programming pneumatics psi

Our programmer needs to know how to program our pneumatics to shut down at 60 psi.

We use labview
__________________



I think, therefore I am lost....- Me

"The difference between me and the rest of the world is sanity. They have it, I don't"
  #2   Spotlight this post!  
Unread 27-01-2010, 12:11
MrForbes's Avatar
MrForbes MrForbes is offline
Registered User
AKA: Jim
FRC #1726 (N.E.R.D.S.)
Team Role: Mentor
 
Join Date: Feb 2006
Rookie Year: 2006
Location: Sierra Vista AZ
Posts: 5,991
MrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond reputeMrForbes has a reputation beyond repute
Re: programming pneumatics psi

The pressure switch that comes in the KOP is set for about 115-120 psi. There is a pressure regulator that you need to use to reduce this to a working pressure of 60 psi or less. And there is another regulator you can use to reduce it further for other purposes.

If you want to limit the high pressure storage part of the system to 60 psi, you'll probably need to get a pressure switch or transducer that is set to 60 psi, or a transducer that can measure the pressure. But you'll probably find out that you really just need to understand the pneumatic system fully, and that you don't need to bother with extra switches.
  #3   Spotlight this post!  
Unread 27-01-2010, 12:38
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,770
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: programming pneumatics psi

The running test you will be required to demonstrate during inspections is that when you enable the robot, the compressor turns on and pressurizes to 120 psi (or slightly less) as verified by the high side gauge and then shuts off under Crio control. While this test is running your inspector will also examine the low side gauge to insure that the pressure there rises to 60 psi and no higher. Then you will be asked to disable the robot and vent the pressure at which time both gauges should return to zero.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #4   Spotlight this post!  
Unread 27-01-2010, 12:57
Daniel_LaFleur's Avatar
Daniel_LaFleur Daniel_LaFleur is offline
Mad Scientist
AKA: Me
FRC #2040 (DERT)
Team Role: Engineer
 
Join Date: Apr 2005
Rookie Year: 2003
Location: Peoria, IL
Posts: 1,964
Daniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond repute
Send a message via MSN to Daniel_LaFleur
Re: programming pneumatics psi

Quote:
Originally Posted by Al Skierkiewicz View Post
The running test you will be required to demonstrate during inspections is that when you enable the robot, the compressor turns on and pressurizes to 120 psi (or slightly less) as verified by the high side gauge and then shuts off under Crio control. While this test is running your inspector will also examine the low side gauge to insure that the pressure there rises to 60 psi and no higher. Then you will be asked to disable the robot and vent the pressure at which time both gauges should return to zero.
Al,

Could you please quote the rule that requires the high side to go to 120PSI?

There are teams considering using compressors that have a max 105PSI.
__________________
___________________
"We are not now that strength which in old days moved earth and heaven; that which we are, we are;
One equal temper of heroic hearts, Made weak by time and fate, but strong in will
To strive, to seek, to find, and not to yield. "
- Tennyson, Ulysses
  #5   Spotlight this post!  
Unread 27-01-2010, 13:10
Unsung FIRST Hero
Al Skierkiewicz Al Skierkiewicz is offline
Broadcast Eng/Chief Robot Inspector
AKA: Big Al WFFA 2005
FRC #0111 (WildStang)
Team Role: Engineer
 
Join Date: Jun 2001
Rookie Year: 1996
Location: Wheeling, IL
Posts: 10,770
Al Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond reputeAl Skierkiewicz has a reputation beyond repute
Re: programming pneumatics psi

Daniel,
This is the test we have been using as part of inspections for at least the last five years. The rules state...
<R74> If pneumatic components are used on the ROBOT, the pneumatic system on the ROBOT must contain as a minimum
• Pressure gauges to display the “stored” and “working” air pressure (see Rule <R76>), the following components, connected in accordance with this section.
• A pressure relief valve, calibrated and set to release at 125psi (see Rule <R77>),
• A pressure switch, calibrated and connected to the ROBOT control system (see Rule <R78>),
• An easily visible and accessible pressure vent plug valve to manually relieve the stored pressure (see Rule <R79>).
And...
<R78> The Nason pressure switch must be connected to the high-pressure side of the pneumatic circuit (i.e. prior to the pressure regulator) to sense the “stored” pressure of the circuit. The two wires from the pressure switch must be connected directly to a digital input and ground port on the Digital Sidecar, and the cRIO-FRC must be programmed to sense the state of the switch and operate the relay module that powers the compressor to prevent over-pressuring the system.
This is tested during the powerup section of the inspection checklist. (hopefully similar to 2009 and prior)

If you are using a compressor that cannot achieve shutoff pressure, then the solution needs to be addressed by the GDC. My first question would of course be what is the max pressure that the compressor can withstand? Does the pressure relief valve protect that max pressure and how to shut off the compressor before achieving that pressure.
__________________
Good Luck All. Learn something new, everyday!
Al
WB9UVJ
www.wildstang.org
________________________
Storming the Tower since 1996.
  #6   Spotlight this post!  
Unread 27-01-2010, 15:36
Daniel_LaFleur's Avatar
Daniel_LaFleur Daniel_LaFleur is offline
Mad Scientist
AKA: Me
FRC #2040 (DERT)
Team Role: Engineer
 
Join Date: Apr 2005
Rookie Year: 2003
Location: Peoria, IL
Posts: 1,964
Daniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond reputeDaniel_LaFleur has a reputation beyond repute
Send a message via MSN to Daniel_LaFleur
Re: programming pneumatics psi

Quote:
Originally Posted by Al Skierkiewicz View Post
Daniel,
This is the test we have been using as part of inspections for at least the last five years. The rules state...
<R74> If pneumatic components are used on the ROBOT, the pneumatic system on the ROBOT must contain as a minimum
• Pressure gauges to display the “stored” and “working” air pressure (see Rule <R76>), the following components, connected in accordance with this section.
• A pressure relief valve, calibrated and set to release at 125psi (see Rule <R77>),
• A pressure switch, calibrated and connected to the ROBOT control system (see Rule <R78>),
• An easily visible and accessible pressure vent plug valve to manually relieve the stored pressure (see Rule <R79>).
And...
<R78> The Nason pressure switch must be connected to the high-pressure side of the pneumatic circuit (i.e. prior to the pressure regulator) to sense the “stored” pressure of the circuit. The two wires from the pressure switch must be connected directly to a digital input and ground port on the Digital Sidecar, and the cRIO-FRC must be programmed to sense the state of the switch and operate the relay module that powers the compressor to prevent over-pressuring the system.
This is tested during the powerup section of the inspection checklist. (hopefully similar to 2009 and prior)

If you are using a compressor that cannot achieve shutoff pressure, then the solution needs to be addressed by the GDC. My first question would of course be what is the max pressure that the compressor can withstand? Does the pressure relief valve protect that max pressure and how to shut off the compressor before achieving that pressure.
Thanks for the clarification Al.

I guess this will have to be a Q&A question since the cRIO could be programmed to read the pressure switch and shut off the compressor @ 120PSI but not be able to test that programming if the compressor is not capable of 120 PSI.
__________________
___________________
"We are not now that strength which in old days moved earth and heaven; that which we are, we are;
One equal temper of heroic hearts, Made weak by time and fate, but strong in will
To strive, to seek, to find, and not to yield. "
- Tennyson, Ulysses
  #7   Spotlight this post!  
Unread 28-01-2010, 09:46
thatoneguy23's Avatar
thatoneguy23 thatoneguy23 is offline
Fiding everything we need to know.
FRC #2389 (Oklahoma STORM)
Team Role: Scout
 
Join Date: Jan 2010
Rookie Year: 2010
Location: Oklahoma
Posts: 41
thatoneguy23 is on a distinguished road
Re: programming pneumatics psi

cool, thanks for the info guys.
__________________



I think, therefore I am lost....- Me

"The difference between me and the rest of the world is sanity. They have it, I don't"
Closed Thread


Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
programming pneumatics holty531 Programming 9 02-02-2008 22:03
PROGRAMMING PNEUMATICS Reaper40 Pneumatics 17 02-02-2008 07:55
Programming Pneumatics? itzrobz Programming 2 20-01-2007 00:30
Programming of Pneumatics Ben Piecuch Programming 3 18-02-2005 02:39
Pneumatics Programming KWalsh Programming 8 19-02-2004 09:17


All times are GMT -5. The time now is 16:38.

The Chief Delphi Forums are sponsored by Innovation First International, Inc.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.
Copyright © Chief Delphi