Can anyone verify that there’s no rule against running a victor-driven mini-cim on a 30A breaker circuit? The mini-cim is ~19A.
Thanks.
Can anyone verify that there’s no rule against running a victor-driven mini-cim on a 30A breaker circuit? The mini-cim is ~19A.
Thanks.
The table in R46 does indeed allow this, but any reason as to why you’re not running it off a 40A breaker? I assume you’re not out of 40A slots on the PDB.
Yep… we’ll most likely be out of 40A slots.
Thanks.
Breakers are sized for the wire they feed. If you choose a smaller gauge wire then you may use a smaller breaker.
I thought we could use the larger gauge wire with a smaller breaker. We have been using 10 gauge for the 40 amp. This is left over from when 10 gauge was required.
The rules (R47) specifiy a minimum wire size per breaker size.
Andy,
Yes you can, the wire size minimum is listed by the breaker feeding that branch. i.e. a 40 amp breaker can be used with #12 wire but I recommend #10 for CIM motors. The wire size is chosen for safety and voltage drop from the NEC handbook for open frame DC wiring. If #14 wire was used with the 40 amp breaker, it is possible to heat the wire to the point at which the insulation fails. #12 wire on the other hand may get warm but not to the point at which a failure would occur. A dead short of course, would be protected by the breaker. At 100 amps, the #12 drops ~0.2 volts per foot. In a typical robot wiring job I would expect to lose almost a volt at the motor input during starting and heavy loading with a fully charged battery.
Can we use CIMs from the 30A? Or any motor controller for that matter?
Thanks!
Isn’t it the other way around?
If you choose a smaller gauge wire then you must use a smaller breaker.
Or maybe it’s the ambiguity of the phrase “smaller gauge wire”…