#46
|
||||
|
||||
|
Re: Keeping the main breaker from tripping
Quote:
|
|
#47
|
|||
|
|||
|
Re: Keeping the main breaker from tripping
No, we compared it to the voltage drop data
|
|
#48
|
|||||
|
|||||
|
Re: Keeping the main breaker from tripping
Jared,
In some ways, replacing a tripped breaker is a good practice. When that breaker trips under high loads, the load is actually fairly inductive. As such when the contacts open under load, there is some pitting of the contact that takes place. This pitting can raise the series resistance, ultimately raising the heat generated for a fixed current. These breakers are unlike the protection breakers used in your home. Those generally will have a design that both protects long term high currents and sudden overloads. The trip curve for these breakers has a wide range because they are simple (cheap) and provide the coverage needed for our designs. No one has mentioned this yet so let me add this to the mix. (Yes, I am the one who said the king had no clothes.) If I observe a team tripping the main breaker for any reason other than a catastrophic electrical failure, I would not consider them a good alliance partner. If we need you to play an entire match to win, why would we take the chance at a good robot who trips the main breaker in the hopes it won't happen in a critical match. Personally, I would rather have an OK robot who doesn't break over a great robot that sometimes sits idle in the middle of the playing field. When I see a team spraying their breaker, I have to wonder...are they covering up a design flaw or are they just being cautious? For those who think spray is illegal can you tell me why you think that? For the peltier, I would consider the rule about being accessible and visible would not be accomplished by putting the breaker in an insulated box. For general knowledge... when you see one or more of us run out on the field when a robot stops during a match, the first thing we are looking at is the main breaker status, followed by indicators on the DSC, cRio, PD and radio. This sweep will give us an indication of what might have occurred. It is the standard list of checks that was formed following the Einstein weekend a few years ago. We want to be sure every team is given every chance to compete. Last edited by Al Skierkiewicz : 10-12-2014 at 08:27. |
|
#49
|
||||
|
||||
|
Re: Keeping the main breaker from tripping
"Canned air" is generally not actually air. Some versions are flammable. If you are using one of those versions, I would avoid spraying it on energized components.
![]() |
|
#50
|
|||
|
|||
|
Re: Keeping the main breaker from tripping
Quote:
Yes, ambient temperatures affect thermal circuit breakers. Using any sort of device to intentionally cool the breaker violates the intent of the safety mechanism. If a team is popping breakers after X time, they are then exceeding the ratings. The only reason for attempting to cool it down is to "cold soak" the breaker to attempt to uprate the breaker and increase the current required to trip it. I see little difference between intent in using compressed air and packing dry ice around a breaker during a match. Now, if a team wishes to cherry pick which breaker they want to use, that is a different matter. But intentionally manipulating the environment around the breaker to prevent the breaker from tripping is a direct attempt to bypass the safety mechanism the breaker provides. |
|
#51
|
|||||
|
|||||
|
Re: Keeping the main breaker from tripping
Quote:
If the breaker under normal operating conditions (ie: starting at roomp temp) can reach current A before tripping, due to temperature A, then if a match is played shortly thereafter, and the temperature of the bar has not returned to room temp, it will actually trip at some current less than A. How is restoring the breaker to the properties it has at room temperature a safety risk? If you accept that the breaker is meant to operate at room temperature in a safe manner, there is no justification for claiming that cooling it to room temperature rapidly is any different than operating it as if it were always at room temperature. |
|
#52
|
||||
|
||||
|
Re: Keeping the main breaker from tripping
As I read this thread, I'm more and more on the fence about this issue. I'm starting to thinks it's fine, mainly because of the point that Cory brought up: the breaker spray doesn't really keep the breaker any colder than ambient temperature, it just resets the temperature to what is was before.
My original opinion that the breaker spray was against the rules was from somebody who made the argument that it was similar to tampering with a thermostat by tricking it into thinking the room is colder than it is. I now realize that this isn't really an effective analogy. |
|
#53
|
|||||
|
|||||
|
Re: Keeping the main breaker from tripping
I would agree that a permanent solution to cooling (keeping the breaker below ambient) the internal temperature of the breaker would be a violation of safety protection for which the breaker is ultimately designed.
The breakers on the robot are intended to prevent fires due to high current in any circuit on the robot. The wiring from the battery to the main breaker is the only circuit not protected. All breakers are meant to protect the wiring for this reason, not the load. The current rating vs. wire size is a derivative of the NEC specifications for open frame wiring. We slightly derate the tables based on the short time in use. These are not continuous (24 hour) currents. Even with the protection, we sometimes do see fires or at least significant smoke events all the time. While we are on the subject, if you remove a motor(s) but leave the wiring, you must remove the breaker feeding that branch. (Consider this a 'best practice" method.) Last edited by Al Skierkiewicz : 11-12-2014 at 07:44. |
|
#54
|
|||
|
|||
|
Re: Keeping the main breaker from tripping
Tim Allen would be proud of First this year. "more power" This year a large portion of First teams will be pushing the the robot power system to the limit. A large number of robots are going to push power draw beyond rating and eat up safety factor of many components of the power system. There are going to be problems. Saw many examples of this last year. Smart teams will develop power management strategies and be able to push the power system with out failures and reliability problems. Those who don't will learn the hard way of what happens when you push systems beyond their safe operating zone. Scouting needs to track teams that have "power problems". Bad alliance choice. Get smart or suffer. The new control system has the resource to help teams with power management. This is a comprehensive systems problem and is complex. Teams will need to put much effort into this. Positive is that this is an excellent opportunity for students to learn the process of data collection, analysis and the development of strategies based on this. The bad part what we are teaching future engineers. "More Power" is not an attitude future engineers should embrace. First could address this problem by limiting motor choice for drive trains. That would get the forum hopping. Or more like the real world, First could attach cost to the robot power. Like each cim above 4 costs a team xx points every match. With the new PDB they could asses a xx point penalty for every total robot power draw above xxxx watts. We should teach the cost of power.
|
|
#55
|
||||
|
||||
|
Re: Keeping the main breaker from tripping
You are already penalized for using too much power. You trip the main breaker.
As Al says, that should move you down the pick list for alliance selection. Kinda like mecanum wheels. Maybe that should be a scouting question. |
|
#56
|
|||
|
|||
|
Re: Keeping the main breaker from tripping
Quote:
By cooling the breaker, you are trying to bypass the safety mechanism it represents which includes long duration overloads such as you are apparently inducing in your design. How long does it for the breaker to trip when you practice? Last edited by adciv : 11-12-2014 at 13:13. |
|
#57
|
||||
|
||||
|
Re: Keeping the main breaker from tripping
Quote:
|
|
#58
|
|||
|
|||
|
Re: Keeping the main breaker from tripping
This one is really more about safety than short circuts. Touching live prong would be quite dangerous and undesireable, so the outlet design offers a level of safety. European plugs are actually better, because your finger can never touch energized metal, but the US design is better than having prongs stick out of the wall.
|
|
#59
|
||||
|
||||
|
Re: Keeping the main breaker from tripping
Quote:
So I feel that cooling the breaker is a bad idea because you are "resetting it" to ambient temps but not doing the same for the wiring which it is supposed to protect. |
|
#60
|
|||||
|
|||||
|
Re: Keeping the main breaker from tripping
Quote:
|
![]() |