Quote:
Originally Posted by ozrien View Post
The changes between 1.60 and 1.62 are slight changes in the status LED. There is no compressor related change between the two.

If your having trouble with your PCM, go to the self-test page of the roboRIO web-page configuration.
Jump to "Self Test"...
http://wpilib.screenstepslive.com/s/...ribution-panel

This will tell you...
(1) -if the PCM is enabled (robot is enabled)
(2)- if the pressure-switch is closed (pressure is not full)
(3)- if the compressor-output is on

(3) requires (1) and (2) regardless of which firmware is used.

Does the compressor turn off when the robot is disabled? If not then it sounds like the compressor ground input is shorting to robot ground somewhere outside of the PCM.

When the compressor is on, is (1),(2),(3) reported in the self-test?

Another easy check is to just disconnect the pressure switch. The PCM has two weidmuller connectors that normally go to the pressure-switch. When the pressure-switch signals not-full, it shorts the two leads together (relay). When the pressure-switch signals full, the two leads are open. So if you short the two BLUE PRESSURE SW. connectors on the PCM with a wire, instead of connecting to pressure-switch, PCM will behave as though the pressure-switch reads not-full. Remove the wire and PCM will behave as though pressure-switch reads full.
How do we get the old version of the firmware (1.60)? We know for sure the pressure switch is good. We did series of tests to isolate it. When we did the self test there was no single instance when the compressor is indicated full.
Right now we will try a new PCM and see what happens. We will try this tomorrow. I will keep you updated.
  #32   Spotlight this post!  
Unread 18-01-2015, 17:56
jSchnitz's Avatar
jSchnitz jSchnitz is online now
Lead Programmer, Operator
AKA: Jacob Schnitzlein
FRC #1986 (Team Titanium)
Team Role: Programmer
 
Join Date: Mar 2014
Rookie Year: 2014
Location: Lee's Summit, MO
Posts: 20
jSchnitz is on a distinguished road
Re: Air Compressor not turning off.

Quote:
Originally Posted by dradel View Post
Ours won't even turn on!!
Do you have a solenoid anywhere in your code? Our experience was that the compressor needed that before it would run.
  #33   Spotlight this post!  
Unread 19-01-2015, 13:08
WDB WDB is offline
Registered User
FRC #2363
 
Join Date: Jan 2015
Location: Virginia
Posts: 4
WDB is an unknown quantity at this point
Re: Air Compressor not turning off.

Quote:
Originally Posted by ozrien View Post
The changes between 1.60 and 1.62 are slight changes in the status LED. There is no compressor related change between the two.

If your having trouble with your PCM, go to the self-test page of the roboRIO web-page configuration.
Jump to "Self Test"...
http://wpilib.screenstepslive.com/s/...ribution-panel

This will tell you...
(1) -if the PCM is enabled (robot is enabled)
(2)- if the pressure-switch is closed (pressure is not full)
(3)- if the compressor-output is on

(3) requires (1) and (2) regardless of which firmware is used.

Does the compressor turn off when the robot is disabled? If not then it sounds like the compressor ground input is shorting to robot ground somewhere outside of the PCM.

When the compressor is on, is (1),(2),(3) reported in the self-test?

Another easy check is to just disconnect the pressure switch. The PCM has two weidmuller connectors that normally go to the pressure-switch. When the pressure-switch signals not-full, it shorts the two leads together (relay). When the pressure-switch signals full, the two leads are open. So if you short the two BLUE PRESSURE SW. connectors on the PCM with a wire, instead of connecting to pressure-switch, PCM will behave as though the pressure-switch reads not-full. Remove the wire and PCM will behave as though pressure-switch reads full.
We put the firmware version 1.62 back in to reconfirm.
The compressor STILL is not turning off -- while minutes before, the other (v1.6) PCM was working perfectly.

Also, after removing the 2 pressure switch leads from the PCM, we see this:

The self test completed successfully.

PCM is enabled.
Compressor is close-looped on sensor
Comp Is On
Pressure is not full

Checked also for damage, shorts, or stray wire bits, but it's clean.
Other than getting another PCM to try, I don't know what to do next.
Ideas?
  #34   Spotlight this post!  
Unread 19-01-2015, 13:37
ozrien's Avatar
ozrien ozrien is offline
Omar Zrien
AKA: Omar
no team
Team Role: Mentor
 
Join Date: Sep 2006
Rookie Year: 2003
Location: Sterling Heights, MI
Posts: 522
ozrien has a reputation beyond reputeozrien has a reputation beyond reputeozrien has a reputation beyond reputeozrien has a reputation beyond reputeozrien has a reputation beyond reputeozrien has a reputation beyond reputeozrien has a reputation beyond reputeozrien has a reputation beyond reputeozrien has a reputation beyond reputeozrien has a reputation beyond reputeozrien has a reputation beyond repute
Re: Air Compressor not turning off.

So judging from the Self-Test the PCM reports that the "Pressure is not full" despite the pressure-switch inputs on the PCM not being wired to anything. That is likely the root cause for WDB's symptom, and not firmware. This sounds like hardware and your "other PCM" likely works regardless of what firm is in it.

To further confirm it's not a firm issue, I put up 1.60 PCM firm (one-dot-sixty) at...
http://www.crosstheroadelectronics.c...ation-1.60.crf
... Flash 1.60 back into your bad PCM and I bet you will still find that the self-test still reads "Pressure is not full" despite having the PCM not connected to the pressure-switch.

For any given functional PCM : When the pressure switch is not connected, Pressure should read as "Pressure is Full", regardless of all other factors. This is deliberate so an unplugged pressure switch causes compressor to stop.

dumbuya, can you do the same check? Unplug the pressure-switch from the PCM and run the Self-Test to see if the pressure still reads "Pressure is not full".

At any rate dumbuya and WDB, I recommend contacting support@crosstheroadelectronics.com for next steps.
  #35   Spotlight this post!  
Unread 19-01-2015, 14:21
WDB WDB is offline
Registered User
FRC #2363
 
Join Date: Jan 2015
Location: Virginia
Posts: 4
WDB is an unknown quantity at this point
Re: Air Compressor not turning off.

Quote:
Originally Posted by ozrien View Post
So judging from the Self-Test the PCM reports that the "Pressure is not full" despite the pressure-switch inputs on the PCM not being wired to anything. That is likely the root cause for WDB's symptom, and not firmware. This sounds like hardware and your "other PCM" likely works regardless of what firm is in it.

To further confirm it's not a firm issue, I put up 1.60 PCM firm (one-dot-sixty) at...
http://www.crosstheroadelectronics.c...ation-1.60.crf
... Flash 1.60 back into your bad PCM and I bet you will still find that the self-test still reads "Pressure is not full" despite having the PCM not connected to the pressure-switch.

For any given functional PCM : When the pressure switch is not connected, Pressure should read as "Pressure is Full", regardless of all other factors. This is deliberate so an unplugged pressure switch causes compressor to stop.

dumbuya, can you do the same check? Unplug the pressure-switch from the PCM and run the Self-Test to see if the pressure still reads "Pressure is not full".

At any rate dumbuya and WDB, I recommend contacting support@crosstheroadelectronics.com for next steps.

Confirmed. Reflashed the suspect PCM back to 1.6 and the same behavior was observed. Removing the pressure switch from the PCM should not allow the compressor to run, but it still runs. So it looks like a hardware problem with this specific PCM. Put in our other PCM in and it works perfectly.

We took a picture of the board near the pressure switch contacts and there might be some anomaly there (you'll have to zoom in a little), but we'll get a replacement PCM anyway.

Thanks Omar for your assistance!
Attached Thumbnails
Click image for larger version

Name:	PCM_poss_press_sw_short.JPG
Views:	56
Size:	487.7 KB
ID:	17896  
  #36   Spotlight this post!  
Unread 19-01-2015, 15:51
dumbuya dumbuya is offline
Registered User
FRC #1769
 
Join Date: Feb 2006
Location: Lenexa, Kansas
Posts: 16
dumbuya is an unknown quantity at this point
Re: Air Compressor not turning off.

Quote:
Originally Posted by ozrien View Post
So judging from the Self-Test the PCM reports that the "Pressure is not full" despite the pressure-switch inputs on the PCM not being wired to anything. That is likely the root cause for WDB's symptom, and not firmware. This sounds like hardware and your "other PCM" likely works regardless of what firm is in it.

To further confirm it's not a firm issue, I put up 1.60 PCM firm (one-dot-sixty) at...
http://www.crosstheroadelectronics.c...ation-1.60.crf
... Flash 1.60 back into your bad PCM and I bet you will still find that the self-test still reads "Pressure is not full" despite having the PCM not connected to the pressure-switch.

For any given functional PCM : When the pressure switch is not connected, Pressure should read as "Pressure is Full", regardless of all other factors. This is deliberate so an unplugged pressure switch causes compressor to stop.

dumbuya, can you do the same check? Unplug the pressure-switch from the PCM and run the Self-Test to see if the pressure still reads "Pressure is not full".

At any rate dumbuya and WDB, I recommend contacting support@crosstheroadelectronics.com for next steps.
No matter what test setup we did it shows on the self test " Pressure is not full". We found a fix now by swapping a new PCM and it works as intended.
However, I cannot tell you what we find to be the issue other than to say we might have had bad PCM.

One thing I could try is update 1.6 firmware in the old ( "bad") one and see if it is going to respond as intended.

Thanks for your urgent response to the issue.
  #37   Spotlight this post!  
Unread 20-01-2015, 11:10
dumbuya dumbuya is offline
Registered User
FRC #1769
 
Join Date: Feb 2006
Location: Lenexa, Kansas
Posts: 16
dumbuya is an unknown quantity at this point
Re: Air Compressor not turning off.

Thank you to all for sharing your experiences with the PCM.

We swapped the PCM with a new one and it worked as expected.
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 16:46.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi