Can you use two channels of PDP (40A) each in parallel combination to provide 80A current to a single motor and having three more motors on the other 40 A channels taking current to 320 A.
Or can you use two channels in series combination to provide 24 volts to a motor?
I don’t think it’s possible but I just want to confirm from someone who has used this board
and if you can do suggest some power distribution board that can provide either 24V DC or has upto 80-90 A channels.
I think old PDP was 24V
can I get it from somewhere?
Serial for 24V would not work at all; the circuits are in parallel of the same 12V battery.
Parallel for more current would work, but it compromises the safety reasons you use breakers in the first place. Further, if you did trip one, the other would follow immediately. Then, as one would come back in before the other, you’d likely trip it before the other one came back, assuming the load was still in the circuit. If you need an 80A circuit, get an 80A breaker.
Maxi fuses are available up to 80A; if you do this, do not use it in a PDP (which is not sized internally for that much current); use it with afuse holder designed for up to 80A.
Optionally, auto parts shops sell breakers this size in the same style as the FRC standard 120A main breaker.
Something like this, perhaps (though 50A, not 80). I’ve got one coming in on Monday.
Those are also available with more positions though you’ve have to check the mfg ratings to see if you could supply a 320a load with just a single bus.
Personally I’d use this breaker as it has a manual reset and the brackets that will allow you to place them in the configuration needed to gang a pair with the buss bar.
Ahmed,
You need to be a little more descriptive in your question. If you are simply asking about FRC use, what you ask is not legal. While the PDP is designed to use 40 amp breakers, the copper on the board is capable of much higher currents. Remember that a large CIM has a stall current of 131 amps. I have not heard of a PDP failure due to over current except when abused by having metal flakes inside or having bypassed the standard breaker recommendations. If you have a non-FRC application please specify what that app might be in both volt and amp specifications.