatar
EricH EricH is offline
New year, new team
FRC #1197 (Torbots)
Team Role: Engineer
 
Join Date: Jan 2005
Rookie Year: 2003
Location: SoCal
Posts: 19,827
EricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond reputeEricH has a reputation beyond repute
Re: 30a breaker for 40a spot on pdb

Quote:
Originally Posted by Bruceb View Post
Are they allowing more then 5 people in to do all that stuff Wednesday night?
Bruce
Nope. 5 is the max, unless you can steal some from another team that's already in there. (All the other teams are probably trying to do the same thing...)
__________________
Past teams:
2003-2007: FRC0330 BeachBots
2008: FRC1135 Shmoebotics
2012: FRC4046 Schroedinger's Dragons

"Rockets are tricky..."--Elon Musk

  #24   Spotlight this post!  
Unread 31-03-2010, 17:09
robself705's Avatar
robself705 robself705 is offline
Team Leader / Mechanical
AKA: Rob Self
FRC #0706 (Cyberhawks)
Team Role: Mechanical
 
Join Date: Nov 2008
Rookie Year: 2009
Location: Arrowhead High School Wisconsin
Posts: 72
robself705 is a name known to allrobself705 is a name known to allrobself705 is a name known to allrobself705 is a name known to allrobself705 is a name known to allrobself705 is a name known to all
Re: 30a breaker for 40a spot on pdb

Ok, I know what everyone is saying that the breakers should last well above their rated amperage but this is not true and it is not the issue or the question. I physically tested all of the breakers yesterday because we are adding a programmed throttling device that limits the cim motor power under high loads. We have an external ammeter that measures the amperage draw to 2 amps. Yesterday I WAS ACTUALLY STALLING A CIM and tripping the 40 amp breaker, the problem is each 40 amp breaker will let you pull 50 amps for about 2 seconds before it trips. They let you spike up to 80 amps for a fraction of a second. We can draw 180 + amps for over 30 seconds JUST FROM OUR CIMS. We also have a vacuum that draws up to 30 amps continuously. WE ACTUALLY TRIPPED OUR BREAKER IN A MATCH. So its not a question of whether or not it can happen, it did. Switching to 30 amp breakers would partially solve the issue. I tested them and they allow about 35 amps draw for a second before they trip. This would mean MAX from the cims we could draw 140 amps for just second. This would partially solve our issue, it would just be a lot easier to swap them they have to re wire. We are counting more on our current draw feedback to keep this issue from happening again. But it does happen, the main can be tripped.

However we might try swapping out our main breaker to see if that is the issue. I was looking at charts previously posted and it should last for 20 seconds with 200% draw. We didn't have low enough ohm resistors to test the main breaker.

I'm am not yelling so don't get the wrong impression I just want to make it clear what the issue is. Thanks for everyone's valuable input
__________________
Rob Self-
Cyberhawks Team 706
Hartland, WI

Our breakaway bot in action (13-3-1): Team 706 in action

Last edited by robself705 : 31-03-2010 at 19:50.
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
A Tip for the PDB Pavan Dave Electrical 4 06-01-2008 22:20
CIM motor on 30A jason701802 Motors 4 05-02-2007 20:23
What guage wire do you use for 40A circuits SuperBK Electrical 6 21-01-2007 14:58
Bad 40A Breaker Richard Wallace Electrical 3 18-02-2003 21:42
Our 20A and 30A and 40A breakers . . . Frank(Aflak) Technical Discussion 8 01-02-2003 08:36