Determining Correct Circuit Breaker

How can we determine the correct circuit breaker to use for a particular motor? I know the CIMS use 40 AMP breakers, but we are using a PG motor and 2 Snowblower motors. Would we need to look at the stall current to determine the breaker size? Ex: the PG has a 22 amp stall current, so we'd use a 30 amp breaker.
Reply With Quote
  #2   Spotlight this post!  
Unread 02-13-2018, 10:10 PM
phargo#1018 phargo#1018 is offline
Registered User
AKA: Peter Argo
FRC #1018 (RoboDevils)
Team Role: Mentor
 
Join Date: Dec 2013
Rookie Year: 2009
Location: Indianapolis, IN, USA
Posts: 79
phargo#1018 has a brilliant futurephargo#1018 has a brilliant futurephargo#1018 has a brilliant futurephargo#1018 has a brilliant futurephargo#1018 has a brilliant futurephargo#1018 has a brilliant futurephargo#1018 has a brilliant futurephargo#1018 has a brilliant futurephargo#1018 has a brilliant futurephargo#1018 has a brilliant futurephargo#1018 has a brilliant future
Re: Determining Correct Circuit Breaker

Certainly the motor is one consideration in selecting your breaker, but you may want to consider the load you expect placed upon the motor.

I expect that you would want 40 Amp breakers for motors being used for your drive base, and possibly for your climbing mechanism. Depending upon what you choose to lift cubes you may need 40 amps for that as well. Realize that you only have 8 40 Amp slots.

Chances are motors used for intake rollers can operate properly on 20 Amp breakers.

Consider how much load you are applying to the motor and make your selection on that basis.
Reply With Quote
  #3   Spotlight this post!  
Unread 02-13-2018, 10:13 PM
MrForbes's Avatar
MrForbes MrForbes is offline
Registered User
AKA: Jim
FRC #1726 (N.E.R.D.S.)
Team Role: Mentor
 
Join Date: Feb 2006
Rookie Year: 2006
Location: Sierra Vista AZ
Posts: 6,401
MrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond repute
Re: Determining Correct Circuit Breaker

The circuit breaker is related to the size of the wire uses to connect the speed controller to the motor and PDP.

You might want to use a breaker and wiring that exceed the stall current of the motor, but you are limited to 40 amps, so you can only do that with the low power motors.

If you are running the motor near stall, you might want to rethink your design!
Reply With Quote
  #4   Spotlight this post!  
Unread 02-14-2018, 09:38 AM
Team6928 Team6928 is offline
Registered User
FRC #6928
 
Join Date: Jan 2018
Location: Greeneville, Tennessee
Posts: 58
Team6928 is an unknown quantity at this point
Re: Determining Correct Circuit Breaker

Quote:
Originally Posted by MrForbes View Post
The circuit breaker is related to the size of the wire uses to connect the speed controller to the motor and PDP.

You might want to use a breaker and wiring that exceed the stall current of the motor, but you are limited to 40 amps, so you can only do that with the low power motors.

If you are running the motor near stall, you might want to rethink your design!
We aren't running near stall, but just wanted to be sure of the breaker size. When you wire a PG motor do you wire it to a 40 amp breaker or lower? Window motors/snowblower motors I assume can use 20 amp, but not sure about the PG
Reply With Quote
  #5   Spotlight this post!  
Unread 02-14-2018, 09:47 AM
Daniel_LaFleur's Avatar
Daniel_LaFleur Daniel_LaFleur is offline
Mad Scientist
AKA: Me
FRC #2040 (DERT)
Team Role: Engineer
 
Join Date: Apr 2005
Rookie Year: 2003
Location: Peoria, IL
Posts: 2,319
Daniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond repute
Send a message via MSN to Daniel_LaFleur
Re: Determining Correct Circuit Breaker

Quote:
Originally Posted by Team6928 View Post
We aren't running near stall, but just wanted to be sure of the breaker size. When you wire a PG motor do you wire it to a 40 amp breaker or lower? Window motors/snowblower motors I assume can use 20 amp, but not sure about the PG
You need to look at the load you will put on that motor (and the duration of that load). The motor curves in the spec sheet will help you here. Loads can go above the breaker for short durations (hence the duration of the load statement)

Size the breaker for the load on that motor, then size the wires for the breaker used.
__________________
"We are not now that strength which in old days moved earth and heaven; that which we are, we are;
One equal temper of heroic hearts, Made weak by time and fate, but strong in will
To strive, to seek, to find, and not to yield. "
- Tennyson, Ulysses
Reply With Quote
  #6   Spotlight this post!  
Unread 02-14-2018, 11:44 AM
MrForbes's Avatar
MrForbes MrForbes is offline
Registered User
AKA: Jim
FRC #1726 (N.E.R.D.S.)
Team Role: Mentor
 
Join Date: Feb 2006
Rookie Year: 2006
Location: Sierra Vista AZ
Posts: 6,401
MrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond repute
Re: Determining Correct Circuit Breaker

Personally, I would use a smaller circuit breaker, either 20 or 30 amp depending on what the motor is doing, and the odds of it having to work too hard, for long enough to pop a 20 amp breaker.

As an example, we put a BAG motor on the wrist on our robot, and ran 18 gauge wire to it, and powered it from a 20 amp breaker. If it has problems, we will consider rewiring it and using a larger breaker, but I don't expect it to have problems...the control system for it is working well, and we designed it so the motor needs to use less than 20% of stall torque to operate the mechanism under load.
Reply With Quote
  #7   Spotlight this post!  
Unread 02-14-2018, 09:18 PM
garyk garyk is offline
Programming Mentor, 972 and 2643
FRC #2643 (Dark Matter)
Team Role: Mentor
 
Join Date: Dec 2006
Rookie Year: 2005
Location: Santa Clara (Silicon Valley) Calif.
Posts: 171
garyk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant future
Re: Determining Correct Circuit Breaker

Our breakers are thermal breakers and are very slow to blow. Iíve see a stalled motor pull 90 amps, measured, through a 40 amp breaker with enough time for me to react.

Data sheet with graph at http://www.snapaction.net/pdf/vb3.pdf for our VB3 20A and 30A fuses.

From that page, a 150% overload (I hope that means 150% load and not 250% [100% load + 150% over]) takes 3.9 to 47 seconds to blow. Yes, fourty-seven seconds.

Same for our MX5 40A fuses: http://www.snapaction.net/pdf/MX5%20Spec%20Sheet.pdf.

Probably ought to go smaller rather than larger.
__________________

Silicon Valley Regional 2005, 2006 972
Silicon Valley Regional 2007 668 Xerox Creativity Award
Championship Event 2007 668
Portland Regional 2008 668
Silicon Valley Regional 2008 668, 972
Beta Test Team 2008 668 (with 100 & 254)
Silicon Valley Regional 2009 668 Regional Chairman's Award; 2643
Sacramento Regional 2009 668 Winning Alliance (thanks, 1717 & 2473!), 2010 Winning Alliance 3256
CalGames 2006, 2007, 2008, 2009, 2010, 2011 Field Tech
NorCal FTC Regional 2008, 2009 Inspector
Championship Event 2009
San Diego, Silicon Valley Regionals; Champ. Event 2010 668, 2643, 3256
Silicon Valley, Madera Regional 2012 2643
WRRF Programming Instructor 2006-2016
Regional Woodie Flowers Award 2014 2643 Utah Regional

Reply With Quote
  #8   Spotlight this post!  
Unread 02-15-2018, 06:49 AM
Daniel_LaFleur's Avatar
Daniel_LaFleur Daniel_LaFleur is offline
Mad Scientist
AKA: Me
FRC #2040 (DERT)
Team Role: Engineer
 
Join Date: Apr 2005
Rookie Year: 2003
Location: Peoria, IL
Posts: 2,319
Daniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond repute
Send a message via MSN to Daniel_LaFleur
Re: Determining Correct Circuit Breaker

Quote:
Originally Posted by garyk View Post
Our breakers are thermal breakers and are very slow to blow. Iíve see a stalled motor pull 90 amps, measured, through a 40 amp breaker with enough time for me to react.

Data sheet with graph at http://www.snapaction.net/pdf/vb3.pdf for our VB3 20A and 30A fuses.

From that page, a 150% overload (I hope that means 150% load and not 250% [100% load + 150% over]) takes 3.9 to 47 seconds to blow. Yes, fourty-seven seconds.

Same for our MX5 40A fuses: http://www.snapaction.net/pdf/MX5%20Spec%20Sheet.pdf.

Probably ought to go smaller rather than larger.
Ratings on breakers are typically misunderstood.
The rating is the continuous amperage where it will NOT trip.

90 amps is only 225% of rating for a 40 amp breaker, so I would expect ~10 seconds before it initially trips.

Breakers are also NOT designed to protect the devices on the wire. They are designed to prevent the wires themseves from catching fire, which is why FIRST requires specific wire sizes for the breaker rating.
__________________
"We are not now that strength which in old days moved earth and heaven; that which we are, we are;
One equal temper of heroic hearts, Made weak by time and fate, but strong in will
To strive, to seek, to find, and not to yield. "
- Tennyson, Ulysses
Reply With Quote
  #9   Spotlight this post!  
Unread 02-15-2018, 11:29 AM
Mr V's Avatar
Mr V Mr V is online now
Registered User
FRC #5588 (Reign)
Team Role: Coach
 
Join Date: Feb 2011
Rookie Year: 2009
Location: Maple Valley Wa
Posts: 1,189
Mr V has a reputation beyond reputeMr V has a reputation beyond reputeMr V has a reputation beyond reputeMr V has a reputation beyond reputeMr V has a reputation beyond reputeMr V has a reputation beyond reputeMr V has a reputation beyond reputeMr V has a reputation beyond reputeMr V has a reputation beyond reputeMr V has a reputation beyond reputeMr V has a reputation beyond repute
Re: Determining Correct Circuit Breaker

Quote:
Originally Posted by Daniel_LaFleur View Post
Ratings on breakers are typically misunderstood.
The rating is the continuous amperage where it will NOT trip.

90 amps is only 225% of rating for a 40 amp breaker, so I would expect ~10 seconds before it initially trips.

Breakers are also NOT designed to protect the devices on the wire. They are designed to prevent the wires themseves from catching fire, which is why FIRST requires specific wire sizes for the breaker rating.
Correct, breakers fall under the group of devices known as Circuit protection devices, they are not for protecting devices fed by the circuit. Their purpose is to prevent wires from heating to the point where the insulation is compromised, nothing more.
Reply With Quote
  #10   Spotlight this post!  
Unread 02-15-2018, 06:46 PM
garyk garyk is offline
Programming Mentor, 972 and 2643
FRC #2643 (Dark Matter)
Team Role: Mentor
 
Join Date: Dec 2006
Rookie Year: 2005
Location: Santa Clara (Silicon Valley) Calif.
Posts: 171
garyk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant futuregaryk has a brilliant future
Re: Determining Correct Circuit Breaker

Quote:
Originally Posted by Daniel_LaFleur View Post
Ratings on breakers are typically misunderstood.
The rating is the continuous amperage where it will NOT trip.

90 amps is only 225% of rating for a 40 amp breaker, so I would expect ~10 seconds before it initially trips.

Breakers are also NOT designed to protect the devices on the wire. They are designed to prevent the wires themseves from catching fire, which is why FIRST requires specific wire sizes for the breaker rating.
Huh, obviously I didnít know that. One of the things I love about a FIRST and FRC is how much I learn from my students and the FIRST community. Thanks!
__________________

Silicon Valley Regional 2005, 2006 972
Silicon Valley Regional 2007 668 Xerox Creativity Award
Championship Event 2007 668
Portland Regional 2008 668
Silicon Valley Regional 2008 668, 972
Beta Test Team 2008 668 (with 100 & 254)
Silicon Valley Regional 2009 668 Regional Chairman's Award; 2643
Sacramento Regional 2009 668 Winning Alliance (thanks, 1717 & 2473!), 2010 Winning Alliance 3256
CalGames 2006, 2007, 2008, 2009, 2010, 2011 Field Tech
NorCal FTC Regional 2008, 2009 Inspector
Championship Event 2009
San Diego, Silicon Valley Regionals; Champ. Event 2010 668, 2643, 3256
Silicon Valley, Madera Regional 2012 2643
WRRF Programming Instructor 2006-2016
Regional Woodie Flowers Award 2014 2643 Utah Regional

Reply With Quote
Reply


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 12:02 AM.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi